Deduction Of Overburden From Bearing Capacity


EngrUzair
 Share

Recommended Posts

Aoa.

 

While designing foundations for building and other structures, allowable bearing capacity is used to calculate required area (spread) of footing. There are two approaches of structural engineers, regarding value of allowable bearing capacity, actually to be used.

 

First approach says that the weights of soil below ground level and the footing concrete must be deducted from the allowable bearing capacity value given in the soil investigation report, to determine net bearing capacity. This net bearing capacity is to be used to be used for calculating footing area required to support the load from superstructure.

 

The second approach, says that NO deduction is required for soil and concrete below ground level, because:

a.   soil investigation is carried out while original soil over burden is in place, and only superstructure load is to be carried out by the foundation,

b.   Allowable bearing capacity given in the soil investigation report is very conservative, as it is commonly calculated by employing a factor of safety of 2.5 to 3.

 

The first approach results in comparatively larger footing sizes.

 

The question is, which of the above two approaches should be followed? And, why (code or some other references)?

Link to comment
Share on other sites

I am aware of both practices. There is another practice of adding overburden in the reported value of bearing capacity (source: wl*l/8).

I am also looking for the answer.

As per my cursory knowledge, it depends on method of the computation of bearing capacity's value.

Need to ask some competent Geo-technical engineer about it.

 

 P.S: Ignore "source: wl*l/8"

Link to comment
Share on other sites

Aoa.

 

Thanks for you responses.

 

@Umar!

 

I haven't read about the second approach in the literature I have gone through so far. However, I have heard some people talking about this approach.

 

@baz!

 

Thanks for apprising about third approach. Although I have seen many soil investigation reports, I haven't came across this type of approach yet..

Link to comment
Share on other sites

  • 1 month later...

All three approaches exist there.

 

First approach deducts over burden ( which is the most common approach) 

 

Second approach is to go straight a way with B.C at that depth, this has many observations and is not practiced widely because

1) Soil has to bear load of super structure along with load of foundation

2) Allowable B.C is calculated on certain assumptions as well which are catred for by placing a factor of safety of 2 to 3. But keeping in view the factor of safety, we calculate size of footing on service load. So factor of safety has already been relied up on in terms of sizing the footings.

 

Third approach is to add up the weight of excavated soil in B.c values. This is generally done for deep excavations like two or three basements. But with that approach geotechnical engineer recommends that excavated surface should not be left open for longer period. If one has excavated the site and there comes a halt in construction after excavation then site must be rechecked by geotechnical engineer before placing of foundation. This is so because soil starts to get relaxed and if cracks get developed then provision of adding up weight of excavated soil does not remain valid.

Link to comment
Share on other sites

W.salaam..

I dont have an article at hand but I have came across multiple geotechnical reports that ask for that.

Basic theory for LRFD design being that factored loads shall meet factored strength. The geotechnical report provides an ultimate bearing capacity with a resistance factor of 0.3-0.6. Structural engineer has to design for all Ultimate Limit States using (0.3 to 0.6)*Ultimate Bearing Capacity. The important thing to note here is that only settlement is a Serviceability Limit State and all other Limit States are ultimate. i will update this post with power point presentation that elaborates the discussion. This is what engineers do in Canada.

Thanks.

Link to comment
Share on other sites

  • 2 months later...

When ever we say Allowable bearing capacity, It can be either Gross allowable bearing capacity or net allowable bearing capacity. And it is the most important thing to decide when to add over burden, when to subtract and when not to. 

More over keep this equation before you 

for equilibrium

q(all.gross) > P/A +Y.Df

where 

q(all.gross) = gross bearing capacity

Y.Df = Backfill load

P/A = Applied pressure

 

q(all.net) = q(all.gross)-Y.df = (P/A +Y.Df) - Y.Df 

hence for equilibrium

q(all.net) > P/A

where 

q(all.net) = net allowable bearing capacity

Y.Df = Backfill load

P/A = Applied pressure

 
So gross bearing capacity is capacity available to bear pressure of existing soil as well as applied loads and net bearing capacity is capacity available to bear just applied pressures because pressure caused by existing soil has already been deducted.

