*SEFP Consistent Design*

*1997 UBC vertical earthquake term*

*Doc No: 10-00-CD-0002*

*Date: May 30, 2013*

*Article is ripped: Good one to share though* 

 

For Strength Design, Ev has the effect of increasing compression and tension/uplift effects on vertical load carrying systems. Ev is not applicable for Allowable Stress Design. The new term, Ev, was introduced in the 1997 UBC. UBC Section 1630.1 defines Ev as the load effect resulting from the vertical component of the earthquake ground motion.
 
For Strength Design, Ev is defined as 0.5CaID. For Allowable Stress Design, Ev is defined as 0.
Ca= seismic coefficient from UBC Table 16-Q
I = importance factor from UBC Table 16-K
D = dead load
 
UBC Section 1630.1.1 defines the earthquake load, E, as the earthquake load on an element of the structure resulting from the combination of the horizontal component Eh and the vertical component Ev.
E = Rh*Eh + Ev (UBC 30-1)Rh= redundancy factor defined in UBC Section 1630.1.1Eh = earthquake load resulting from either the base shear, V, or the design lateral force, FpSubstituting the definition of Ev into this equation results in:E =Rh*Eh + 0.5CaID (Modified 30-1)The 1997 UBC defines load combinations in Section 1612. Strength load combinations 12-5 and 12-6include E.1.2D + 1.0E +(f1L + f2S) (UBC 12-5)0.9D (1.0E or 1.3W) (UBC 12-6)Substituting modified equation 30-1 into these equations results in:1.2D + 1.0 Eh + 0.5CaID + (f1L + f2S) (Modified 12-5)(0.9 + 0.5CaI)D + Eh (Modified 12-6a)(0.9 - 0.5CaI)D - Eh (Modified 12-6b)

All terms with Eh are effects of horizontal earthquake components. These loads can be in any direction, for example, vertical loads on rigid frame columns, horizontal loads on columns, and diagonal loads on braced frames. Similarly, all terms with D, L, or S are effects of vertical loads or components. These loads can be in any direction, for example, vertical loads on beams, horizontal loads on rigid frame columns, and diagonal loads on braced frames.

Example:For typical California values of Ca = 0.40 and I = 1, the modified equations become:1.4D + 1.0Rh*Eh + (f1L + f2S)1.1D + Rh*Eh0.7D + Rh*Eh

The impact of the vertical earthquake component on modified Strength Design equations 12-5 and 12-6a is to increase compression effects on columns and foundations. The impact of the vertical earthquake component on modified Strength Design equations 12-6b is to increase tension and uplift effects on columns, anchorage, and foundations. There is no impact of the vertical earthquake component on Allowable Stress Design load combination equations.

Link to comment
Share on other sites

  • 7 months later...

In etabs we use EQX , EQY for respective directions. so this earthquake force should have carry both its vertical and horizontal component with itself. so there is no need to define these modified equations when we are assisted by software. but during manual calculations we have to incorporate these modified equations.

Is my understanding correct?  kindly correct and explain me if i am wrong ???

Link to comment
Share on other sites

AQ, you need to include additional vertical effects, in addition to the horizontal effects of EQx and EQy

In ETABS, if vertical component is applicable in your design then you must select appropriate settings from special seismic loading form and define rho and omega factors.

Link to comment
Share on other sites

  • 3 years later...

Another thought;

1. Vertical effects are not required in ASD analysis of UBC-97 but are required in ASCE 7-05.

2. Inclusion of vertical effects make no sense according to Gary R.. Searer;

SEAOC adopted the concept of vertical effects for the sole purpose of adjusting the seismic design in line with 1.4D factor of dead loads in earlier codes. This factor was changed to 1.2D due to better approximation of dead loads in the new codes. So in order to rule out the discrepancies vertical effects were introduced.

"Certain unintended consequences of this action were only discovered after the code was published"... For example one design that was safe in ASD suddenly became unsafe in strength design combinations. In near-fault areas of Ca=0.6, resistance to overturning decreases by a huge margin to 60% of dead loads.

The author explains that;

With the exception of a single story structure, ignoring live load totally in the resisting load combination is very very conservative.

In order to accelerate portions of the building rapidly upward, the upward forces must exceed gravity by a large amount, thus resisting weight is significantly greater than just 1.0 dead load.

The problem became more complicated with the inclusion of vertical effects in ASD in ASCE 7-05 in a try to align the ASD design with strength design as far as vertical effects were concerned.

He recommends using 1.2D +- E + f1L + f2S or 0.9D +- Eh.

Refer to:

 
2006 Annual Meeting of the Los Angeles Tall Buildings Structural Design Council  Alternative Procedures for Design of Tall Buildings
 POORLY WORDED, ILL-CONCEIVED, AND UNNECESSARY CODE PROVISIONS
Gary R. Searer, S.E. Consultant Wiss, Janney, Elstner Associates, Inc

https://www.scribd.com/doc/285836953/Poorly-Worded-Ill-Conceived-and-Unnecessary-Code-Provisions

 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       