*SEFP Consistent Design*
*Pile Design*
*Doc No: 10-00-CD-0005*
*Date: Nov 21, 2017*
 

This article is intended to cover design of piles using Ultimate Limit State (ULS) method. The use of ULS method is fairly new for geotechnical design (last decade). The method is being used in multiple countries now (Canada, Australia etc). The following items shall be discussed:

  1. Overview
  2. Geotechnical Design of Piles (Compression Loads, Tension Loads and Lateral Loads)
  3. Structural Design of Piles (Covering both Concrete and Steel)
  4. Connection of Pile with the foundation (Covering both Concrete and Steel)
  5. Pile Group Settlement
  6. Things to consider

 

1. Overview

Piles provide a suitable load path to transfer super-structure loads to foundation where shallow foundation are not suitable - this can be due to a number of reasons like existing space constraints or suitable soil strata is not present immediately below structure. Other uses can be to meet design requirements like to have reduced settlement etc.

This article shall cover the use of straight shaft cast-in-place concrete piles and straight shaft driven steel pipe piles. There are a number of additional piles types like belled concrete piles, precast concrete piles, screw / helical steel piles etc but the discussion to choose a suitable pile type is not in the intended scope of this article. The article is intended  to discuss design requirements for straight shaft piles only (both concrete and steel) . The aforementioned topic about pile selection is a very diverse subject and requires a separate discussion on its own.

Before I get into the nitty and gritty of pile design, it is important to highlight that as a structural engineer working on pile design, there are a number of parameters that you would require from the geotechnical engineer. Generally, these parameters are provided in the project geotechnical report. Based on those parameters, the geotechnical design of piles is performed first followed by structural design of pile. The next section talks about  the geotechnical design of piles.

2. Geotechnical Design of Piles.

Geotechnical design of pile means sizing of pile. This includes determining the following two geometric properties of piles:

1) Diameter or radius

2) Length

Straight shaft piles embeded in soil derive their capacity from two sources. The first one is the skin friction along the pile length and the second one is the end bearing. In order to complete the geotechnical design of piles or in simple words to "size up the piles", you will need skin friction values for different soil strata through which the pile would penetrate or lie and the bearing capacity of the layer in which pile would terminate.

This information is provided by the geotechnical engineer in the project geotechnical report. Generally, they would provide a table showing skin friction values of each soil layer for both tensile and compressive loads along with end bearing values of each layer. In addition to this, for areas susceptible to frost loading, the geotechnical engineer would also provide ad-freeze and frost heave forces. You can't design a pile without knowing what these values are. So this is something that you need from a geotechnical engineer. 

Once you have received the project geotechnical report with all the required information, you need to start  sizing the piles. The easiest way to do it is to create an excel sheet and do preliminary calculations for different standard diameters like 200mm, 324 mm, 406mm, 460mm, 508mm, 610mm, 762mm and 914mm. The geotechnical report shall also provide recommendations if certain top soil layers need to be ignored or not.

Example Problem:

From your structural analysis, the maximum factored compressive load is 100 kN. and maximum factored tensile load is 50 kN. You need to size a pile (do geotechnical design) to meet that applied load. Sizing piles for geotechnical capacities is simple. Here is the formula for capacity of pile based on skin friction only (ignoring end bearing for simplicity):

ULS Geotechnical Pile Axial Capacity: Pi * Pile Diameter * Total Embedment Length of Pile * Skin Friction Value * Resistance Factor

Where,

Pi= 3.14

Pile Diameter = 2* Radius

Total Embedment Length of Pile = Pile Embedment Length - Frost Depth

Skin Friction Values = See geotechnical for values

Resistance Factor = 0.4 for compression and 0.3 for tension.

For, the above problems, lets assume Skin Friction values of 80 kPa for both tension and compression and initial pile size (diameter) of 324 mm, Frost Depth of 3000 mm.

For total length of 10m (lets assume a starting length), Total Embedment Length of Pile = 10m - 3m = 7m (Total Length - Frost Depth)

ULS Geotechnical Pile Compressive Capacity= 3.14 * (0.324m) * 7m * 80 kPa * 0.4 = 228 kN > 100 kN Okay.

ULS Geotechnical Pile Tensile Capacity = 3.14 * (0.324m) * 7m * 80 kPa * 0.3 = 171 kN > 50 kN Okay.

The above problem shows you how to calculate the compressive and tensile capacities (also called the axial capacities) of the pile. For lateral capacity, you will need to know the modulus of sub grade information from the geotechnical engineer and use a software like LPILE to see the response against the lateral load. It is important to note that lateral deflection of pile is a service limit state meaning that it should be checked against unfactored loads.

Generally, for petrochemical and oil and gas industries, pile service loads are defined as a deflection limit that will depend upon the maximum allowable movement of pile considering an elastic response from soil as well as the maximum movement piping and its attachments can take. Here is a scenario explaining that. For example, your geotechnical engineer recommends a maximum lateral movement of pile to be limited to 6mm so that soil around pile stays elastic. The structure you are designing, has a wind load deflection of 12mm. The pipes and equipment plus their connections shall be designed for 6mm+12mm = 18mm movement of structure. You need to notify piping of this deflection limit and if they are okay, you are good. If they are not, you will have to stiffen up the structure  to lower the overall structure deflection and work with piping to see alternate routing for pipe. For pile design, you need to see what diameter pile shall have a capacity at 6mm lateral deflection greater than the applicable horizontal service load. To calculate pile capacity for different pile head movements, you will need to use LPILE or similar software.

LPILE shall provide you a graph that would show you that how much a pile would move under applied lateral load or moment. LPILE is very easy to operate. You can look at the program tutorials and work your way through. It will also provide you the analysis results for a pile embeded in soil with soil modelled as springs along the length. This analysis result is important and allows us to see what is the maximum moment and shear developed in pile due to applicable load and based on combined response of soil and pile interaction.

If you don't have LPILE, you can ask the geotechnical engineer, to provide you with pile lateral capacity graphs. In this case, you will need to  provide the geotechnical engineer with estimated pile sizes, estimated axial and lateral loads, pile head condition (Fixed or Pinned) upfront. The goetech engineer will run the LPILE for you and provide you the graphs that will show the maximum load a pile can take against different lateral displacement values and would also provide the maximum moment due to max lateral load. I have done this on a number of projects and this is standard industry practice. 

3. Structural Design of Piles.

After completing the geotechnical design of pile, the structural design of pile needs to be performed. In order to do that, you will need to know the maximum moment in pile due to the application of axial and lateral loads. As mentioned above, the easiest way is to use  LPILE output as it provides you with deformed shape of the pile along with the maximum moments and shears due to applied loads - the analysis of pile embedded in soil. Using LPILE analysis results, you can use beam-column capacity formulas to design a steel pile or column interaction diagram to design a concrete pile. Beam-Column capacity formulas vary with different codes so therefore I haven't included any example. For steel piles, corrosion allowance should be considered as per the code requirements. Generally its 1.5mm each exposed face so for pipe piles it will be 3mm considering exterior and interior face of the pile.

4. Connection of Pile with the foundation (Covering both Concrete and Steel)

The connection of pile and foundation / pile cap is extremely simple for concrete piles. All you need to do is to develop the bars from concrete pile in concrete foundation/ pile cap. For steel piles, similar concept is there, except for you need to weld rebars on top of cap plate.

5. Pile Group Settlement

Single pile or pile groups should always be check for settlement. Geotechnical consultant shall be contacted to get guidance on what method should be used. Methods like equivalent raft method or finite element analysis can be carried out to get settlement numbers.

6. Things to Consider

For pile group, group effects are generally provided by the geotechnical engineer that can be applied to pile group. The group effects are a function of pile diameter and centre to centre spacing. Pile capacities are reduced if they are spaced closely. For straight shaft piles, rule of thumb is to place them greater or equal centre to center distance of to 3 * diameter of pile. For lateral loads, pile capacities are reduced at 3 * diameter spacing and generally piles need to be spaced at 5 * diameter to have no lateral reduction. Also, straight shaft piles if placed too close might result in pile installation issues. Some piles already installed might heave up if other piles are being installed in close proximity. Impact of pile driving to existing structures should also be considered especially if there is sensitive instrumentation installed in close proximity.

Hope this article provides the much needed guidance on pile design. It is written for beginners and a lot of things have been kept simple. Your feedback is more than welcome. Please post any questions should you have.

Thanks.

 

Link to comment
Share on other sites

19 hours ago, Sohaib Akhtar said:

Great information... can you please  also share  information related to pile cap design , my case is a single pile with pile cap over it ....

Pile caps are designed as slabs. For the case where you have a big pedestal on a pile cap, your pedestal is designed as a column and pile cap is designed as a slab taking the loads from the superstructure through the pedestal to piles. You need to check moment, one way shear (perpendicular and diagonal directions) and two way shear for pile cap.

Thanks.

 

Link to comment
Share on other sites

  • 2 weeks later...

@UmarMakhzumi

Dear Engr i would to disagree regarding your statement of design of Pile cap as a typical Slab.

  1. Normally pile cap behaves like a Deep Beam action, normal bending/flexural theory is not applicable to Pile Cap design. ACI and AASHTO recommends to use STRUT n Tie model for Pile Cap.
  2. However for ease of analysis and design, due to absence of expertise on STM, structural engineers design it the other way. 
  3. The behaviour of Pile cap supported on Pile follows Bolt Analogy.
  4. Furthermore, for modelling in FEM softwares, In Usual analysis of raft slab, you put soil springs under the raft, however for pile cap we ignore effect of soil and pile cap is supported only on piles.

           Thank You

Link to comment
Share on other sites

On ‎2017‎-‎12‎-‎10 at 7:53 AM, SALMAN CH said:

 

  1. Normally pile cap behaves like a Deep Beam action, normal bending/flexural theory is not applicable to Pile Cap design. ACI and AASHTO recommends to use STRUT n Tie model for Pile Cap.
  2. However for ease of analysis and design, due to absence of expertise on STM, structural engineers design it the other way. 

Salman Ch,

Thanks for your comment. Pile cap would only behave as a deep beam if distance between ratio of slab thickness to distance between piles is more than whatever is required by code for deep beam action. I live in Canada and here if the shear span to depth ratio is less than 2.5, deep beam action can be considered. If not, it is a normal slab. ACI has a different limit. So yes, it may be a deep beam or not, but same would be applicable to a slab if your columns are too close. Anyway, thanks for highlighting that as now the clarification may be useful for someone who isn't aware of this

On ‎2017‎-‎12‎-‎10 at 7:53 AM, SALMAN CH said:
  •  
  • Furthermore, for modelling in FEM softwares, In Usual analysis of raft slab, you put soil springs under the raft, however for pile cap we ignore effect of soil and pile cap is supported only on piles.

This is standard practice and there can be different reasons for not considering soil springs. For example, in North America, heave is a big problem and generally pile caps have a layer of void form below them. Void forms are compressible and analysis should never consider soil springs for that reason as there would never be a hybrid action in that scenario. Also in typical cases stiffness of pile group is >> than soil so it doesn't make sense to put soil springs.

Thanks.

 

Link to comment
Share on other sites

On 12/11/2017 at 7:00 AM, UmarMakhzumi said:

Pile cap would only behave as a deep beam if distance between ratio of slab thickness to distance between piles is more than whatever is required by code for deep beam action

Dear Engr @UmarMakhzumi I just want to add something in it, I feel in this quote you wrote”MORE than require by code “by mistake, in simple words when the distance between supporting reactions is less than the twice depth of the member. I would like to add the ACI and AASHTO references in this regard.

Thank You

 

 

 

ACI PILE CAP.png

AASHTO 5.6.png

Link to comment
Share on other sites

8 hours ago, SALMAN CH said:

Dear Engr @UmarMakhzumi I just want to add something in it, I feel in this quote you wrote”MORE than require by code “by mistake, in simple words when the distance between supporting reactions is less than the twice depth of the member. I would like to add the ACI and AASHTO references in this regard.

Thank You

 

 

 

ACI PILE CAP.png

AASHTO 5.6.png

I think you both are talking about the same thing. His statement is about ratio of slab thickness (h) to distance between piles (L) -> (h/L) being more than the code number and what you have referenced talks about distance between load points (L) to ratio of slab thickness (h) -> (L/h) which has to be less if the first statement is correct.

Link to comment
Share on other sites

@UmarMakhzumi.. @Ayesha...Thank You for your concern. Yes we r on the same page . However my interest was only to highlight the fact that pile cap design is not like slab, due to pile spacing criteria and typical patterns, it will behave like a deep beam in almost every structure. However i feel there is no proper technical inputs on this component of structure and engineers follows whatever practices are in their offices.

In this regard i would like to add little knowledge as per my experience , that unlike the normal slab, the critical sections for maximum FORCES will also be changed , it needs 5 to 6 special investigation as per the reference handbook mentioned in commentary of ACI. 

Regards

 

Edited by SALMAN CH
Link to comment
Share on other sites

  • 4 years later...

Great article.  In these environs, the top 10' (3m) is excluded for exterior piles for desiccation as well as frost, and 5' (1.5m) or so for interior piles, for the same reason.

The pile lengths would be reduced to that required for the load capacity.

If you have different loads, they would try to maintain the same diameter for the pile and change length to accommodate loading rather than change pile diameters. It's less costly in this area to keep the same size pile. For a 12" (300mm) pile, reinforcing would typically be a single 15M deformed bar in the centre.

"Pile caps are designed as slabs."

They used to be designed as beams... current trend over the last couple of decades is to design them using 'Strut and Tie' methods.

LPile is a common program in this area; I've not used it. It has a good reputation.  I have several programs written in SMath to help me for axial loading and lateral loading, and use P-M concrete column design for checking for piles with moments.

 

Edited by Dik
added info
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.