Interstorey Drift Limits, Moment Releases And Base Fixity


Yasir Saleem
 Share

Recommended Posts

Hello everyone,

 

I am looking for some answers to simple questions like

 

1.  What is the inter story drift limit for steel columns , and what is the maximum deflection allowed at the mid span of the column which has axial load and lateral loading as well ? 

 

2.  How we decide the end at which moment need to be released and which one like M22 or M33? Does this depends upon the support end and type of support?

 

3.  What is the difference between the pin support and fix support in terms of its application to the model? As lateral meaning is not required its the sense that on which basis we decide that oke we donot model pin support and assign fix support to the model. and then when we are designing base connection like base plate and anchor bolt and position of anchors on the base plate. Does this all only gives us freedom in the fixity of structure at the base like we are free on locating the suitable position for anchors on the base plate or it has to do something else as well ?

 

4. What about the wind loading? if we calculate the wind load manually and then apply it as a lateral load to the whole structure is ok or we just go as making the areas around the nodes and apply the load only to the nodes and then chk the deformation. What about the wind analysis we do by the help of software how accurate are they as the deformation due to wind is nothing in many cases if you see the analysis report or table... 

Link to comment
Share on other sites

Hello everyone,

 

I am looking for some answers to simple questions like

 

1.  What is the inter story drift limit for steel columns , and what is the maximum deflection allowed at the mid span of the column which has axial load and lateral loading as well ? 

 

2.  How we decide the end at which moment need to be released and which one like M22 or M33? Does this depends upon the support end and type of support?

 

3.  What is the difference between the pin support and fix support in terms of its application to the model? As lateral meaning is not required its the sense that on which basis we decide that oke we donot model pin support and assign fix support to the model. and then when we are designing base connection like base plate and anchor bolt and position of anchors on the base plate. Does this all only gives us freedom in the fixity of structure at the base like we are free on locating the suitable position for anchors on the base plate or it has to do something else as well ?

 

4. What about the wind loading? if we calculate the wind load manually and then apply it as a lateral load to the whole structure is ok or we just go as making the areas around the nodes and apply the load only to the nodes and then chk the deformation. What about the wind analysis we do by the help of software how accurate are they as the deformation due to wind is nothing in many cases if you see the analysis report or table... 

 

1) Inter-story drift limit depends upon type of lateral loading, i.e., wind and seismic. The following two articles explain how to check them for both kind of lateral loading.

http://www.sepakistan.com/topic/1341-ubc-seismic-drift-limits/

http://www.sepakistan.com/topic/109-building-drifts-in-etabs/

Maximum deflection are allowed based on codes too. A Column with axial load and later loading is a beam-column. You can use a limit of L/360 as per UBC for that. This is for local member. For overall structure, you need to satisfy wind and seismic limits. See the links above.

 

2) Yes it does and no it doesn't. There is a trade off between pinned and fixed support and both have reasons for that e.g., impact on foundation. You as a engineer should value reasons, then analyze the same type in the model and finally make sure your connection is fabricated so that what you idealized is real too. Also, you need to see your framing to see what kind of connection would serve best.

 

3) To some extent it is what you are saying. If you assume pin, your anchor bolts need to be inside flanges along the webs as you wouldn't develop any moment in base plate. So your base plate wont be that thick. If you go other way, your base plate would be thick with stiffeners and anchor bolts located outside to make that happen. But, assuming pin or fix will have an impact on frame member sizes. It is not just location of anchor bolts. You quantity of steel may bump up if you move from fix to pin and vice versa depending upon framing.

 

4) Wind should be same for both types. I have done both and my drifts were same. Check your calculation and do a comparison of shears and drifts to see you calculated forces correctly.

