Use Of Mass Source Command In Etabs
haro0n
  On 10/28/2018 at 3:09 AM, Ayesha said:
@NMN ASCE 7 says to use 20% of any snow load greater than 30psf as seismic weight. For Canadian Code, you will need to see your local jurisdiction code. If the code doesn't says anything about it, you can use ASCE 7 clause and include the snow load.
This all depends how you have defined the loads. Some people differentiate between dead loads by creating a dead load case and a super dead load case. Other don't. So go with the option based on your loads definitions.
I have seen 25% snow load somewhere but you should check this for Building Code of British Columbia as I see you are working in UBC.
  • 2 months later...
Sustained is generally defined as something the structure would "always see". For process industry structure, sustained load is the load due to operation of the plant (Dead, Pipe Operating, Guide, Anchor) and transient would be wind and seismic.
To answer your question, live load is never sustained. Its time bound by definition and its load factor represents that statistical probability of occurrence. So you should never classify a live load as sustained load unless specified otherwise by the Code or Client Specification that you are using.
Hope that helps.