Simply Supported Beam Model As Shell Element
Dr Yueh
I am trying to understand Shell element behavior . I have modeled a simply supported beam of 24 ft with 1ft thick shell element (Depth  2ft). Meshed Along length 24  and 2 along depth. Applied 3 kip point load at  Node along top surface to create a 3 kip/ft loaded simply supported beam of  1 ft Width X 2 ft Depth. Assigned the beam as spnadrel.
In my opinion Moment wrt to major axis should be = 3*24^2/8 = 216 kip-ft/ft
But according to etabs moment is 138 kip-ft moreover the diagram is rectangular .
Can anyone explain please??
Edited by Saiful Islam Zaber
Saiful Islam,
I like your curiosity and your question is good too. Generally for beams, if you wan to do 3-D modelling, solid elements should be used.The definition below would help you understand the difference:
Shell elements are used to model structural elements in which two dimensions are much greater than the third one and when the change of the analysed feature across this third direction can be neglected. It is reasonable for static analysis of panel/planar elements such as slabs or walls as well as thin-walled spatial elements such as shells. The advantages of the use of shell elements, as you said, results mainly from time-saving due to reduced number of finite elements (and consequently the equations to solve). So, anytime you can reduce the problem to planar problem and neglect what happens at the thickness of the element I don't see the reason to use solid elements.
The results from the following simple analysis: http://www.javelin-tech.com/blog/2012/10/shell-vs-solid-elements/ suggest that it is when the third dimension is at least 20 times smaller than the other ones.
However, if the change of the analysed feature is on a comparable level in all directions of the analysed element, solid elements should be used. It is the case e.g. in block elements, like massive concrete elements which are among my interests. In such elements, the observed thermal and moisture fields are highly non-stationary and the resulting thermal and moisture gradients lead to formation of the internal restraint in the elements which, in turn, is the origin of (self-induced) stresses in the element. If that fact was neglected, we would not be able to analyse this phenomenon.
To simplify, shells elements are best for walls, slabs and modelling 3D elements where the thickness is smaller like surface elements.
Hope this helps.
@UmarMakhzumi   Thanks a lot.
As there are two type of shell in Etabs - horizontal and Vertical ( Slab and Wall ) , Modelling the simply supported Beam  by Slab Shell shows 216 kip-ft moment which is correct but Wall type shows 138 kip-ft  which is not expected.
That brings the question " How should I model link beam between Shear wall or How should I model Deep Beam or swimming pool hanging from a large depth beam (but not Deep beam) bottom, as Slab or Wall?"
I am not aware of the difference.
You can model a beam/ deep beam using beam elements and then mode the swimming pool as slab?
Let me know what you think. The picture above isn't clear. If you can explain what the framing and intent is, that would be great.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik