dear ahmed !THIS IS ALARMING SITUATION. there are certain things which i dont know about your project,but i have assumed and calculated required thickness of your panel,which comes to be AT LEAST 9.2 INCH.REFERENCE ACI318-14 (TABLE 8.3.1.2)
1-THIS 5cm deflection is immediate,the long term will be approximately 12 cm,but you can calculate exactly by yourself. i dont know what is allowable deflection in your case.
2-i have considered your panel interior ,and taken 9.2m clear span.
• L/480 for the part of the total deflction that occurs after attachment of elements, that is, the
sum of the long-time deflction due to all sustained loads and the immediate deflction due
to any additional live load, for flors or roofs supporting elements likely to be damaged by
large deflctions.