Pile design
Sohaib Iqbal
Sohaib,
I will try to explain to you the procedures involved in designing a pile.
1) Pile design involves meeting the two limit states: Axial and Lateral (also called serviceability for piles)
Considering ULS design for piles, you need a geotechnical report that contains skin friction values for pile design along with recommended factors for tensions, compression and frost loads. Geotechnical report will also provide you either parameters for lateral design or load deflection graphs.
2) Once you have the geotechnical report, you do initial sizing of the pile based on the load. Geotechnical report recommendations will allow you to size the pile based on geotechnical capacity, which is how much load can be transferred from pile to soil based on pile geometry.
3) Once you have sized the piles based on geotechnical, you will need to do structural checks to make sure pile structural capacity is greater than geotechnical capacity.
4) For literature, you can have a look at attached.
Foundation Analysis and Design - FEMA.pdfFetching info...
  On 10/7/2016 at 7:54 AM, m waqas said:
is buckling of pile prevent the surrounding soil? my kl/r value come to be 133.
For structural design of pile, you need to consider soil horizontal springs that would provide lateral support to pile. Use LPILE software with data from Geotech values.
  • 6 years later...
  On 8/28/2016 at 2:13 AM, UmarMakhzumi said:
Sohaib,
How can we add tensile and compressive capacity of pile in etabs
i am not sure if there is an option in ETABS to do it. I would suggest to export reactions to excel and check the reactions against max tensile and compressive capacity of pile.