I have observed few issues while getting the design results of reinforced concrete members from ETABS (v 9.7.4). I wanted to share this issues with you and get your input and observation on it.

  • ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.
  • If your model has lateral loads, ETABS will give you design moments in column irrespective of its status as braced or un-braced as per ACI 318 criteria. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.
  • ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

    Method A gives lower T and higher V, so FEMA 451 has advised not to use the value of time period less than this value even if rigorous analysis gives a lower value.

    I have seen the results where Etabs have use the value of time period less than Ta; in-fact as low as 0.5Ta, which can increase the base shear two times.

Link to comment
Share on other sites

  • 2 months later...

1

On 5/1/2016 at 2:26 PM, baz said:
  • ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

Astounding observation. Just to add my 2 cents that in exterior columns, minimum e does not govern. For interior columns it is always good idea to design columns for minimum eccentricity. Yes this is conservative and depends on the choice of designer.

 

2

On 5/1/2016 at 2:26 PM, baz said:
  • ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of column, if ETABS has included sway moments.

Even if the structure is braced, magnification factors will be so small that they will not matter much.

 

3

On 5/1/2016 at 2:26 PM, baz said:
  • ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.
     

See discussion below

Link to comment
Share on other sites

  • 2 weeks later...
On ‎7‎/‎27‎/‎2016 at 8:42 AM, Rana said:

Astounding observation. Just to add my 2 cents that in exterior columns, minimum e does not govern. For interior columns it is always good idea to design columns for minimum eccentricity. Yes this is conservative and depends on the choice of designer.

According to the section 10.10.6.5 and its commentary (of ACI 318-08), we do not need to use minimum eccentricity if there are negligible second order effects.   

Link to comment
Share on other sites

  • 4 months later...
On 5/1/2016 at 2:26 PM, BAZ said:

I have observed few issues while getting the design results of reinforced concrete members from ETABS (v 9.7.4). I wanted to share this issues with you and get your input and observation on it.

  • ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.
     

Do you mean "There is no need to use the value of time period that is LESS than Ta" or "NOT LESS than Ta"?

 

As you quoted FEMA 451, it says

Ta is lower-bound limit (more conservative for base-shear as T-computed would be higher)

CuTa is the upper-bound limit (can be ignored for drift calculations)

 

But,

 

There is no guidance on if T-computed is less than Ta, not even in ETABS manuals. All the documents highlight the upper limit but not the lower one.

For example, consider a bearing wall building, (density of walls/floor is large), T-computed is ~ 0.10s, however Ta=0.5s; huge difference.

ETABS only checks the upper limit (lets say 1.0s) and not the lower one and selects 0.10 automatically and calculates base shear for this T.

 

However, if I am getting you right or as per; 2009 NEHRP Recommended Seismic Provisions; Chapter 4, page-41, it says;

if T-computed is less than Ta, then use Ta.

https://www.fema.gov/media-library-data/1393888487069-c071850c3050c34da135376baa478a1b/P-752_Unit4.pdf

Please shed some light on this issue.

 

Link to comment
Share on other sites

There is no lower limit for T but there is an upper limit for Maximum V, so even if the time period calculated by ETABS is significantly lower than Ta, code provisions for maximum base shear would govern and the calculated value of T would be ignored.

Similarly, no vertical distribution of force would take place for a small time period hence your design would still be in reasonable FOS limits.

Link to comment
Share on other sites

4 hours ago, Saad Pervez said:

Similarly, no vertical distribution of force would take place for a small time period hence your design would still be in reasonable FOS limits.

Does vertical distribution depends on time period? It must depends on weight participation and stiffness of floors.

Link to comment
Share on other sites

12 hours ago, Engr Waqas said:

Does vertical distribution depends on time period? It must depends on weight participation and stiffness of floors.

UBC97 1630.5: Concentrated force at top, Ft, becomes zero if time period is 0.7 seconds or less. My statement was not 100% correct. Apologies.

Link to comment
Share on other sites

  • 2 weeks later...
1 hour ago, BAZ said:

 

I meant that.

Wow. But there is no clear reference for this in ubc or asce. I got the sense and could save some structures from over-design but would be very difficult to convince authorities without a clear overt, explicit reference to building codes.

Link to comment
Share on other sites

I have another point,

 

Quote

The period of formulas in the 1997 Uniform Building Code (UBC1997), the 1996 Structural Engineering Association of California (SEAOC) recommendation...are derived from those developed in 1975 as part of the ATC3-06 project [Applied Technological Council (ATC) 1978] largely based on periods of buildings measured from their motions recorded during the 1971 San Fernando earthquake.

