Dear fellows,

i have some queries regarding UBC code and and IBC-2003.

I am carrying out study study in Saudi Arabia, Comparative study for Saudi Arabia maximum and minimum earthquake zones based on UBC and SBC(IBC-2003).

As there is no provision for SBC or IBC in Etabs so I calculated base  shear by hand.(see attached files).Maximum earthquake zoning of Saudi Arabia is 2B according to old SBC(was based on UBC) and S1= 12.6 % and Ss = 43.7 % of g, according to new SBC(based on IBC-2003). There is big difference in values of base shear and lateral forces in both codes.

Please check the files attached.

Can any body suggest and guide me about these results.

(Region 4 in SBC = zone 1 in UBC and Region 6 = Zone 2B in SBC)

 

Also

It is right way to calculate Ss=43.7/100  * 9.81 = 4.26 (which is very big) ?

UBC.docx

SBC.docx

Link to comment
Share on other sites

Dear fellows,

i have some queries regarding UBC code and and IBC-2003.

I am carrying out study study in Saudi Arabia, Comparative study for Saudi Arabia maximum and minimum earthquake zones based on UBC and SBC(IBC-2003).

As there is no provision for SBC or IBC in Etabs so I calculated base  shear by hand.(see attached files).Maximum earthquake zoning of Saudi Arabia is 2B according to old SBC(was based on UBC) and S1= 12.6 % and Ss = 43.7 % of g, according to new SBC(based on IBC-2003). There is big difference in values of base shear and lateral forces in both codes.

Please check the files attached.

Can any body suggest and guide me about these results.

(Region 4 in SBC = zone 1 in UBC and Region 6 = Zone 2B in SBC)

 

Also

It is right way to calculate Ss=43.7/100  * 9.81 = 4.26 (which is very big) ?

 

All I can understand from your post is that you are doing a comparison between two codes for Saudi and trying to find out quantitative difference of base shear? Also, I believe you want someone to check your numbers?

 

Before you do that you need to understand the differences between UBC and IBC Seismic Design Philosophy; you aren't comparing apples to apples if you just compare numbers. There is a lot different between two codes. Both codes design to a different Maximum Considered Earthquake (MCE). Considering everything is constant, IBC will give you a higher base shear. Read the attached article:IBC and UBC Comparison.PDF

 

Use the method provided in code to identify your seismic response coefficients. Ss=Ground acceleration at short (0.2 second) period, which will allow you to determine Sms and subsequently Sds. Code outlines the procedure to calculate all these components. I don't know why are you calculating Ss like you did. 

 

Documents attached are result output, and calculation is not attached. Without a calculation, no one knows how you came up with the numbers. My best advice to you, to check your numbers is to compare them with a solved example. You can't go wrong.

Link to comment
Share on other sites

well this is not always true. Last year I did a similar comparative study in Saudi for one of our projects.

 
UBC-97 gave higher base shear due to the fact that the actual calculated base shear exceeds the maximum allowed value that is independent of time period.
Buildings were in moderate seismic zones and the height of building where the actual base shear was less than the max base shear was 16m for concrete and 18m for steel structures.
These buildings were low rise having 3 stories max.
 
In IBC 2006/ASCE 05 maximum base shear formula has T and actual base shear is constant for all heights. That is the reason max base shear governed  upto 14m height of concrete and 12m height for steel structures.
 
In nutshell IBC 2006 gave us upto 64% reduction in base shear magnitude in concrete and upto 56% reduction in steel buildings as compared to that of UBC-97.
Link to comment
Share on other sites

All I can understand from your post is that you are doing a comparison between two codes for Saudi and trying to find out quantitative difference of base shear? Also, I believe you want someone to check your numbers?

