I am trying to do the design of culverts (single and multi cell) using moment distribution method.

1. Confused about how to calculate horizontal and vertical moments in the wall. Which one will govern?

2. ACI 350-01 says use minimum shrinkage reinforcement ratio as 0.003. Which seems to result in #4 bars @4"c/c which seems too much.

3. Can anyone give me the link to download ACI 350-06 ?

4. Any excel sheet or document using moment distribution for culvert design will really help.

Link to comment
Share on other sites

Hira,

On 2018-03-12 at 5:33 AM, Hira Malik said:

1. Confused about how to calculate horizontal and vertical moments in the wall. Which one will govern?

Goto this post and download the attachment that shows how to calculation horizontal and vertical moment in the wall.

 

On 2018-03-12 at 5:33 AM, Hira Malik said:

2. ACI 350-01 says use minimum shrinkage reinforcement ratio as 0.003. Which seems to result in #4 bars @4"c/c which seems too much.

Please see this:

 

On 2018-03-12 at 5:33 AM, Hira Malik said:

3. Can anyone give me the link to download ACI 350-06 ?

These requests can't be entertained as it violates forum posting policy. Please see forum posting rules here.

On 2018-03-12 at 5:33 AM, Hira Malik said:

4. Any excel sheet or document using moment distribution for culvert design will really help.

Please see answer to 1. The coefficients provided in the document are very easy to use. 

Thanks.

Link to comment
Share on other sites

25 minutes ago, UmarMakhzumi said:

Please see answer to 1. The coefficients provided in the document are very easy to use.

Those are for 2 way slabs types I guess ? My wall is 17m in span and 1.5m in height i.e. one way and main reinforcement will be along height... so it will be simply designed by taking soil lateral loads as (ka*unit weight*height) right?

Link to comment
Share on other sites

On 2018-03-13 at 10:56 PM, Hira Malik said:

Those are for 2 way slabs types I guess ? My wall is 17m in span and 1.5m in height i.e. one way and main reinforcement will be along height... so it will be simply designed by taking soil lateral loads as (ka*unit weight*height) right?

(ka*unit weight*height)  is the base pressure of the triangular force. You need to use ka*1/2*Gamma*h*h as the force and then multiply the force by lever arm (I think its 1/3rd (likely) or 2/3rd height - see literature) to get the moment at the base. If you have got a long wall, you should also do a check for counterforts to see if they are required or not. I am not sure why you called this a culvert, if its a long retaining wall. If you have a slab on top level, then the design would be different. Can you share a picture or a drawing.

Thanks.

Link to comment
Share on other sites

Yes its a culvert with long walls and slab on top. And so it cant be designed as a retaining wall. But due to longer length, main reinforcement will be that along the shorter span i.e. height (vertical reinforcement). I was thinking it should be designed using attached formula for for FEM when performing Moment Distribution, and W will be same as we do for triangular load. I was just confused if I need to use the walls coefficient method but I guess that's for walls with 2-way action which isn't the case here.

 image.png.abae41e243cf992ee303bf26946fa6d0.png

Edited by Hira Malik
Link to comment
Share on other sites

On 2018-03-15 at 11:07 PM, Hira Malik said:

Yes its a culvert with long walls and slab on top. And so it cant be designed as a retaining wall. But due to longer length, main reinforcement will be that along the shorter span i.e. height (vertical reinforcement). I was thinking it should be designed using attached formula for for FEM when performing Moment Distribution, and W will be same as we do for triangular load. I was just confused if I need to use the walls coefficient method but I guess that's for walls with 2-way action which isn't the case here.

 image.png.abae41e243cf992ee303bf26946fa6d0.png

There is something else that you need to consider. For the case when you have a top slab, that means that you will have two walls - one on each side with ta top slab. So technically speaking the lateral pressure from each side should cancel each other out. But your wall should still be designed to transfer the forces as they are part of load path. Long story short, yes you can use the formula specified but if your length is long, check for counter-forts so that you don't get two way bending of the vertical wall.

Thanks. 

Link to comment
Share on other sites

1 hour ago, UmarMakhzumi said:

So technically speaking the lateral pressure from each side should cancel each other out.

Not sure about this. Both walls will act individually won't they? Yes the inward water and outward soil pressures on each one wall will cancel each other but not completely. Therefore, I am considering the Culvert as empty to maximize the outward soil pressure.

Link to comment
Share on other sites

6 hours ago, UmarMakhzumi said:

Here is what I was thinking. If your culvert is a buried box with a top slab then the lateral pressure from both sides would cancel each other out. Is this the case?

Thanks.

Yes. And each wall will have soil pressure from outside and water pressure from inside.

Link to comment
Share on other sites

4 hours ago, Hira Malik said:

Yes. And each wall will have soil pressure from outside and water pressure from inside.

So there could be times when the culvert is dry and you only have soil pressure acting on your walls. The net soil pressure would equal out (as applied on both exterior faces) assuming that the construction sequence is to backfill both walls at same time. That would help you with sliding and overturning. But you will still need to reinforce your wall for the case of when culvert is dry and earth pressure is on the wall.

Thanks.

 

 

Link to comment
Share on other sites

  • 1 month later...

For any retained wall, always use all applicable cases e.g. for a water tank;

case1: full tank, no backfill

tension on external side of wall at mid span (if top slab exists) check crack width for 0.27mm

tension on inside of wall at base and at top (if top slab exists) check crack width of 0.15mm

 

case2: tank empty (e.g. for cleaning); backfill exists

this is opposite of case1

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.