BEAM COLUMN CONNECTION LIMIT STATES
groszni awesome
Assalamualaikum, im designing beam to column connection,
i wanted to know what are some limit states on the beam and also on the column?
and also i need a correction in my design, heres what i did :
1. designed the top and down flange  groove weld to resist tension caused by Mu, Tu=Mu/(h-1/2tf.2)
2. designed amount of bolts on the web based on shear force
3. designed the connection plate on the web based on the shear force / axial (tension force) on the beam.
4. designed the fillet weld based on shear force acting on the beam
what else i have to check/design?
regards.
Groszni,
What you did is good. You need to check the following as well:
1) Geometry Checks which include End Plate Thickness, Bolt Edge Min and Max Distances, Bolt Hole Pitch.
2) End Plate Tension and Block Shear along vertical line of bolts (You might have already checked it).
3) Check beam web shearing strength at weld.
Hope that helps.
  On 12/12/2017 at 3:17 PM, UmarMakhzumi said:
Groszni,
Hope that helps.
but i didnt use an end plate connection, the flange of the beam got welded to the flange of column, and the web of the column connects by double vertical connection plate attached/welded to column (fin plate i guess).
Sorry by end plate I meant the plate that is connecting the beam web to the  column. More specific checks for your case would also include:
1) The column web needs to take the force of M/d transferred by beam flange. The minimum thickness of the column web should be greater than wc >1.9*M/(db*dc*Fy) where dis the depth of beam or column as per subscript. If the web thickness is not enough, the panel zone would require diagonal stiffener. The equation is based on Canadian Code S16.
2) Bearing resistance of column opposite to beam compression flange. If you do this check, you need not to provide any stiffener in the connection area if the checks passes.
do you calculate the dimension of the stiffner as a tension member by using these load-> required load for stiffener = force load by beam flage - column web resistance ?
I Would like to know that you have designed your column end plate as moment resisting connection with two layer of bolts then why you need to weld our beam to the column. It is very difficult on site and as per my experience I have never seen to types of connection at one end.
no its not an end plate connection i guess, the beams flange is rigid conneted to the column (welded using SMAW complete joint penetration). and the web got a fin plate (if i aint wrong for the term) connection design using bolted connection. And no i didnt design it, im working at a fabricator firm, and the client wanted us to do the connection analysis based on model of connection they drawn for us.
Here is what I do:
For Stiffener Against Beam Compression Flange; Force in Stiffener = Fst Compression = Difference between flange force and bearing resistance provided by column web.
For Stiffener Against Beam Tension Flange; Force in Stiffener = Fst Tension= (Mf/ db) - Tr
Where, Tr = 7* Phi * tc2 * Fyc
I should have talked about the stiffener against tension flange in my earlier reply. Anyway, these are the only two checks assuming that your column is at-least Class 2 or Class 1. There are other checks if its Class 3 and Class 4. Generally Class 3 and 4 sections are not provided as columns so all good. This is all based on Canadian Code S16.