Link to comment
Share on other sites

sir agree with you about the first point and i have already gone through these pages but my concern is still about the deflection of a certian member in the mid span. I say it like this that you have a steel column which is fixed at both ends and its height is say 5 meters how much the allowed deflection for that at midspan. column is loaded by uniform lateral load. As if we go to that l/360 crityeria then the deflection is too much i have seen in BS that for curtian walls and mullions this is l/175 or l/250 my question is this deflection is at the end again what about the mid span. Oke one thing we chk the slenderness of the section and it should be less then 200. what if this ration is less like 60 or 160 and the deflectionn of our coulmn is like 100 mm to 300mm? What is the criteria for that. I chkd this by considering the coulmn as a simply supported beam and calculated the deflection manually at mid span . but again what are the upper limits to confine it.    

 

About wind what about the wind results from the analysis as in many cases no value any reason for it or i am doing something wrong.

Link to comment
Share on other sites

sir agree with you about the first point and i have already gone through these pages but my concern is still about the deflection of a certian member in the mid span. I say it like this that you have a steel column which is fixed at both ends and its height is say 5 meters how much the allowed deflection for that at midspan. column is loaded by uniform lateral load. As if we go to that l/360 crityeria then the deflection is too much i have seen in BS that for curtian walls and mullions this is l/175 or l/250 my question is this deflection is at the end again what about the mid span. Oke one thing we chk the slenderness of the section and it should be less then 200. what if this ration is less like 60 or 160 and the deflectionn of our coulmn is like 100 mm to 300mm? What is the criteria for that. I chkd this by considering the coulmn as a simply supported beam and calculated the deflection manually at mid span . but again what are the upper limits to confine it.    

 

About wind what about the wind results from the analysis as in many cases no value any reason for it or i am doing something wrong.

Yasir, post a image of your complete frame, identifying the column you are talking about. What kind of lateral force resisting system you have? Generally, for columns, drift is checked at the story of interest rather than deflection at midspan; so you can not do a correlation by modelling it as a beam. Anyhow, what is your utilization of the column? And are there any beams framing in to the column at different levels? Post images so that situation can be assessed. Also post member sizes.

About the wind: what is the difference of your manual calculations from software generated total wind load? Post calculations.

Link to comment
Share on other sites

Sir g if you look at the drawing and first section at the top left side these columns the consultant has asked for inter story deflection for that section. so how will i chk that inter story deflection. i am attaching the commented copy as well from the consultant. The engineer who was working before me in this office calculated the deflection for that section busing L/200 and submitted that in the report which got rejected. So look at the drawing i think you will understand what i am saying. You will see the comment in the same first section top left side of drawing.

NYU-ATA-DRG-C1-AR-00003-00.dwg

NYU-ATA-DRG-C1-AR-00003-00 REV.02_STATUS_B_iss1_revA.pdf

Link to comment
Share on other sites

This is what I understood from the drawings: non structural members, about 5 m in length, are called upon to support the lauver. These nonstructural members are supported at bottom, mid height and at top of panel by concrete beams.

Now the question is: what should be the 'serviceability requirement' for these non-structural members. According to IBC, floor beams supporting non-plaster ceiling should be limited to a max live load, as well as wind load, deflection of l/240. But I would say that this member should fall in the category of the one's not supporting any ceiling. In that case the deflection for both load cases is limited to l/180 (IBC).

Link to comment
Share on other sites

Yes sir you are right that these are nonstructural members and and the limits you mentioned i have gone through these, but my element is attached at the top as well and consultant is asking question of inter story drift here and these deflections are again at the top end as you mentioned (not supporting the ceiling) what about the mid span if the element is fixed at both ends. 

Link to comment
Share on other sites

Checker has used the word 'interstory deflection' in his comments. I think he wants you to make sure that these members will not deflect to a extent that will damage those lauvers. So, the values that I have mentioned above are for beam or flexural members. These nonstructural members need to be checked, against wind loads, for mid span deflection. You don't have to model its connects that will resist end moments, it seems unneccesary: model these members as having simple supports, and consequently design the bolts at mid and at top for shear and tension. You can do the same for the bottom connection.

