ShearWall - Temperature Design in ETABS


rummaan17
 Share

Recommended Posts

Dear all,

I am trying to design shearwalls through ETABS with temperature load applied over shell. At various location, spandral section fails in Shear due to temperature and piers (sometime in shear, mostly in flexure).  (See Attached Image)

Certainly all the problem in Shearwalls are due to temperature. I don't want to increase cross section of spandral or pier at some location just due to temperature load case as it will appears non-uniform with rest of the wall. 

I have seen stiffness modifier affect distribution of forces and also rigid/semi rigid daiphragm assumption. 

 

Can anybody guide how to properly design the shear wall with temperature load applied in ETABS or share any similar experience. Thanks in Advance.    

Pier SHear Failure.JPG

Spandral Shear Failure.JPG

Link to comment
Share on other sites

There is alot of debate as what stiffness modifier to use F11=F22 for temperature. Previously, slab was getting high temperature reinforcement which was fixed using this value of F11=F22. Walls still have F11=F22=0.7 which is also a reason for high temperature load. 

Link to comment
Share on other sites

You should not get moment from temperature load in ETABS. Because temperature is applied as axial load not as gradient like in SAP.

 

Yes walls will fail in F11, F22 (axial force, tension mostly). But remember for tension, walls will be cracked and to account for cracking you have to apply a very low value of axial stiffness. I would say to start with F22 and F11 as 0.25 and if it still fails you can even reduce it to like 0.10 (tension will be carried only by steel) plus some portion by tensile capacity of concrete.

 

This is true if cracks are not your concern like in water tanks etc.

Imagine what is the goal of your calculations? failure mode? service or ultimate? Ultimate right? Ok, now at ultimate stage what is the predicted cracking mode? How much cracking do you expect? For axial tension, I expect fully cracked concrete with section capacity only equal to n.As. So nAs/Ag is the modifier you should use for f11 and f22 in tension.

 

For compression, i dont expect cracks so section is mostly less cracked (only from shear or flexure).

Link to comment
Share on other sites

@Rana,

Good comments. I have got a few questions about the subject that I believe will make this topic more detailed.

8 hours ago, Rana said:

You should not get moment from temperature load in ETABS. Because temperature is applied as axial load not as gradient like in SAP.

I am assuming that the discussion here is for temperature design for the final finished building and we are not discussing temperature affects cobsidering sequential construction (which could be an interesting case- general comment). Here are the questions:

Temperature loads generally produce tension or compression. For the current case, I assume there would be some slabs connected to shear wall. Considering that the building is insulated at all level and temperature is maintained inside the building once it would be operational, temperature differential would exists at top slab (roof) , which would likely induce moment in the wall. Why isn't that being considered.

Also, the discussion above talks about temperature induced load in shear wall as axial load. I would like to know the source of axial tension in shear wall if temperature in building is maintained?

8 hours ago, Rana said:

Yes walls will fail in F11, F22 (axial force, tension mostly). But remember for tension, walls will be cracked and to account for cracking you have to apply a very low value of axial stiffness. I would say to start with F22 and F11 as 0.25 and if it still fails you can even reduce it to like 0.10 (tension will be carried only by steel) plus some portion by tensile capacity of concrete.

I am not sure what would be the best way to consider temperature loads concurrent with other loads, but what I have done is run a separate load combination as temperature load and add that load combination to other load combos (RISA 3D). I design steel structures for Oil and Gas industry so genre is different. In my opinion, the affect of temperature on shear wall should be considered in combination with other working loads. The design would be similar to that of a beam column subjected to axial load. I am not sure if additional reduction is stiffness is justified based on isolated consideration of temperature load. What do you think ?

Thanks.

Link to comment
Share on other sites

Dear Mr.Umar,

We have to submit our design for peer review which includes one international and one local consultant. I was amazed when they asked to apply load on overall structure. Even in my opinion its only outersurface that is most prone to temperature change, as here in middle east mostly building inside is temperature controlled. 
Though we also design slab for temperature change for all level, which i don't find just.   I was getting high temperature stress even in slab which was then modified when I started using 0.25 modifier. The temperature reinforcement decreased drastically. I still consider SAFE as a better option to design as it consider temperature difference between top and bottom surface. But still shear walls remain a question, as if I decreased stiffness modifier of forces F11=F22 it will transfer all loads to column. 


