Tributary Area Of Slab On Beam.
Suhail Gul
use the one which is in the attachment ... tributary area at 45 degrees just like in ACI i think in chapter 13...
the one in the other picture giving load on short beam as Lx/3 where as if you do by 45 degree method you get Lx/4 so...there is a difference...I dont know from where you got that image of the loading method....may be from Reynolds book but boy it depends on support conditions and side conditions too....so use 45 degree method otherwise check in reynolds book for more cases..
Formulas in the figure titled 'attached thumbnails' gives the equivalent Uniformly distributed load for computing maximum bending moment, where as the other one is the equivalent UDL for maximum shear.
Bear in mind that the actual loading is triangular, or trapezoidal, depending upon the location of the beam.
Use wlx/3  or W*Lx/6[3-(lx/ly)^2] for computing BM.
i have came across discussion on this topic and it was like this. what u will say abut this discussion is it true or not
Triangular loading on shorter side beams of slab
equivalent UDL
For BM computations w (equivalent) = w*Lx /3
For SF computations w (equivalent) = w*Lx /4
Trapezoidal loading on Longer side beams of slab
equivalent UDL
For BM computations w (equivalent) =( 3-m^2)*w*Lx /6
For SF computations w (equivalent) = ( 2-m)*w*Lx /4
where Lx/Ly=m
Lx= short span of slab
its interesting that the formulas given by zoya for both case of SF computation for both shorter and longer side gives same result as if we solve by actual method of 45degree tributory area also shown in the attached file which suhail has shared.
Triangular loading on shorter side beams of slab  equivalent UDL
Trapezoidal loading on Longer side beams of slab  equivalent UDL
so seniors what u would say??
Use 45 degree to get your tributary Area. Calculate tributary area, multiply by load and divide by length. Thats it.  You don't need to have a forumla.
  • 3 years later...
Just to add what Ayesha said,
I remember way back, that to convert the triangle and trapezoidal loads to equivalent UDL you multiply it by 1.33 or 1.30. As I mentioned refer to Reynold's book, it explains various cases in detail.
Following is an attachment from Reynolds's Reinforced Concrete Designer's Handbook - 10th Edition
59226e3f33d5f_Pagesfrom10th_edition_reynolds_steedman_unpw.thumb.jpg.41858a23e2e6ec12503823d99cd68db9.jpg