What would be the proper choice between shell and frame for modelling 1.2m x 0.6m vertical element? 

 

In a building I am studying expansion joints. All columns are 600mm dia circular. Except some vertical elements 1200x600mm.

 

1) The question is what system for seismic behaviour you would consider as per ASCE? shear wall or frame? 

 

2) How would you model 1200x600 as frame or as shell?

Link to comment
Share on other sites

1200x600mm should be treated as column; It has a noticable weak axis response (espically as other members of LFRS are about same size in one axis).

I don't know about your framing and column count, but % of baseshear resisted by rectangular columns would be greater in one axis and almost equal in other. If you want to get more classy, compare % of base shear distribution ratio between your rectangular and circular columns to get a feel but with the information provided at hand, best bet would be to model it as a frame element. This answers your part 1 too.

Thanks.

Link to comment
Share on other sites

Aoa.

 

Keeping in view ACI 318-05 section 21.4.1.2 for special moment frames, a vertical member with 1200x600mm cross sectional dimension should be treated as a "column". Therefore,

 

1) a "frame' system should be adopted for analysis,

 

2) the 1200x600mm section should be modelled as a 'frame' or 'column'.

Link to comment
Share on other sites

Uzair I know the clause you are talking about. But it is for special moment frames whereas I have ordinary. 

 

Umar, these large rectangular columns attract 70% of base shear when modelled as frames and 95% when shells. What would you do when you have 10mx20m large bulky column? Still model it as frame? Whereas in reality it has continuous support like compression tension couple making the base fixed?

 

I know we can model 200x200mm column as frame and then longer things as shells and then a mass by 3d brick elements. So whats close to reality? 1200mmx600mm vertical element as shell?

Link to comment
Share on other sites

Uzair I know the clause you are talking about. But it is for special moment frames whereas I have ordinary. 

 

Umar, these large rectangular columns attract 70% of base shear when modelled as frames and 95% when shells. What would you do when you have 10mx20m large bulky column? Still model it as frame? Whereas in reality it has continuous support like compression tension couple making the base fixed?

 

I know we can model 200x200mm column as frame and then longer things as shells and then a mass by 3d brick elements. So whats close to reality? 1200mmx600mm vertical element as shell?

I am not sure that why you are getting different % of base shear for case of frame elements and shell elements. The analysis should give you the same results for both cases as stiffenes for frame and shell element wouldn't differ.

In general, the only advantage of modelling shear walls using shell elememts is that you can easily model wall openings and shell elements are much easier to model for a given length of wall compared to frame elements. In this case, I doubt if there are any openings.

Anyhow, Walls have 2D behaviour and Shell or Frame elements should suffice from analysis point of view. Once you get the forces you can resolve them in max compression and tension forces when designing for foundation or reinforcement in walls. This answers your "10mx20m large bulky colum" wall question too. I could see why you are asking this question.1200 x 600 mm columns is not that big.

Thanks.

Link to comment
Share on other sites

Umar, there is a difference between stiffness of shell and a line element due to Poisson ratio although negligible.

 

I am getting higher forces because the line element was pinned and when modelled as shell...it is also pinned but now has 3 pin supports instead of 1 in line...so these 3 pin supports making the shell more stiff at base.

 

PS: This explanation is not mine..so I am not satisfied with this too.. because as I know the lateral force in rigid diaphragm should depend on stiffness of vertical elements and stiffness of line and shell dont differ much so the the base shear in these columns should not jump from 70% to 95%. Agreed. Btw does the above explanation about base fixity has any effect? I dont think so but just asking?

Link to comment
Share on other sites

Uzair I know the clause you are talking about. But it is for special moment frames whereas I have ordinary. 

 

Umar, these large rectangular columns attract 70% of base shear when modelled as frames and 95% when shells. What would you do when you have 10mx20m large bulky column? Still model it as frame? Whereas in reality it has continuous support like compression tension couple making the base fixed?

 

I know we can model 200x200mm column as frame and then longer things as shells and then a mass by 3d brick elements. So whats close to reality? 1200mmx600mm vertical element as shell?

Dear waseem As per ACI code 318-14, Horizontal dimension to thickness ratio is less than 3, so it should be treated as column. In my opinion it should be modeled as frame element

Link to comment
Share on other sites

Well I dont believe in aspect ratios thing. ACI also clearly mentions in this clause commentary that it is the behaviour that determines if its a column or a wall not just merely the aspect ratios. Anyway one good thing to check is the moment diagram.

Link to comment
Share on other sites

Well basically code considers a member as compression member when primary stress is longitudinal compression. The differentiation between column and wall is based on the principal use However code permits walls to be designed using principles stated for column. With that just to differentiate arbitrarily code defines columns basing on aspect ratio. In combination these two aspects support the point of view that member under your consideration should be treated as column and may be modeled as frame. Moreover moment diagram may not be a decisive factor in your case because what i got from discussion your member is a compression member. So the question is how to model that compression member.

Link to comment
Share on other sites

Thanks Imran Zafar, I will study this in detail and will update if I find something new.

