cantilever beam fails in etabs no matter how big section I assign. Please help! my etabs file in attached herewith.

cantilever beam failure elevation view grid 2.bmp cantilever beam failure.Docx shear failure in cantilever beam.bmp

house for thulo kancha uncle 2.EDB

Edited by Beenay Beenay
Link to comment
Share on other sites

  • 3 weeks later...

Actually there is nothing much to elaborate. I have designed many buildings in etabs. I came across this problem in two buildings and I cant find the cause. Cantilever beams just fail in shear no matter how big of a section I assign or how little load I apply. Its just a regular building. Nothing exceptional about it. I have remodeled it few times in Etabs 2015 and 2016 to see if there is some issue with the version of etabs that I am using. But I came across the same problem in both versions. But cantilever beams don't fail when I remove earthquake load pattern. Design summary show very very high unrealistic shear force. I don't know the reason why. thanks for showing interest.

Link to comment
Share on other sites

4 hours ago, Beenay Beenay said:

Actually there is nothing much to elaborate. I have designed many buildings in etabs. I came across this problem in two buildings and I cant find the cause. Cantilever beams just fail in shear no matter how big of a section I assign or how little load I apply. Its just a regular building. Nothing exceptional about it. I have remodeled it few times in Etabs 2015 and 2016 to see if there is some issue with the version of etabs that I am using. But I came across the same problem in both versions. But cantilever beams don't fail when I remove earthquake load pattern. Design summary show very very high unrealistic shear force. I don't know the reason why. thanks for showing interest.

Try section modifier for torsion as 0.01 and then check. It may help

Link to comment
Share on other sites

22 hours ago, Beenay Beenay said:

Actually there is nothing much to elaborate. I have designed many buildings in etabs. I came across this problem in two buildings and I cant find the cause. Cantilever beams just fail in shear no matter how big of a section I assign or how little load I apply. Its just a regular building. Nothing exceptional about it. I have remodeled it few times in Etabs 2015 and 2016 to see if there is some issue with the version of etabs that I am using. But I came across the same problem in both versions. But cantilever beams don't fail when I remove earthquake load pattern. Design summary show very very high unrealistic shear force. I don't know the reason why. thanks for showing interest.

Never came across such an issue. Share the results may be?

Link to comment
Share on other sites

On 7/30/2019 at 12:42 PM, Beenay Beenay said:

cantilever beam fails in etabs no matter how big section I assign. Please help! here is my etabs file - https://drive.google.com/open?id=10Pr_WSKlv9L77CIb_aP9HbpYuux38fvA

Please have a look at the file now. As per my understanding it is very much okay now. You were inputting the wrong modifiers. For your reference I have also uploaded an image for appropriate section modifiers. Please find the attached files. Thanks

Section modifiers.JPG

house for thulo kancha uncle 2-check.EDB

Link to comment
Share on other sites

On 8/17/2019 at 3:11 AM, abbaskhan2294 said:

Please have a look at the file now. As per my understanding it is very much okay now. You were inputting the wrong modifiers. For your reference I have also uploaded an image for appropriate section modifiers. Please find the attached files. Thanks

Section modifiers.JPG

house for thulo kancha uncle 2-check.EDB 240.49 kB · 2 downloads

Thank you for your support. You guys in Sepakistan have been most supportive so far. I couldn't open the etabs file you uploaded because it might have been saved in the later version of etabs than mine. I did not modified any modifier from default value of 1 except for torsional constant in which I plugged in 0.001. I think its ok to leave all the modifiers at the default value of 1. Plugging in the value of 0.35 and 0.7 for beam and column respectively give less reinforcement. These modifiers are only supposed to be used in deflection check from what I have read in discussion forums. Only changing one modifier i.e. torsional constant to 0.001 to avoid torsion in beams, hence avoiding the beam failure in torsion(as beams can transfer torsion to columns and other beams as moment)  should suffice for a good design) from what I have read in forums. I was just wondering how can "not changing" the modifiers to the above values can show the cantilever beams as failed. I know modifying the torsional constant to negligible value  to avoid beam failure in recommended. But I think leaving other modifiers to value of 1 should not be a problem. I would appreciate if you can provide any explanation or clarification on this issue. Thanks a lot!

Edited by Beenay Beenay
Link to comment
Share on other sites

That is a very nice question asked. Well section modifiers just not only has to do anything with deflection but stiffness of the member too and stiffness in RCC is a major factor controlling the reinforcement. Just as u explained the torsional constant if it is input as 1 it means the beam is so stiff that all the torsional moment will be taken by this beam alone and it will not be distributed in the adjacent members thats why beams always fail in torsion when torsion modifier is used as 1. But if u start playing with the torsion modifier and decrease it u will see that the torsional demand acting on it previously has now been distributed amongst other members and as a result reinforcement in all the other adjacent columns and beams increases. This condition is known as compatibility torsions. 

Coming back to moment of inertia modifiers case, Building systems are broadly classified into moment resisting frames, Bracing system and dual systems. 

When designing columns in buildings with braced systems (shear walls), they recommend to use a section modifier for both Ixx and Iyy as 0.1 and when u do such , columns in buildings with greater heights will have 1% reinforcement for the sake that u have assumed that ur column stiffness is too less (from the section modifiers) and all the load is taken by the bracing systems alone. 

