How can we analyse the existing building wether it is safe or not using etabs
Yochan Stha
  • 6 months later...
  On 4/30/2019 at 6:44 AM, Tufail Mabood said:
So far i know, All you have to do is, to take core samples and evaluate it strength. On the bases of these results you can do assessment of the existing structure in SAP2000.
That would provide you with the concrete strength of existing building at locations where you have taken the core, but other things that you need to confirm are if reinforcement provided matches the drawing and if the structure was built according to the drawings. You need to spot check reinforcement using PUNDIT for general elements and thoroughly check critical elements, check geometry, and use of existing building against the design drawing and also you need to know what code the existing building was designed too. After all that, you can evaluate the structure and then proceed with foundation checks.
I would agree with this, as here in New Zealand we do quiet abig number of builidng and bridge assessments on frequent basis. Number one goal in doing an assessment is to get the as built information along with all the records of structure and do detailed inspection of the structure along with several tests for concrete and reinforecment scans at critical locations. Once you are comfortable with all the information you had you can start it any way by hand or using a software. If in case some info is missing you can discuss with th client the assumptions you are considering for your analysis based on the codes and design methods of that era.
The procedure which we normally follow here for testing is schmidt hammer testing for the concrete strength and hiliti use rebar scanner for steel reinfrocement checks. This gives good idea. in case of critical structures where more precise info is required we hire testing companies for rebar scanning and exact size, shape and spacing. They do X-Ray testing, wave testing etc to verify the reinforcement and give us the results. the next step is IL4 structures like hospitals etc there if we donot have good information on the as built we might go for some core testing and break the plaster on walls to see the actua size of reo and even cut steel reo (only in case the building was built prior to 1920). The location of the steel sample is based on structural system, and normally the secondary or tertiary elements are used for this type of testing.