New Column Dowels To Be Grouted Due To Wrong Layout????


RASHEED
 Share

Recommended Posts

Dear Seniors,

One of our running projects has layout problem in which columns are out of 10 inches from center line.We need to adjust it as we have to install steel shed above it.Now there are two options,either we have to dismantle the footings or we have to drill holes and grout new dowels with chemicals.Now the problem is that what should be the depth of drill and if we drill hole then hook (development length) can not be provided.

So please give me suggestions based on your experience.We are using 20 mm dowels and axial load is 146 kip.

 

Thanks! 

Link to comment
Share on other sites

This is anchorage to concrete problem (i think, other please confirm) There are many industry post-installed anchors companies like Hilti which provide their own software to calculate these things. Check on Hilti website.

Link to comment
Share on other sites

Rana Waseem bhai we grout anchor bolts in already existing concrete section for installation of steel structure but i was not sure about reinforcement steel whether code allows the grouting of new dowels of columns or not??? 

 

Thanks!

Link to comment
Share on other sites

The best option is Hilti. If there is steel shed then do not use normal drilling. As there will be severe lateral loading due to wind. Ask Hilti, they are costly, but they provide very good and reliable solution as in Lahore on all roof top towers, normally hilti solution is applied.

 

Thanks

Link to comment
Share on other sites

Rasheed,

If the only problem you are asking about is how to anchor the dowels, you may contact Hilti (as you have already been correctly advised by others) for necessary advice as well as execution of job.  It is not a new technique, and is being commonly used all over the world, in connection with strengthening and retrofit of concrete structures.  There is no harm in using it, provided it is designed and executed by a specialist firm (like the one mentioned above).

 

You should however be careful that by relocation of column, column footing will become a bit eccentric, and may require rechecking to see it remains sufficient for the new situation or not. 

 

However, if you need a bit detailed advice, you will have to share some more details regarding your structure and extent of problem, e.g.,

- What type of structure it is? All RCC or partially concrete and partially structural steel? in what proportions?

-Total number of storeys,

- upto which level work has completed?

- what is the actual bay spacing in both direction?

- how many columns are causing problem?

- What other options you are thinking of?

 

 

Regards

Link to comment
Share on other sites

My 2 cents- Hilti is your best bet. But you need to pick the right anchor bolt out of their catalogue and tell them which one would work for you. When you are doing that, please make sure that you consider group effect factors, sustained load factors and everything that is written in the foot notes.  Also, recheck your base-plate once you have confirmed number of Hilti bolts required and their pattern. 

 

Thanks.

Link to comment
Share on other sites

Uzair bhai ,

Actually this is one storey steel shed structure in Lahore column size is 15 x 15 inches,concrete used is 2500 psi and reinforcement steel is 20 mm diameter.Column spacing is 20 ft ,height of column is 6ft and axial load applied on column is 146 kip.

 

i am afraid of neglecting the hook (development length) at the bottom of column as we can insert only straight dowels.

 

Thanks!

Link to comment
Share on other sites

Uzair bhai ,

Actually this is one storey steel shed structure in Lahore column size is 15 x 15 inches,concrete used is 2500 psi and reinforcement steel is 20 mm diameter.Column spacing is 20 ft ,height of column is 6ft and axial load applied on column is 146 kip.

 

i am afraid of neglecting the hook (development length) at the bottom of column as we can insert only straight dowels.

 

Thanks!

 

Even if you provide a straight bar, all you need to check is that your bar develops greater than 146 kips of axial load + tension due to moment. If you don't want to use Hilti, use epoxy, drill the bars, check the epoxy-steel ULS, Concrete Breakout of Dowel Group and finish your design. Why are you afraid of neglecting the hook. Design for what you provide. Period.

 

Thanks.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       