 

 

Sir Umar,

unfortunately what we discussed (that shell and frame should give same base shear in those elements) is not matching with my models. I checked models again with Poisson's ratio = 0 so shell = frame stiffness. But still I am surprised to see that those few elements when modelled as lines carry only 329 kN shear and when modelled as shell carry 922 kN shear. What could be the reason?

 

Line elements have one pin support at base. Shell elements have 3 pin supports at base.

 

Now if I change shell pin supports from 3 to 1 (keeping the middle pin support) the shear on shells is almost the same as that of frames. It is now 342 kN (very near to 329 kN of frame elements)

 

So the base fixity is doing something here? What you say?

Link to comment
Share on other sites

Thanks Imran Zafar, I will study this in detail and will update if I find something new.

Sir Umar,

unfortunately what we discussed (that shell and frame should give same base shear in those elements) is not matching with my models. I checked models again with Poisson's ratio = 0 so shell = frame stiffness. But still I am surprised to see that those few elements when modelled as lines carry only 329 kN shear and when modelled as shell carry 922 kN shear. What could be the reason?

Line elements have one pin support at base. Shell elements have 3 pin supports at base.

Now if I change shell pin supports from 3 to 1 (keeping the middle pin support) the shear on shells is almost the same as that of frames. It is now 342 kN (very near to 329 kN of frame elements)

So the base fixity is doing something here? What you say?

There are a number of things that require discussion here:

I am not sure if "Base Fixity" is the right term to use but clearly what is happening here is that with at least 2 base pin supports(the default when we model a wall in ETBAS) the shell elements "behave" as a true wall. Unlike for the case of single pin support where lateral resistance is through moment resistance only and the action is that of a frame instead of a wall.

To explain further, assume a model in which only shear wall is modelled(no other structural elements) by using a single pin node at the base. The structure is unstable by itself and any lateral load would cause the wall to rotate about base. Thus for situations in structural systems where shear walls are modelled using a single pin at base, we are enforcing a "frame action" rather than a wall action. That is why your base shear per support is coming close to that of column but slightly higher, the reason for which is given below in 4th paragraph.

If you increase the number of pin supports at base to more than two, you would not see any significant increase in the amount of base shear attracted by the wall. As already stated this is because minimum 2 nodes are required to enforce wall action any any further increase is meaningless other than offering a more even load for foundation design.

In addition to this, I would also like to mention the case when you modelled a single pin under wall and obtained a slightly higher base shear than that to when columns were modelled (342kN vs 329kN). The reason for this is the reduced length of the beams when walls are modelled result in a slightly stiffer system and increase shear per column.

Thus base fixity means nothing. The real jab lies in how ETABS calculates stiffness of shear walls and frames and interaction of shell and frame elements. What is apparent to me is that shell elements when modelled and meshed represent discrete structures rather than individual component of a structure.

For interest, you should compare the stiffness of single cantilever column to that of a cantilever wall fixed at base. Apply a 1kN load to both and note the deflection. Are results different. I bet they would be. Apparently ETABS might be using some assumptions related to wall geometry to justify a higher stiffness calculation.

Regarding your model, I would still suggest to model vertical elements as columns as your system is way too redundant than a shear wall system; I don't know about column count but naturally your number of columns would be >> than a typical wall system and I believe applying wall provisions in this case would be overkill.

Thanks.

Link to comment
Share on other sites

Thanks, yeah thats a good point about reduced beam length in case of shell element or wall.

 

No I no. of columns is not more than these shell elements. They are almost equal. Ayway I am using frame resisting system but the question now is between shell or frame.

 

For more than 2 supports to capture wall action, let me verify this in a an example.

 

And for a simple cantilever shell vs frame, the result is same. I have done it previously many times, the only difference is that a shell is more stiffer than a frame of the same size because of possions ratio. As for shells flexural rigidity is EI/v instead of EI in case of frames.

Link to comment
Share on other sites

  • 9 months later...

I am facing a similar situation again. What exactly is the difference between multi-storey frame with columns modelled as line element, and the same frame with same sizes with columns modelled as shell elements.

Link to comment
Share on other sites

i have done all the experiments before posting and the results are;

 

we will get the same displacements if we

 

1. model a cantilever column with fixed support

2. model a shell element of same size with pinned supports (more than 1 support will act as fixed) and dividing total horizontal tip load as work equivalent load with poison ratio = 0.

 

 this is logical.

 

now lets move on

 

if we model a frame with columns as line elements, and then replace these columns with shell elements of same size with above assumptions in step 2 we will get different results.

 

reason behind is the joint stiffness where beam frames into vertical elements. to get same results adjust the beam in shell models to the full length of shell elements (making joint more stiff).

 

this is again logical

 

now move to next step

 

replicate these models for 10 stories, you will need to adjust the beams framing into shell elements to get the same results as that of multi-storey plane frame.

go so forth

 

now the problem lies when you actually model a 3d building...with line elements as columns, and then using shell elements as columns of same size. thats where im stuck.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies