Load Cases For Deflection Check
Waqas Haider
Assalam o alaikum,
What are load cases for which i need to check my deflection.
ACI table 9.5 ( b ) there need to check two types of deflections.
i) Immediate deflection due to live load
ii) Total deflection [which is sum of long term deflection due to sustained loads [sustained load means majorly dead load and some portion of minimum live load which is permanently applied]  and immediate deflection due to live load)
And long term deflection can be calculated as immediate deflection due to sustained loads (sustained load means majorly dead load and some portion of minimum live load which is permanently applied) multiplied by 2.
So equation goes some what like this
i) for immediate deflection,
Deflection = immediate due to live
ii) For Total Deflection
Total Deflection = immediate + long term
where immediate deflection due to Live
Long term deflection = 2 x Immediate deflection due to dead             2 is taken for simplicity in case of five years
so
Total deflection = immediate deflection due to Live  + 2 x immediate deflection due to sustained load (dead majorly)
Kindly varify.
You are right, some may take the remaining part of immediate delection(0.75* deflection due to live load) assuming 0.25 sustained load, adding it to long term def.
the equation becomes :
Long term Deflection = factor * sustained load + 0.75* immaediate due to live load
Mohammad