Link to comment
Share on other sites

Yasir, see the attached file. 

  • Make sure, your wind & settlement are in one direction. In the attached sketch, I didn't have enough space to draw everything systematically, so I just randomly drew stuff.
  • Your settlement at C should be Delta 1 + Delta 2
  • Make sure you run all your combos for wind

 

@Sir Zeeshan, I think his checker wants him to calculate the effect of story drifts on the member itself. Same as we used to talk about designing members that not part of lateral force resisting system but are attached to lateral force resisting system, and will undergo a delta equal to story drift that will induce moment & shear in them.

SEFP yasir.pdf

Link to comment
Share on other sites

Sir g please have look at these what is wrong and where...all the deflection criteria which are available or i have seen give us or tell us about the end deflection only. Slenderness and buickling is only one thing which t=is there to chk the element but what about this what i as asking, and if i am wrong please do correct me.

post-68-0-53247100-1372136709_thumb.png

post-68-0-75474500-1372137374_thumb.png

Link to comment
Share on other sites

Sir g please have look at these what is wrong and where...all the deflection criteria which are available or i have seen give us or tell us about the end deflection only. Slenderness and buickling is only one thing which t=is there to chk the element but what about this what i as asking, and if i am wrong please do correct me.

Yasir, like posted above the max midspan for element is controlled by the maximum deflection acceptable at that point by attached non structural member. What I cann't understand is that why are you checking max deflection at midspan when your checker is asking you to satisfy interms of story drifts?

Link to comment
Share on other sites

sir does that means that this we should not consider even if our deflection is like that much we just go with the delta if its oke then leave whatever the model show. and what about report when we print the report for certain load cases and the values are high does that will not annoy the checker ?

Link to comment
Share on other sites

sir does that means that this we should not consider even if our deflection is like that much we just go with the delta if its oke then leave whatever the model show. and what about report when we print the report for certain load cases and the values are high does that will not annoy the checker ?

For a non-structural member attached as cladding, unless limits or drifits are specified by vendor brochure, you are left with wind code provided limits only as your criteria. You also need to make sure that your wind loads are reasonable. Your loading looks high to me. Plus your are looking at displacements where as limits are imposed for drifts. As long as you are satisfying code specified criteria your checker cant say anything, i still think he wants you to do what I posted above in the pdf.

Link to comment
Share on other sites

@umar I don't think so that checker will ask him to ascertain the effect of story drift on nonstructural member. If his structural system,  which, I think, is comprised of RCC frame, satisfy the the drift limits that will limit, or avoid, the damage to cladding/non-structural-members, he does need to do anything else on these non-structural members. 

 

Yasir could inquire from him about that aspect, to know if he is worried about the damage to these vertical posts, and attached louvers, due to the drift experienced by RCC frame. In any case you can check the strength of these post against the moment and shear that will result from drift. 

 

I think that strength and serviceability limits should be satisfied for these non-structural members, independently of main structural system. It is the mid span deflection due to wind load that also needs attention.

 

The thing you have mentioned refers to the members which are part of a system resisting gravity loads. Code requires us to design these members, meant to resist only gravity loads, for drift inflicted by the members,  part of Lateral load resisting systems, on to them . The box-shaped posts, used in current discussion, only supports louvers.

Link to comment
Share on other sites

@ Yasir, Is the height of your frame(RCC) about 10m ? I am not able to understand the arrangement made at about 5m; it does not look part of main frame, but an arrangement to support door opening.

Link to comment
Share on other sites

sir thanx for the detail comment i was going to write some of your concerns about the limits that sir umer shared above these are there when gravity load or point load is acting and drift the consultant concern for these posts is midspan deflection due to wind load how much they will deflect and what is limit.

 

Sir Zeeshan the height of total frame system is 10 m but there are two floors each with height of 5235 and at mid the RCC element is slab with beam just like at top. 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       