 

Before you do that you need to understand the differences between UBC and IBC Seismic Design Philosophy; you aren't comparing apples to apples if you just compare numbers. There is a lot different between two codes. Both codes design to a different Maximum Considered Earthquake (MCE). Considering everything is constant, IBC will give you a higher base shear. Read the attached article:attachicon.gifIBC and UBC Comparison.PDF

 

Use the method provided in code to identify your seismic response coefficients. Ss=Ground acceleration at short (0.2 second) period, which will allow you to determine Sms and subsequently Sds. Code outlines the procedure to calculate all these components. I don't know why are you calculated Ss like you did. 

 

Documents attached are result output, and calculation is not attached. Without a calculation, no one knows how you came up with the numbers. My best advice to you, to check your numbers is to compare them with a solved example. You can't go wrong.

 

The response of Umar Makhzumi is comprehensive, clear and correct.

Link to comment
Share on other sites

The response of Umar Makhzuni is comprehensive, clear and correct.

 

In addition, following should be noted.

It is advisable that all designs in Pakistan adhere to IBC rather than UBC-97, which is now considered defunct.

Use of UBC-97 with latest resistance codes for structural concrete (like ACI 318-05, 318-08, 318-11) and AISC codes with publication dates after 1997 is technically incorrect and must be avoided.

 

I hope that structural design community should adapt to the IBC and the appropriate use of resistance codes.

Link to comment
Share on other sites

 

well this is not always true. Last year I did a similar comparative study in Saudi for one of our projects.

 
UBC-97 gave higher base shear due to the fact that the actual calculated base shear exceeds the maximum allowed value that is independent of time period.
Buildings were in moderate seismic zones and the height of building where the actual base shear was less than the max base shear was 16m for concrete and 18m for steel structures.
These buildings were low rise having 3 stories max.
 
In IBC 2006/ASCE 05 maximum base shear formula has T and actual base shear is constant for all heights. That is the reason max base shear governed  upto 14m height of concrete and 12m height for steel structures.
 
In nutshell IBC 2006 gave us upto 64% reduction in base shear magnitude in concrete and upto 56% reduction in steel buildings as compared to that of UBC-97.

 

 

True, there can be certain cases where UBC gives a higher base shear. However, without knowing basis of study, parameters involved and data points/ no of runs and sensitivity of each parameter quoted results, it hard to conclude. Keeping numbers apart, there are other differences too. IBC considers seismic design category which affects your calculated base shear whereas UBC considers your seismic zone only. While designing a hospital in a lower seismic category, you may end with a higher base shear than for a commercial building with a higher design category, both comparisons being done for IBC.  As I said, it is not an apples to apples comparison, and your results can be different based on what parameters you consider. To me, the whole exercise is pointless, because basis are different. Number crunching.

Link to comment
Share on other sites

  • 2 months later...
  • 2 years later...
  • 1 year later...

Dear All:

[1] Please note that Structural Designers in Pakistan are still using DEFUNCT UBC-97. I am a one person team trying to change this practice.

[2] In addition, by using ETABS, they use UBC-97 and latest ACI & ASCE CODES, which is incorrect.

Link to comment
Share on other sites

On 12/1/2017 at 11:19 AM, zenith.international said:

Dear All:

[1] Please note that Structural Designers in Pakistan are still using DEFUNCT UBC-97. I am a one person team trying to change this practice.

[2] In addition, by using ETABS, they use UBC-97 and latest ACI & ASCE CODES, which is incorrect.

So what you will do,

will you going to change the Pakistan Building Code?

 

Link to comment
Share on other sites

On ‎2017‎-‎12‎-‎03 at 5:48 PM, zenith.international said:

Let's develop a group of like minded Engineers and make a petition to PEC and KBCA and ACEP.

I will lead but but need numbers.

Please get your petition ready and we will support you through our forum.

Thanks!

Link to comment
Share on other sites

I will develop the Text for KBCA bylaws to replace the current clause in Chapter 11 of KBCA by laws. 

 In the mean while need volunteers to develop list of Enginners with email addresses so the revised Text can be sent to them and they Endorse it.

We start with local Bodies, like KBCA and then towards PEC for revising the Building Code of Pakistan Seismic Provisions 2007.

Prof.Dr. Shoaib Ahmad

 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.