using staad foundation advanced, I designed a strap footing for two eccentrically loaded columns(offset of left column=-600mm and offset of right column=600mm) of one bay, 3 storey building with grid spacing of about 14 ft in x direction and 12 ft in y direction. The dead load was about 300kN and live load was about 60 KN and earthquake load was about 40 KN in -y direction with moment about z axis 25 KNm. soil bearing capacity was 150 KN/m^3. I used the load combination 1DL+1LL and 1DL+0.8LL+0.8EL. strap beam was in x direction. I got footing size 1.75mx1.75m. footigg thickness 200mm. no of 12mm bars in x direction=6 and no. of 12mm bars in z direction=23. I got doubly reinforced strap beam with 0.53m depth and 9 inch width. bottom reinforcement=3 no. of 12mm bars top reinforcement=6 no. of 16mm bars. And for shear reinforcement it says:"Since nominal shear strength of concrete is greater than maximum shear force, shear reinforcement is not required". I just want to know are the results I got practical or is it likely that I had made some mistakes. I have doubt whether the following result in right or wrong: the vast difference of reinforcement in x and z direction which are 6 and 23 no. of 12mm bars respectively for 1.75mx1.75m footings. and another doubt is requirement of no shear reinforcement in strap beam. Please help me!
IMO, you must check & verify your design through manual calculations.
Following links provide procedure and examples, for designing of strap footings manually:
1. Strap Footing- Shallow Foundations.pdf
2. Special Footings and Beams on Elastic Foundations.pdf
3. Strap Footing Design.pdf
one of my friends told me that the width of strap beam should be greater than the column width. I don't know on what basis he said that. I don't think its true. I have designed a strap footing of width 9 inches and depth 22 inches. Do dimensions of  my strap beam goes against any code? Or I can  design the strap beam just as other beams in superstructure such that B/D is not less than 0.3.
Yes, your friend is right. It is preferable to use a beam width, about 6 inch larger than the column. It permits easy placement of column and strap beam bars at the junction of the two structural members, without interference. This extra width of strap beam also serves as a support for the column form work later on.
Strap beam is also designed like other beams. For proper transfer of loads, its width however should not be less than the width of columns to which it is connected.
Strap beam can be designed a normal beam taking negative moment at mid span. They are generally not designed to take soil reaction and are separated by a flexible layer from soil. You can read for example in Nilson book about the design guidelines.