Goel and Chopra 1997 [1] developed improved empirical formulas to estimate the fundamental vibration period of RC moment resisting frames (MRF) buildings for use in equivalent lateral force analysis specified in building codes using motions of many buildings recorded during earthquakes.

The data used in [1] have been combined from the motions of buildings recorded during the 1971 San Fernando, 1984 Morgan Hill, 1986 Mt. Lewis and Palm Spring, 1987 Whitter, 1989 Loma Prieta, 1990 Upland, 1991 Sierra Madre and 1994 Northridge earthquakes

(Source: http://www.tdmd.org.tr/TR/Genel/pdf/TDMSK010.pdf)

Lower bound and upper bound limits of regression analysis are given as in building codes.

 

More exact solutions (such as in analytical models) give higher T than Ta due to absence of partition and infill walls etc. But my concern is for buildings having large shear walls areas such as tunnel construction, very very dynamically stiff (e.g. 0.1s). In such cases (T-computed < Ta) and as mentioned by following paper, we should not use Ta (as per discussion in posts above) and should use T-computed.

Paper can be found here: http://erolkalkan.com/Pubs/12.pdf

Quote

As is observed from those figures, the obtained finite-element analysis results significantly differ from the code-referred values...The significantcant deviation between current code given formulas and finite-element analysis leads to intolerable errors for the dynamic parameters and corresponding design loads.

Also see this: http://www.sciencedirect.com/science/article/pii/S1687404815000565

Link to comment
Share on other sites

I think both ETABS and UBC 97 provisions are correct.

As ETABS completely follows UBC97 therefore only UBC's provisions are elaborated below.

UBC seismic design philosophy limits the minimum time period (in the form of maximum base shear ) to Ts (UBC response spectrum) which is equivalent to Cv/2.5Ca.

For elaboration ,

V=CV.I.W/R.T

Substitutue T=Ts=Cv/2.5Ca in above eqn

therefore 

V=(CV.I.W/R)X(2.5Ca/Cv)

i.e V=2.5Ca.I/w (the maximum base shear that ETABS and UBC97 uses)

Therefore time period regardless of its shorter value below Ta cannot be lesser than Ts which is in contrast with UBC97 provisions that are inherent in ETABS.

However, analysis indicating time period lesser than Ta indicates a over stiff/over design structure, therefore it is recommended to maintain a natural period closer to 0.1x (no of floors).

 

 

 

 

Link to comment
Share on other sites

1 hour ago, Syed Umair Haider said:

I think both ETABS and UBC 97 provisions are correct.

As ETABS completely follows UBC97 therefore only UBC's provisions are elaborated below.

UBC seismic design philosophy limits the minimum time period (in the form of maximum base shear ) to Ts (UBC response spectrum) which is equivalent to Cv/2.5Ca.

For elaboration ,

V=CV.I.W/R.T

Substitutue T=Ts=Cv/2.5Ca in above eqn

therefore 

V=(CV.I.W/R)X(2.5Ca/Cv)

i.e V=2.5Ca.I/w (the maximum base shear that ETABS and UBC97 uses)

Therefore time period regardless of its shorter value below Ta cannot be lesser than Ts which is in contrast with UBC97 provisions that are inherent in ETABS.

Dear Umair, I understand what you said, but, that is only one of the condition I asked about (see below). Ok let me put this in following way;

lets call T-computed simply as T, there are following 4 cases;

a. T < Ts < Ta

b. T > Ts but < Ta

c. T > Ta but < CuTa {not my concern}

d. T > CuTa {not my concern}

Now lets focus on condition a & b; Let's say; Ts=0.3s and Ta=0.7s

Condition a

Assume T=0.1s which is less than both Ts and Ta

In order to jump to V, we need to first set the time period.

a1. If we use Ts, then obviously maximum base shear would govern. This is what you are referring to.

a2. if we use Ta (which is higher than Ts), base shear would be less than Max. V so we get some saving.

Now the question is what T you'd use? Ts or Ta?

As per FEMA (moment frame example) use Ta.

As per research papers I have mentioned for tunnel construction you should use actual T (or in other words Ts as Max V would govern, as you rightly pointed out).

 

Condition b

Assume T=0.5s which is more than Ts but less than Ta.

Still, if we go with FEMA approach, we should use Ta which will give us lesser base shear. And use of actual T would give us higher base shear.

 

So the question remains, what value of T to be used?

Quote

However, analysis indicating time period lesser than Ta indicates a over stiff/over design structure, therefore it is recommended to maintain a natural period closer to 0.1x (no of floors).

