Collectors requirement and Omega factor in foundation design
Waqas Haider
Assalam o alaikum,
i m confused whether collectors and chords are only required in Flat plates/slabs or also required in beam slabs? because in beam slab we are having beams at perimeter of every panel and they can act as chords and for diaphragm bending and as collectors at junction of slab to shear wall. Usually, in seismic zone 4, i dont design diaphragm exclusively. i just design it as simple slab and design my beams in SMRF or Dual Frame in etabs.
Also i m confused in excerpt from a document stating
The Special Seismic Load combination is also indirectly identified in Chapter 18, Section 1809, Foundation Construction – Seismic Zones 3 and 4.
1809.3 Superstructure-to-Foundation Connection. The connection of superstructure elements to
the foundation shall be adequate to transmit to the foundation the forces for which the elements
were required to be designed.
For instance, since Section 2213.5 Column Requirements specifically identifies the Ω0 factor, Section
1809.3 requires the column-to-foundation connection to be designed for a load combination which includes
the Ω0 factor.
What does it mean? In seismic zone 3 or 4, we need to design foundations for special seismic combos ALWAYS or only if we r having discontinuous system? The full document is also attached. Thanks.
OmegaFactorDiscussion.pdf
Below is an excerpt from the document titled: Seismic Design of ReinforcedConcrete Mat Foundations. The document is prepared by NEHRP.
Earthquake load effects, E, are defned in ASCE 7-10 §12.4.Inherent in the defnition of these seismic demand levels is thestructural response modifcation factor, R, which is dependenton the type of lateral force-resisting system considered for thesuperstructure. The same overturning that is determined at thebase of the superstructure is to be applied directly to the matfoundation. Consideration of higher foundation demand levelsis triggered only by unusual structural geometries, such as acantilever column system or a discontinuous lateral system,which require the consideration of a system overstrength factor,per ASCE 7-10 §12.4.3. By defining earthquake load effects with an inherent R-value, some inelastic behavior is assumed in the superstructure and therefore implies that a mat foundation also may experience inelastic demands.
You can also study the document in this link: bulletin.nzsee.org.nz/13/2/0171
1. collector elements not required in 2-way beam (beam should be sufficiently rigid).
2. to complete the load path (as BAZ mentioned), omega factor needs to be considered all the way down to foundation. For if a discontinuous element at last floor is designed for omega factor, i would design all the columns/walls below and even the foundation on increased forces to make sure the load path works.