Temperature load is applied in conjunction with other load combination as stated by ASCE 7-10 with loads factor not less than 1.   Thats all I know about it uptill now. 

 

Link to comment
Share on other sites

7 hours ago, rummaan17 said:

Dear Mr.Umar,

We have to submit our design for peer review which includes one international and one local consultant. I was amazed when they asked to apply load on overall structure. Even in my opinion its only outersurface that is most prone to temperature change, as here in middle east mostly building inside is temperature controlled. 
Though we also design slab for temperature change for all level, which i don't find just.   I was getting high temperature stress even in slab which was then modified when I started using 0.25 modifier. The temperature reinforcement decreased drastically. I still consider SAFE as a better option to design as it consider temperature difference between top and bottom surface. But still shear walls remain a question, as if I decreased stiffness modifier of forces F11=F22 it will transfer all loads to column. 


Temperature load is applied in conjunction with other load combination as stated by ASCE 7-10 with loads factor not less than 1.   Thats all I know about it uptill now. 

 

Rummaan17,

Thanks for the summary. It does provide some useful background on the topic. 

Temperature loads should be applied but only to areas exposed to temperature differential (Roof slab or periphery members if exposed). Lets get some feedback from @Rana as he might has more experience on temperature load application in commercial design and see where this goes.

Thanks.

Link to comment
Share on other sites

1. I forgot to mention and as is Rummann understood correctly, that reason for using reduced stiffness for axial tension is that we will get less tension from analysis (due to less stiffness/restraint).

2. Negative temperature will produce tension near restraint (like slab supported on heavy walls).

3. What is the use of building? Is it a car park where you need to apply temperature to all the structure? Otherwise as Umar and you already pointed out, its the top slab where you need to consider differential temperature between top and bottom slab and thats not possible with ETABS 9 atleast.

4. Yes, tension should be checked on appropriate combination with other loads and that is 1.2D+1.6L+1.2T plus other loads if you have. If still you are getting tension that means it will be carried by modulus of rupture + steel only.

5. I would recommend you to use reduced stiffness of 0.25 and then also subtract the tension capacity of concrete (equal to half of 0.62(f'c^0.5)xthicknes in Mpa), half because slabs are restrained as per ACI.

6. For compression, cracking modifier should be increased but walls are quite stronger in compression. So just use 0.25. This is your separate model for temperature analysis. Keep it separate from lateral analysis where you might be using 0.7 or 0.35 modifiers for shear walls. Or it will affect the distribution of lateral forces to columns as you pointed out. But keep in mind, that is the real situation, if temperature cracks walls before earthquake hits, walls would be very weak transferring lateral forces to columns. Others can shed light on this more.

Link to comment
Share on other sites

Thanks alot Mr.Rana . Indeed very useful. This thing was a pain for me since I have started applying temperature. 

At my last peer submission I finally realize that we should keep temperature model separate. There is also one more thing I figured out 

I was using Rigid daiphragm assumption at start which was resulting in very high axial forces in ETABS spandral. (ETABS doesn't design for spandral axial forces and designer has to check manually).  I discussed with CSi Support about this and they told to use semi-rigid as temperature has no point with rigid daiphragm.

Now, I use separate model with semi-rigid daiphragm for temperature which has decreased my axial load in spandral but has affected walls alot in terms of shear and flexure. 

Now what I understood.  That i will keep a separate model with all WALLS and SLABS modifier =0.25 just for temperature analysis. Hopefully it will solve my problem. 

 

Link to comment
Share on other sites

13 hours ago, Rana said:

5. I would recommend you to use reduced stiffness of 0.25 and then also subtract the tension capacity of concrete (equal to half of 0.62(f'c^0.5)xthicknes in Mpa), half because slabs are restrained as per ACI.

6. For compression, cracking modifier should be increased but walls are quite stronger in compression. So just use 0.25. This is your separate model for temperature analysis. Keep it separate from lateral analysis where you might be using 0.7 or 0.35 modifiers for shear walls. Or it will affect the distribution of lateral forces to columns as you pointed out. But keep in mind, that is the real situation, if temperature cracks walls before earthquake hits, walls would be very weak transferring lateral forces to columns. Others can shed light on this more.

