Ordinary shear wall design - ACI
Muqtadir
In Aci-318, example 29.6 provides details on how to design a special wall. I want to know on how to design an ordinary shear wall, specifically interested in designing of the boundary elements.
Another query is that, the vertical flexural rft acts like vertical shear rft? As aci 318 quotes 0.0025 for vertical shear rft and 0.0015 for vertical rft in separate quotations?
Ordinary shear walls are designed as normal shear walls according to chapter 14. Boundary elements are required for special structural walls, where compression load is high and the bars could buckle.
For cast in place shear walls, yes the limit for vertical bars is 0.0025, where did you find 0.0015 limit? Please quote.
Aci 318-11...14.3.2
But both walls have different t nominal shear strength formula's.
So, the check of 'c' determines if you are to use special wall or an ordinary wall?
Section 14.3.2 and the minimum limit of 0.0015 applies to walls that are not resisting shear.
If the wall is resisting horizontal shear forces in the plane of the wall, section 11.9.9.4 applies, and vertical reinforcement should be minimum 0.0025 times the gross concrete area.
  On 9/20/2017 at 9:22 AM, Muqtadir said:
Aci 318-11...14.3.2
It's up to you to decide which type you intend to use (ductility) and then design accordingly.
