Assalam o alaikum,
Is there any restriction on diameter of shear hoops in seismic zone 4? We can not provide less than 3/8 in stirrups. But for seismic zone 3,4 is there any further restriction regarding size of stirrup? My main concern is to know whether i can use 3/8 in dia stirrups hoops in zone 4 if it is satisfying spacing limits and required shear ratio?
in my case column size is 12x21,
And regarding calculations of my transverse reinforcement, spacing came out 4 inch max.
Now according to 21.6.4.4 of ACI 318-08
I am to provide not less than giver by following two equations
Ash = 0.3*s*bc*fc'/fyt*[(Ag/Ach-1)]
or
Ash = 0.09*s*bc*fc'/fyt
in my case
s = 4 inch
bc = 9 inch for one direction and 18 inch for other
fc' = 3ksi
fyt = 40ksi
Ag = 252 in2
Ach = 162 in2
So in my case
For bc = 18 inch
Ash = 0.9
and
Ash = 0.486
So I need to provide at least 5 legs of #4 stirrup perpendicular to 21 in dimension
For bc = 9 inch
Ash = 0.45
and
Ash = 0.243
So I need to provide at least 3 legs of #4 perpendicular to 12 inch dimension.
baz bhai, am i getting it right?
Is this a MUST check to perform? What If I just provide ratios obtained from ETABS and dont satisfy it?
From Etabs I got much lesser required rations i.e. 2 legged #3 @ 4 inch is satisfying my etabs required ratio. But ETABS MANUAL of concrete frame design CFD-ACI-318-08, Topic 3.4.4.3 says
"The column shear reinforcement requirements reported by the program are based purely on shear strength consideration. Any minimum stirrup require-
ments to satisfy spacing considerations or transverse reinforcement volumetric considerations must be investigated independently of the program by the user."
ACI 318-08 R21.6.4.4 says
"Instead, Eq. (10-5) and (21-4) are required, with the intent that spalling of shell concrete will not result in a loss of axial load strength of the column. Equations (21-3) and (21-5) govern for large-diameter columns, and are intended to ensure adequate flexural curvature capacity in yielding regions."
Waqas!
You should remember that we have to satisfy all applicable DESIGN CODE requirements, while designing a structure. IMO, in case of special moment frames subjected to bending and axial load (required in seismic zones 3 & 4 or SDC D, E & F), ACI 318-08 Section 21.6.4.4 is certainly applicable, and HAS TO BE SATISFIED.
Chapter 29 of PCA Notes on ACI 318-08 contain very elaborate examples on how to make design calculation for earthquake resistant structures. You might like to have a look at Example 29.3 section 5, describing in detail the method of calculating transverse reinforcement (hoops, ties etc.)