congbui93
 Share

Recommended Posts

Hi, I am designing a building follow ACI 318. In designing slab, I used equivalent frame method. Now i am stuck with calculate the column strip width. May may you help me to find out the column strip width of line 3. It should be 8/2 m or 4.8/2 m, thank you so much! 

 

the plan is attached below.

post-2434-0-44514200-1444610963_thumb.jp

Link to comment
Share on other sites

With reference to ACI 318-08 Section 13.2.1, column strip width is dependent on the dimensions of the two slab panels, present on two sides of the column line.

 

For line 3, two slab panels exist for each line portion;  one of the size 8000 x 8700 (upper side slab) and second of size 8000 x 4800 (lower side slab).

On the first (upper) slab side, column strip width shall be 0.25*(minimum of 8000 & 8700) = 0.25*8000 = 2000. Whereas, on the second panel side, required column strip width will be 0.25*(minimum of 8000 & 4800) = 0.25*4800 = 1200. Total column strip width for line 3, will therefore be the sum of of these two strip widths = 2000+1200 = 3200.

 

HTH.

Link to comment
Share on other sites

With reference to ACI 318-08 Section 13.2.1, column strip width is dependent on the dimensions of the two slab panels, present on two sides of the column line.

 

For line 3, two slab panels exist for each line portion;  one of the size 8000 x 8700 (upper side slab) and second of size 8000 x 4800 (lower side slab).

On the first (upper) slab side, column strip width shall be 0.25*(minimum of 8000 & 8700) = 0.25*8000 = 2000. Whereas, on the second panel side, required column strip width will be 0.25*(minimum of 8000 & 4800) = 0.25*4800 = 1200. Total column strip width for line 3, will therefore be the sum of of these two strip widths = 2000+1200 = 3200.

 

HTH.

Hi EngrUzair, I don't understand the way you chose column strip width. Why can we add 2000 and 1200 together to be the column strip width? May you explain a little bit more for me.

In my opinion, As 0.25*4800=1200 is the smallest number so the column strip width on each side should be 1200. Therefore, the column strip width is 2400. Is that right? 

Link to comment
Share on other sites

congbui93,

 

See the attached images. These have been taken from chapter 20 of PCA Notes on ACI 318-08, dealing with design of two way slabs using Equivalent Frame Method. First image shows the width of Column Strips, for both interior and exterior frames, when the length L2 is less or equal to length L1 of the slab panel. Whereas, the second image indicates the column strip widths for the SAME LINE, when the length L2 is  equal to or greater than length L1 of the slab panel.

 

post-1539-0-23170400-1444672110_thumb.jppost-1539-0-50486200-1444672127_thumb.jp

 

Moreover, procedure for analysis of two way slabs (both without and with beams) using Equivalent Frame Method, has been explained in detail, in Examples 20.1 and 20.2 of the PCA Notes.

 

Regards.

Link to comment
Share on other sites

Column strip width for Line B = L2 / 4 + L3 / 4

 

Column strip width for Line 2 = L2 / 4 + L2 / 4

 

Dear EngrUzair,

 

For Line B, If we choose 

""Column strip width for Line B = L2 / 4 + L3 / 4"

so the width of each side of the column will not be equal. Does it violate the requirement from the code?

 

"A column strip is a design strip with a width on 

each side of a column centerline equal to the lesser of 0.25ℓ2
and 0.25ℓ1. A column strip shall include beams within the 
strip, if present"
 
Does the code require the width on each side must be equal? .I don't know weather I understand the code properly or not?
 
For Line 2, If we choose
"Column strip width for Line 2 = L2 / 4 + L2 / 4"
Why don't we consider L3 since L3<L2 ?
 
Finally, thank you again for your help and enthusiastic. 
Link to comment
Share on other sites

congbui93,

 

I have tried to search an example, involving the design data similar to your problem, but was unable to find it. May be someone else, here on the forum, able to point to some definite source in this regard.

 

The answers to your questions given below, are based on ACI code basics and my understanding of their intent.

 

For Line B, If we choose

""Column strip width for Line B = L2 / 4 + L3 / 4"

so the width of each side of the column will not be equal. Does it violate the requirement from the code?

 

"A column strip is a design strip with a width on
each side of a column centerline equal to the lesser of 0.25ℓ2
and 0.25ℓ1. A column strip shall include beams within the
strip, if present"

 

All the examples, i have come across (Including those given in PCA Notes), use same width on each side of column line. As such, width of column strip should be equal on each side. Moreover IMHO, keeping in view basic intent of the code (i.e., using the Lesser of the spans for each slab panel, for column strip stiffness calculations), SMALLEST span of the two adjacent slab panels SHOULD BE USED for calculating the width of column strip for their common column line.

 

In line with above argument, width of column strip for Line B should therefore be equal to" L3 / 4 + L 3/4". 

 

Does the code require the width on each side must be equal?

 

IMO, yes.

 

For Line 2, If we choose
"Column strip width for Line 2 = L2 / 4 + L2 / 4"
Why don't we consider L3 since L3<L2 ?

 

You are right. We must consider lowest spans for the common column lines, in order to be on safer side.

 

In the end, following are the column strip widths, IMO applicable to your frame:

 

Column strip width for Line B = L3 / 4 + L3 / 4

 

Column strip width for Line 2 = L2 / 4 + L2 / 4

 

 

Regards.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.