Enlarging Column Necks To Overcome Punching Of Mat


mhdhamood
 Share

Recommended Posts

Dears;

I had a problem in a MAT foundation which is; in a part of the Mat there are two high loaded columns , that create a problem of Punching.

But I cant go in depth of the Mat, so I suggest to enlarge the column neck( The column between the slab on grade and the Mat) which is 0.5 meter in height. That solved the problem.The following questions now I have :

a. Do u agree with me????

b. I didn't design this part of column instead I reinforced it as the steel ratio of the above column. The reason that I didn't design it , is that I enlarge it around the center of the above column so no eccentricity . Do u agree??

c. And how about if it was enlarged eccentrically, Shall I add the Moment from eccentricity to the moment from analysis of the bottom of the above column and design this neck??

Link to comment
Share on other sites

a. yes I agree with you

 

b. It might be SAFE, it might not. depends on the moment diagram which depends on the base fixity (pin or fixed). You must design it properly. If this is an interior column then it should be okay (only P and no M).

 

c. If it was enlarged eccentrically, yes you have to account for the moment M = P.e 

Link to comment
Share on other sites

Just one thing I want to add that if this is highrise building then you need to check the axial forces in the adjacent beams if you increase it eccentrically and if there are some grade beams. It will not effect in all cases but better to check. ;

 

Secondly if you increase it eccentrically then  take care how you will continue the reinforcement from this column to above column as everything depends upon the reinforcement. and in this case you need to model slab on grade and check the inplane stresses if there is soil outside because your total burried area will act as one unit

 

One last important thing, you said the column creating problem in punching and when you increase size it is solved. you can not suddenly increase the size in that small length too much. You need some curtailment for column size. For example if the column above slab on grade is 300mm in diameter then you can not provide 600 mm dia below slab on grade. So please take care of this.

 

These are just my opinions anybody can comment of not agree...... :)

 

Thanks

 

Muneeb

Link to comment
Share on other sites

mhdhamood,

 

IMO, by increasing column dimension in-between the slab-on-grade and the mat foundation, you are actually increasing the mat thickness, which is otherwise needed to account for larger punching. 

 

I would (in case mat foundation is yet to be poured), treat the 'enlarged column neck' and the mat portion exactly beneath it, as a single mat (of thickness equal to sum of normal mat thickness and 0.5 m i.e thickness of 'enlarged column neck') and will provide reinforcement as per requirements of larger mat thickness. This concept is similar to what has been discussed in following thread: (http://www.sepakistan.com/topic/1689-drop-in-mat-foundation/ )

 

BTW... (1) How are you analyzing & designing the mat foundation? Using some software (CSI SAFE etc.) or manually?

           (2) Has the mat foundation already been poured, or is yet to be poured?

Link to comment
Share on other sites

Thanks a lot to all;
Exactly I enlarged the section from 1.5*0.4 to 1.5*1.5 meter at the neck.
According to the development length of the steel in the column neck to be achieved I will make a hook entering into the slab on grade so I think no problem here 

Muneeb Badar

You said I cant increse it too much please can you interpret why ??


 

EngrUzair
1. Using SAFE.
2. Not executed .
Is your solution valid for my case .?
Link to comment
Share on other sites

Dear

 

The reason is when we suddenly increase the size of column for example from 600 to 300, the forces accumulated at these locations. Actually at each joint the lateral forces normally distributed to adjacent members and also to the below columns. If you suddenly reduce the column size there are much chances of improper stress/forces distribution. So a gradual change is required.

 

Secondly in your case you are suddenly increasing the size at Slab on Grade level. This situation is much more complex. Your structure in soil (structure from slab on grade to foundation level) act as one unit. It means there will be much inplane shear force at slab on grade level. Your complete structure will vibrate starting from slab on grade not from foundation as you provided much thicker columns below slab on grade and made this portion rigid. If you increase the size and do not model slab on grade, I think it will not be good. You can model slab on grade and check the inplane forces distribution at slab on grade level. In this case you can be sure that increasing the column size is affecting or not.

 

This is my concept, anybody can disagree........ :)

Link to comment
Share on other sites

mhdhamood,

 

Since you have increased the column thickness in one direction only, my proposed solution may or may not work in the present case. You will have to verify it, by treating the 'enlarged column neck' as the part of mat footing.

 

In order to deal with punching shear, you normally need to increase shear perimeter 'bo'. This may be done either by increasing thickness of footing (more common and simpler), or by increasing the column size.

 

I was talking about the first option (increasing mat thickness locally), whereas you are tackling the problem using second option (increasing column size).

 

If you are interested in using locally increased footing thickness (instead of increased column size concept),  you may do it  easily in SAFE along with proportioning of required reinforcement.

 

Regards.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies