Jump to content
  • Welcome to SEFP!

    Welcome!

    Welcome to our community forums, full of great discussions about Structural Engineering. Please register to become a part of our thriving group or login if you are already registered.

Thermal Design


mhdhamood
 Share

Recommended Posts

There is no such thing as thermal design in ETABS. You have to use other softwares for finite element analysis for thermal stresses.

 

For the usual design to take into account the temperature loading, don't use rigid diaphragm or it will take all the forces from T.

 

Use usual modifiers and make a load case of T. Then you can always use minus and plus sign in combinations.

 

Use load combinations as per ACI. T comes with 1.2 factor like dead load.

 

Just make sure put reinforcement in beams like in columns. Equal on all faces.

 

And the fun part, let me know how you calculate the crackwidth with P and M-M at service level. If you can't find let me know then.

 

Good luck!

Link to comment
Share on other sites

Thanks Waseem; let me say what we ordinary do then if wront then please coorrect 

What we do in ETABS is :

1. We use ETABS for the effect of temperature on columns and walls and foundations.

2. In ETABS model the modifiers will be : 0.35 beams, 0.7 columns and walls (0.35 if cracked), and m11=m22=m12=f11=f22=f12=0.25 for slabs. 

3. we assign temperature to all elements(columns beams slabs).

4. In addition to load combinations.

 

Now in Safe for slabs design :

1. the modifiers we enter are 0.35 beams, 0.7 columns and walls (0.35 if cracked), and m11=m22=m12=f11=f22=f12=0.25 for slabs.

  So here because we put modifiers to elements, we need another file for slab other than the one we use for deflection and earthquake +gravity laods design .

2. the temperature is assigned to slab.

3. In addition to load combinations.

 

The fun part that you mentioned I dont know , so please help!!

regards our great engineer

Link to comment
Share on other sites

  • 7 years later...

In these environs, only if a building is unheated (eg. some warehouses, parkades, etc.) nearly all buildings are heated in the winter and cooled in the summer. Thermal change in dimensions is normally accommodated by construction details at the time of construction. Once a building is enclosed, there is very little thermal movement.

Link to comment
Share on other sites

  • 1 year later...
  1. Define the Building's Thermal Loads in ETABS:

    • Start by defining the thermal loads that your building will encounter. These include solar radiation, internal heat gains, and external temperature variations.
    • In ETABS, go to Define > Load Patterns, and create new load patterns for each type of thermal load (e.g., solar, internal).
  2. Assign Thermal Loads to Elements:

    • Assign these thermal loads to relevant structural elements (walls, floors, roofs) by going to Assign > Loads > Surface Loads or Assign > Loads > Frame Loads.
  3. Adjust Material Properties for Thermal Analysis:

    • Ensure that the material properties reflect thermal characteristics. This involves setting thermal expansion coefficients and heat capacities. Go to Define > Material Properties, and adjust these settings accordingly.
  4. Element Modifiers for Accurate Analysis:

    • Adjust the element stiffness and strength modifiers to account for the effects of thermal loads. This is crucial for an accurate representation of how the structure behaves under thermal stress.
    • In ETABS, use Assign > Frame > Frame Property Modifiers or Assign > Shell > Shell Property Modifiers to tweak these values.
  5. Thermal Load Combinations:

    • Create load combinations that include thermal loads. Go to Define > Load Combinations, and include the thermal load patterns you defined earlier. This helps in evaluating the structure under combined load effects.
  6. Run the Analysis:

    • Perform the analysis in ETABS to understand the thermal effects on your structure. Review the results for any significant stresses or deformations caused by thermal loads.
  7. Thermal Effects on Foundation - SAFE:

    • Export the thermal load effects to SAFE for foundation analysis if needed. This is particularly important for understanding how thermal expansion and contraction affect the foundation.
    • In SAFE, apply the thermal load effects to the foundation elements and run the analysis to ensure stability and performance.

Remember, precise Construction Estimating must consider thermal loads to ensure the building's safety and comfort. This approach not only enhances the building's performance but also provides a comprehensive cost estimation.

Feel free to reach out if you need more detailed steps or examples. Happy designing!

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.