Seismic Drift Procedure For Real Building
mhdhamood
Dear all;
I have prepared some procedures that in need to your evaluation according to your experience judgement.
I am saying that the following procedures that I will mention will be trusted after your comments that agree or disagree.
The procedure:
1. I get results from tables------> story drift as in pict.1.
2. Let us take one floor as a sample.For that floor we read the results of drift in x-direction as the maximum of
    all load combinations's results  that contain earthquake i.e six load combinations as shown in pic.2 .
3. Do the above for y-direction.
4. As a result the for 4th floor; Drift-x = 0.001986 and Drift-y = 0.001812.
5. Now what are the values we get and how to use it. These values coming from ETABS are representing the difference
    in elastic displacement between the floor and the floor beneath or up divided by the floor height
.(Please correct me if I am
   wrong).
6. Now to get the the seismic drift values from inelastic response we multiply the above drift by 0.7 *R .
    As an example let us say R=4.5 , then seismic drift-x =0.00625 and drift-y= 0.0057.
7. These values now are ready to compare with  ACI code limitations, Assuming fundamental period of structure=0.5  second:
     story seismic drift limit =2.5% * story height
8.  As you may see our story drifts either in x or in y are less than 2.5 %.
post-1776-0-42236900-1429599367_thumb.jp
post-1776-0-92450600-1429599369_thumb.jp
Mhdhamood,
The forum already has 2 complete detailed articles with examples that you can follow to confirm your understanding.
Here are the links:
http://www.sepakistan.com/topic/109-building-drifts-in-etabs/
http://www.sepakistan.com/topic/1341-ubc-seismic-drift-limits/
Dear Mr Umar;
I have read but here I see a difference in the two articles ;
Your article says that use for calculating seismic drift the ultimate load combinations from earthquake (three ones combine Dead+Live + spcx, spcy,spcxy and the other three that combines Dead+Spcx,Spcy,Spcxy)
But Mr Waseem says that using only single load cases SPCX  and SPCY....
which to follow ??
Strength design load combinations should be used to calculate the drift. Analysis should take into the account the reduction of stiffness of structural members, as well as, the effect the effect of gravity load acting on deformed shape ( second order analysis).
You can check the drift only against  against E. The difference is negligible for most of the structural configurations.
  On 4/23/2015 at 5:03 AM, mhdhamood said:
Dear Mr Umar;
which to follow ??
Mhdhamood,
For both cases, the factor with E is 1.0. It wouldn't make any difference.