Minimum Reinforcement Ratio!!!
why the minimum steel reinforcement ratio is greater than shrinkage/temperature reinforcement in slabs?ACI reference is 8.2.1.6,if suppose a lesser reinforcement required what is the reason to provide at least equal to shrinkage reinforcement?
First of all you should refer to ACI 318 by year too. I mean the clause you mentioned is from ACI 2005 or 2008. Because numbering of the clauses has been changed. So 8.2.1.6 in 2005 is different from 8.2.1.6 rather there is no such 8.2.16 in 2008 version. Anyway,
Regarding your question of minimum reinforcement. Always remember that reversal of moments or forces takes place for example in wind or eartquake. So your positive moment becomes negative and vice versa. For example in a blast loading your slab may crack because in middle span the top reinforcement you provided was insufficient. That is the region where you can ignore the reinforcement generally. Thats why ACI has some limits for minimum reinforcement, although the minimum reinfocement will still not be enough for blast loading but thats another issue.
Minimum reinforcement is different than the temperature and shrinkage reinforcement. For example
Temp reinforcement (0.0018bh) is the total area of steel you have to put in slab or footing. Put half at top and half at bottom or total at mid..whatever..ok!
But 0.0018bh if you talk about min flexural reinf you have to put full at top and and full at bottom.
actually i was editing the ACI reference but my pc had no power suddenly :-) so sorry for that,thanx for reply Rana sab