Axial Load In Beams From Temperature Too High
mhdhamood
Engineers;
I have a big question!!!!!!
when I put the thermal load on slabs , I have found the axial load in the beams is increased for intersting values like 1000 kn why its too much.
Then the beams now may not be treated as beams since the axial load more than the 0.1AFc permitted by code. Do I have to design it as columns?
Assuming you got right values of axial forces, the beam theory is not applicable in this case.
You need to design your member for combined effect of axial and bending stresses.
You have not mentioned the nature of axial forces; they should be tensile forces.
Yes Shaker you are right. I have done this in a project intensely (although i believe the temperature values we apply in ETABS are unrleastic for example delta T=20-30C which is too high in my opinion). Anyway we used the same values.
Yes tension, compression force will be so high. Dont forget the compression, if you are designing for 1000KN tension then also design for 1000KN compression.
The easy method is to define these beams as columns in ETABS (P-M-M) design instead of just flexural design as in beams.
As Mr. Baz pointed out, these will be designed for combined axial and flexural loads.
Another easy thing is to design for flexure only and then add area of steel for axial force which T=Ast.fy.phi (This will give more steel as compared to combined axial+flexural design). A conservative approach (A lazy person approach).
So far so good for strength design.
But when it comes to cracking and serviceability design, for example imagine above ground huge water tanks with these axial forces, life does not look so easy in that case. :P
THANKS ENGINEERS;
I WILL SAY WHAT WE DO (MAY BE OUR APPROACH IS CONSERVATIVE):
1.IS ASSIGNING TEMPERATURE OF 25 C ONLY TO THE SLABS (NOT TO COLUMNS, SHEAR WALLS AND BEAMS) .
2.THE STIFFNESS MODIFIERS FOR THE SLAB M11=M22=M12=F11=F22=F12=0.25 (HERE THE NEW THING THE F11,F22 AND F12 MODIFIERS, IN THE MODEL WITHOUT TEMPERATURE NO SUCH MODIFIERS , I AM SURPRISING HERE BECAUSE THESE IN PLANE  MODIFIERS  WILL REDUCE THE EFFECT OF EARTHQUAKE SOMEWHAT, SO IT IS ACCEPTABLE TO USE THEM IN THE SAME MODEL TO CHECK AGAINST EARTHQUAKE?).