0.1 x (no of floors) is for certain moment frame buildings as per ASCE 7-10 seismic design examples book (example 17), that might not be correct for buildings with large no/area of shear walls. Anyway, the intention, as i see, is to use approximate method (Ta) if analysis T is less than Ta, which is in-line with what Baz said. However, after going through the above research papers, I am again inclined towards using T from analysis instead of Ta for such buildings. For moment frames, yes we could use Ta.

Link to comment
Share on other sites

  • WR1 pinned and featured this topic

My initial post was to point to fellow engineers that one must look at the value of the time period used by the ETABS for calculating the base shear.

For normal construction in Pakistan, the construction in which the area of shear walls seldom exceeds 1% of the floor area, the time period of the building should not be significantly less than the value obtained by empirical formulae of UBC 97. If ETABS is using the value which is, say 60%, of that value, then there should be some mistake in modeling, and the design engineer should be aware of that.

Link to comment
Share on other sites

10 hours ago, BAZ said:

My initial post was to point to fellow engineers that one must look at the value of the time period used by the ETABS for calculating the base shear.

For normal construction in Pakistan, the construction in which the area of shear walls seldom exceeds 1% of the floor area, the time period of the building should not be significantly less than the value obtained by empirical formulae of UBC 97. If ETABS is using the value which is, say 60%, of that value, then there should be some mistake in modeling, and the design engineer should be aware of that.

100% agreed. Usually shearwall/floor area is ~ 1%

Link to comment
Share on other sites

 

Dear Waseem

Your concern is valid but the lower limit given in FEMA example doesn't make sense to me as in a general the usage of time period in seismic analysis is not more than the evaluation of ground acceleration that will be imparted in structure in accordance with specific structural characteristics.

Similarly if the specific structural characteristics of a building reveals a time period lesser than generalized approximate time period , then it doesn't make sense to skip the accurate time period and to use approximate one when code itself defines approximate time period as a basis to start analysis for actual T.

More interesting is to note that indicated FEMA example is based on 2009 NEHRP seismic provisions , whereas in a separate document issued by NEHRP afterwards (named expanded seismic commentary to ACE-10) it is recommended to use "Tcomp" if "Tcomp < Ta".

Moreover, i didn't find any lower bound on time period in UBC97 and even in ASCE 7 which is based on same ELF procedure as given in FEMA example.

Therefore, it seems that indicated provisions in FEMA example are overlooked that they have fixed later and usage of Tcomputed if "Tcomputed < Tapproximate" seems valid.

 

 

 

Link to comment
Share on other sites

13 hours ago, Syed Umair Haider said:

 

Dear Waseem

Your concern is valid but the lower limit given in FEMA example doesn't make sense to me as in a general the usage of time period in seismic analysis is not more than the evaluation of ground acceleration that will be imparted in structure in accordance with specific structural characteristics.

Similarly if the specific structural characteristics of a building reveals a time period lesser than generalized approximate time period , then it doesn't make sense to skip the accurate time period and to use approximate one when code itself defines approximate time period as a basis to start analysis for actual T.

More interesting is to note that indicated FEMA example is based on 2009 NEHRP seismic provisions , whereas in a separate document issued by NEHRP afterwards (named expanded seismic commentary to ACE-10) it is recommended to use "Tcomp" if "Tcomp < Ta".

Moreover, i didn't find any lower bound on time period in UBC97 and even in ASCE 7 which is based on same ELF procedure as given in FEMA example.

Therefore, it seems that indicated provisions in FEMA example are overlooked that they have fixed later and usage of Tcomputed if "Tcomputed < Tapproximate" seems valid.

 

 

 

Ok, what about these;

 

#1

2015 NEHRP Recommended Seismic Provisions: Design Examples FEMA P-1051/July 2016

https://www.fema.gov/media-library-data/1474320077368-125c7a1d1a3b864648554198526d671f/FEMA_P-1051.pdf

"Calculation of a period based on an analytical model of the structure is encouraged, but limits are placed on the results of such calculations. These limits prevent the
use of a very flexible model in order to obtain a large period and correspondingly low acceleration."

Page: 2-17

and

"A lower limit to the base shear determined from the modal analysis procedure is specified based on the static procedure, and the approximate periods specified in the static procedure."

Page: 2-18

Also consider the example in section 13.2.6 and I have attached the sketch explaining that example for easy understanding here; (Ta was used instead of Tc).

dyn.jpg

 

#2

See ASCE publication seismic design guidelines based on ASCE 7-10, Example 17 on page; 117 & 118;

a.png

and

b.png

 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       