Lower compressive strength of concrete
Faraz Korimbocus
This one is mostly a practical issue.. If ever cube strength fails after 28 days, say for example the concrete compressive strength with which the structure was designed was 30MPa, and from cube test or non-destructive testing, the compressive strength has been found to be half, 15MPa only. Most consultants usually instruct demolition of the concrete element and re-casting. From a calculation which i made manually, I found that fcu(symbol as per BS 8110) has very little effect on reinforcement calculation. Even if fcu is halved when calculating again, new steel reinforcement calculated may increase by only 2-3%. Furthermore, fcu affects the value of Modulus of elasticity E, which in turn affects stiffness of the member producing a change in deflection of beams for example. But the effect is not so much prominent though, it may still pass in deflection also. Can anyone ellaborate more on this issue, if ever cube strength fails on site, final instruction will be based on what for an engineer supervising on site.
In general, this issue is controlled by relevant clause of contract agreement. Following are the possible options that may be or might have been specified in the contract:-
a. Demolition & recasting, in case actual strength falls MORE than a certain percent below the required concrete strength
b. Strength evaluation of actual structure, according to applicable design code & acceptability or rejection of structure accordingly.
c. Rarely, there might also be an option to strengthen the structure (using conventional or advanced strengthening techniques & materials) to the required level (where possible).
1) Refer to ACI 214R-02 Page No. 214R-9,10,11 and 13
2) Refer ACI 301M-99
3) Refer ACI 318 M-11 Page No. 74