My building is in zone 3 and it has a 2 inch expansion joint in it... So my building is divided into two blocks. Now I m worried when my structure will go under seismic excitation, Whether both blocks of structure will behave exactly same and will have same frequency of vibrations or will both of them can move towards each other causing collision.. Maximum story displacement for my structure is 0.81 inch. and I have assigned it value of R as 8.5. So maximum inelastic response displacement will be 0.7 x 8.5 x 0.81 = 4.82 inch. which is more than expansion joint. Both of blocks are NOT SYMMETRICAL. So both may not be having same stiffness. 

Link to comment
Share on other sites

W. Assalam.

 

In principle, in order to avoid pounding effect (collision of the two buildings during an earth quake), you will need to provide an expansion joint that would be a larger than the maximum drift of both the buildings, at the expansion joint location.

 

I have read somewhere (and If I remember correctly), width of such an expansion joint is LESS than the sum of the maximum drifts of the two buildings. I will have to search for the reference, however, to give you exact relation.

 

You may also go through this post http://www.sepakistan.com/topic/1411-expansion-joint/, containing a good discussion as well a couple of nice references on expansion joints.

Link to comment
Share on other sites

Please also read:

http://www.sepakistan.com/topic/109-building-drifts-in-etabs/

http://www.sepakistan.com/topic/1341-ubc-seismic-drift-limits/

Uzair is right. I don't remember exactly but I believe the minimum distance between buildings should be equal to square root of sum of squares of max inelastic displacements of individual buildings. Its is UBC 97. You can find it easily.

Thanks.

Link to comment
Share on other sites

Dear Engr. Waqas, I dont think 2" expansion joint will be sufficient for a building in seismic zone 3. But other things do matter as well for example; how many stories? etc

 

In ASCE/UBC/Australian codes, seismic separation should be SRSS of inelastic displacements. that is delta = [ (inelastic detla of building 1)² + (inleastic delta of building 2)² ] ^ 0.5

 

Remember that these delta values should be at the same level. For example if a building is 9 story high and adjacent building 3 story high. You have to calculate expansion joint at level 3 of both buildings.

 

Ofcourse you need to check expansion joints at all other stories too (Level 2, Level 1 and basements) if displacement on those levels is more than level 3 (due to high seismic weights or anything).

 

Please also remember that usually in softwares you consider X or -X directions for seismic analysis (and Y / -Y)

 

take the max from X and -X and multiply it with Cd/I (for ASCE) or 0.7R (for UBC) to calculate seismic movement of that building. Do this for the second building and then SRSS will give you final value.

 

HTH

Link to comment
Share on other sites

I have once Done this SRSS in previous office when our new building was to built near an existing building. So we did this under the title SEPERATION OF ADJACENT BUILDINGS from UBC97. Now in my case, my maximum inelastic displacement is 5.3 inch at roof. so SSRS gives me required separation 7.5 inches. Now i m worried it will seem weird to Provide 8" expansion joint because between corridors of upper stories etc, how will i cover it. More over, should i also provide expansion joint in footing? 

Link to comment
Share on other sites

No need for expansion joint in footings...But dont consider it final answer..Discuss with others too...

 

Regarding 5.3 inelastic displacement at roof..yes you need 7.5in gap but first ask why 5.3 inch? That means 132.5mm. Improve your framing. Is your building like 120m high? How many stories? And how much is W and base shear in terms of W?

Link to comment
Share on other sites

  • 1 month later...

My building is just two story building in quetta. And I had provided expansion join in footing but this is not working. Footings get over stressed under columns. Increasing size is not working. I ave provided combined footings but still fail. So now i am thinking to eliminate expansion joint from my footings. Can i eliminate it? My main concern is for thermal stresses. When isolated portions from super structure shrink/expand, can footing handle this movement?

Link to comment
Share on other sites

  • 2 weeks later...

There are different recommendations for expansion joints in different books. I have seen no joints up to 200 feet in some text for RCC buildings. Anyways, you can do analysis for thermal differential case and see how much moment gets induced in your foundation.

Visit the link below for information about carrying out thermal analysis.

http://www.sepakistan.com/topic/1367-effect-of-temperature-changes-on-buildings/

Thanks

Link to comment
Share on other sites

  • Moderator

i am told once that no need to provide expansion joint in raft/footing . i provided no expansion joint in raft and provided 2" expansion joint in the building,so parallel columns along the joint were failing the raft in punching.but senior engineer said its ok columns will not punch.

Link to comment
Share on other sites

i am told once that no need to provide expansion joint in raft/footing . i provided no expansion joint in raft and provided 2" expansion joint in the building,so parallel columns along the joint were failing the raft in punching.but senior engineer said its ok columns will not punch.

You should always do your due diligence. Most senior engineers in Pakistan have limited knowledge.

Never listen to such people as they breed ignorance.

Thanks.

Link to comment
Share on other sites

It would depend. Edge columns usually dont have problem in punching (they carry half load as compared to the interior ones). But again there is lot of moment. So it depends upon loading and span. I dont see much problem in edge columns as far as punching is concerned for usual spans and loading.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.