 

Case when NOT to deduct over burden

 

Lets say in my geotechnical report i have been provided by NET bearing capacity of 1 tsf at a depth of 5 ft. Now it means at 5 ft depth, soil is capable to bear pressure of 1 tsf IN EXCESS of existing soil. Because it is NET allowable bearing pressure and pressure of existing soil has already been subtracted/balanced from bearing capacity. Now only extra available bearing capacity is reported as net. The soil can bear 1 tsf of EXTERNAL/APPLIED pressure which includes load of above structure as well as load of footing. Load of footing is also external and applied. In this case, you need not to deduct over burden because over burden is already deducted and you are provided with NET bearing capacity.

But If you have bearing capacity at 5 ft depth but in return you have plan to backfill upto 7 ft, then obviously extra 2 ft soil is applied pressure. which you need to either add in applied pressure or you should deduct it from the bearing capacity.

 

Case when to deduct over burden

But if my geotech report says me that at 5 ft depth, i have 1.25 tsf GROSS allowable bearing capacity. Now it means my soil is capable to bear 1.25 tsf pressure including pressure caused by existing soil. Because it is gross allowable bearing pressure and i have not subtracted pressure of existing soil. The soil can bear 1.25 tsf of total pressure which includes EXTERNAL/APPLIED pressure caused by load of above structure including load of footing, and pressure caused by existing soil . In this case, for the sake of sizing of footing, you need to to deduct weight of over burden soil so that so may find out net bearing capacity available to resist applied load of structure and footing. Note that, after deducting the pressure caused by existing soil i.e. Y.Df = 110*5 = 550 psf = 0.25 tsf, we again get the same 1tsf bearing capacity available for external/applied loads.

 

Case when to ADD over burden

Now Let say you are given with any of capacity. Let say Net allowable capacity of 1tsf at 5 ft depth. But you know that you are not going to backfill the foundation (in case of basement etc), then NOT ONLY this 1 tsf is available for applied pressure but also that 0.25tsf available which was going to be consumed by existing soil backfill. Now you can add this 0.25tsf to your net bearing capacity to get bearing capacity, available for external loads and you need to find out size of foundation according to this available bearing capacity.

Link to comment
Share on other sites

  • 10 months later...

I would like to draw your attention towards cut/fill levels.

 

Footing resting on Fill

 

If we are placing our footing on an area which is in fill than we have "0" ov.burdron pressure in this equation

       q(gross)= qnet +  over.burdon,     hence  q(g) = q(net)

And we need to take the fill pressure while designing the footing.

 

Footing resting on cut

 

If we are placing our footing on an area which is in cut  than we have " ov.burdron" pressure exists in this equation 

       q(gross)= qnet +  over.burdon, hence  we can increase out bearing capacity.

And we need not to take this pressure while designing the footing,because what we have excavated we have put it again,and the difference of pressure will be nothing.

Link to comment
Share on other sites

W.salaam..

I dont have an article at hand but I have came across multiple geotechnical reports that ask for that.

Basic theory for LRFD design being that factored loads shall meet factored strength. The geotechnical report provides an ultimate bearing capacity with a resistance factor of 0.3-0.6. Structural engineer has to design for all Ultimate Limit States using (0.3 to 0.6)*Ultimate Bearing Capacity. The important thing to note here is that only settlement is a Serviceability Limit State and all other Limit States are ultimate. i will update this post with power point presentation that elaborates the discussion. This is what engineers do in Canada.

Thanks.

 

Here is the presentation that highlights the difference between two approaches for foundation design.

 

Thanks.

 

Use of Limit State Design in Foundation Engineering.pdf

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.