I think there are some items that need to be addressed with the above approach. The ULS state being checked should be done for only one stiffness modifier. The basis aren't consistent when we are using different modifiers for temperature load and others for active loads as both relate to finding the most critical ULS condition under combined loads. Use of separate model can be justified for either where code requires a special design condition to be checked like Dual Systems or when a different limit state is being checked like serviceability.

Second comment that I have is that temperature gradient across a member would not only cause axial loads but as well as curvature/ bending. If ETABS doesn't allow application of temperature gradient then these loads need to be applied to reflect the actual loading condition.

22 hours ago, rummaan17 said:

We have to submit our design for peer review which includes one international and one local consultant. I was amazed when they asked to apply load on overall structure. Even in my opinion its only outersurface that is most prone to temperature change, as here in middle east mostly building inside is temperature controlled. 

You can challenge your peer review team as long as you can defend your position clearly. Do you have load development document created for this project that summarizes basis of all loads?

Thanks.

Link to comment
Share on other sites

2 hours ago, UmarMakhzumi said:

You can challenge your peer review team as long as you can defend your position clearly. Do you have load development document created for this project that summarizes basis of all loads?

 

Dear Mr.Umar, Yes we have created some document for their timely response to our design but I guess we dont have any offical document from start that could justify this load application technique.   Also Mr.Umar, certainly my review team never cease to surprise me as they argue over things that even doesn't make sense to me, who is a newbie in this field. Since, they are approving authority and we are tough on schedule we try to sort it out as they want.


Secondly, i have some similar concerns. This 0.25 modifier track back to reference from code ?   if any please guide me. I started using 0.25 modifier as I found this value on certain discussion on forums and after applying it I found the reinforcement to be just. but as you quoted, using two modifier at ULS state for two different load case ?  how can we back it up.

Any addition would be highly appreciated. Thanks in advance. 

Link to comment
Share on other sites

@rummaan17,

I hear you and that's why we have this forum.

All these questions are legit.  @Rana might be able to shed better light because of his experience in commercial design. If not, we can all agree on most rational conclusion and run numbers to do sanity checks.

Cheers

Link to comment
Share on other sites

First-off, I am not sure about your system, is it a moment resting frame, dual frame or shear wall frame interaction?

I assume it is a building frame system where lateral loads (all) are taken by shear walls (in-plane) and all gravity (mostly ~ 90%) is taken by columns.

The above assumption can be checked by checking reactions after applying 0.7,0.35 modifiers to walls and 0.7 modifiers to columns.

This is your routine design..Right?

Now comes the question of temperature loading, for that please update what is the temperature magnitude you are using? What is the use of building? It is heated/un-heated structure? For example if its a parking structure where under-sides of beams also have temperature loading, slab stresses will be minimal (almost zero if equal values). Also for parking structure, the first slab will have huge stresses due to fixity of base.

And as @UmarMakhzumi pointed out, you also need to check bending under temperature gradient (manually by using C and T approach for a single reinforced section or by computer using complex analysis).

Anyway, In my view, I hope that authorities would not go for that. But for normal temperature analysis, I would recommend you to make a 1 page A4 calculation, stating the design philosophy for temperature loads and put it as appendix or part of your report.

In that report you would mention,

1. use of semi-rigid option

2. use of reduced modifiers for tension cracking for walls (even for columns if they are showing tension). You can use 0.25 and if it not working reduced further. It would be nAs/Ag for the members where you havee tension.

3. show formula for modulus of rupture for restrained slabs and subtract that capacity from ETABS values.

4. Assign piers or average manually the axial force over whole length of wall piers to reduce magnitude further.

 

Make sure that reinforcement provided for temperature is same on both sides for slabs/walls and same on all sides for beams/columns.

 

Now next question is regarding lateral load RE-distribution.

If you reduced the stiffness of walls and columns both by same amount, that would not affect re-distribution of lateral forces.

But if you just reduced stiffness of walls, columns will start taking more lateral loads (depends on relative stiffness of wall/columns, I do not know the dimensions) so As @UmarMakhzumi pointed out, you should this design too. Because axial stiffness of walls/shells = in-plane stiffness of walls/shells so changing axial stiffness will also change the bending stiffness for lateral loads and re-distribution will happen.

So check for this condition too, you might need to increase some columns that again depend on dimensions and framing system. In that case, read Tranath book on tall buildings chapter 3 on lateral loads to see what you actually need to increase, columns or beams?

Please update us what happens.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       