This is what i have understood from the case studies I have performed. sharing other experiences will be great addition. 

Link to comment
Share on other sites

I think I misunderstood your question initially. I thought of it as a simple cantilever beam. However, from the trailing discussion I can discern the said beam was part of a building or frame. And yes, that's where the torsion stiffness play a role.

Link to comment
Share on other sites

There has been very good discussion on this, I will just add my 2 cents. I don't have ETABS, so I have no idea about what the framing so the following comment *might* not be applicable if framing is not what I am thinking, however, please note that for beams supporting cantilevers, you shouldn't release the torsional moment or change its modifiers as the torsion would be equilibrium torsion not compatibility torsion. If your beam is failing, just add another beam inline with cantilever. See image below.

 

Also, I would suggest to *please* add images to question rather than ETABS model as not everyone has the software to check. Also checking someone else's file is cumbersome and time consuming, which a lot of people who volunteer here might not find time for as a result of that the thread may stay unresponsive.

Thanks.

 

 

image.png

Link to comment
Share on other sites

On 7/30/2019 at 1:27 PM, Beenay Beenay said:

I have attached the plan and elevation of the model showing cantilever failure. I have also attached the shear design summary of one of the cantilever beams. Shear force in it is 830 KN which is greater than the reaction at the base of the column for normal residential building of 4 story and 12ftx12ft grid.

Link to comment
Share on other sites

10 hours ago, Beenay Beenay said:

Shear force in it is 830 KN

You need to check your applied load. Is this correct to say that cantilever beam is a balcony beam? If yes, the only load on the beam is the tributary balcony area that it is supporting and that can’t be 830kN. Check your area load units, material assignments, section properties. Clearly there is something wrong in the model. Another method would be to check which load combination is governing shear, then run individual basic load case in that load combination to trace error. 

Thanks.

Link to comment
Share on other sites

On 8/20/2019 at 9:50 PM, Beenay Beenay said:

I have checked the loads and even remodeled it few times in two version of etabs ie 2015 and 2016. I hope someone can find my blind spot in modelling or loading.

Your applied loads need to match actual situation. I am not sure what is happening there, but if you have a simple residentail balcony, you can't have a 840kN shear due to area load (assuming regular areas). Did you just model the balcony by itself and compared it against hand calcs for shear? If not, please do so.

 

Link to comment
Share on other sites

hello everyone 

regarding this issue I can not say for sure, unless I check the model, so please send me the Etabs Model

this problems seems un-logical. I checked the word file I guess the problem is the width of the beam; increase the width of the beam (at least 250mm) because 

beside that the problem may be in modeling and loading too 

Link to comment
Share on other sites

20 hours ago, mortezamobariz said:

hello everyone 

regarding this issue I can not say for sure, unless I check the model, so please send me the Etabs Model

this problems seems un-logical. I checked the word file I guess the problem is the width of the beam; increase the width of the beam (at least 250mm) because 

beside that the problem may be in modeling and loading too 

I have used 12 inchx14inch beam too. The the problem is the same. I have uploaded the model at the begining of this topic, 

Link to comment
Share on other sites

@mortezamobariz Thanks a lot for taking time to check my model. But I think here is one problem. I mistakenly uploaded the etabs file in which I have deleted all the cantilever beams and just slab has remained. I am uploading the file that has cantilever beams. 

house for thulo kancha uncle 2.EDB

Edited by Beenay Beenay
Link to comment
Share on other sites

14 minutes ago, Beenay Beenay said:

@mortezamobariz Thanks a lot for taking time to check my model. But I think here is one problem. I mistakenly uploaded the etabs file in which I have deleted all the cantilever beams and just slab has remained. I am uploading the file that has cantilever beams. 

house for thulo kancha uncle 2.EDB 270.12 kB · 0 downloads

Please open the file which i uploaded. I have modified it with Etabs version 16.0. Download Etabstran2013 and convert the file to ur workable version.

Again I will suggest u that section modifiers have very important role to play. You need to take care of the case i-e whether it is equilibrium torsion or compatibility torsion in order to decide torsion modifier for section.

As far as Ixx and Iyy modifiers are considered, if u go with 1 as section modifier ur section has greater stiffness. Greater stiffness means greater attraction of loads towards itself. As it takes more load in case with section modifier 1 u need more shear reinforcement because more load means more shear demand on the member. Now in such cases the required shear reinforcement exceeds the section capacity and as a result section is dislayed as failed. Also these are short span members and such members are very critical to shear than flexure failure. This failure is referred to as deep beam failure. Please check definition for deep beam in Aci code.

If u go with the other option with section modifiers for moment of inertia as 0.35 (as suggested by ACI) which is pretty much valid for under reinforced cracked sections, it is actually the real representation of the beam element. In such cases less loads will be taken by the beams and consequently less shear demand. please use the section modifiers as suggested and then see ur structural elements. Thanks

Link to comment
Share on other sites

Apparently, you have a "load transfer problem".

The first and foremost thing that is expected is that reactions should equal applied loads. This should always be checked by design engineers unfortunately  this doesn't happen so often. If your applied loads don't match reactions, there is no point in discussion "Design Results" because your are designing for a model that doesn't represent "actual conditions".

For your situation, have you tried only modelling the balcony beams in a new ETABS model and check the reactions as suggested above? 

Or did you try isolating the load combinations and checking reaction for each load case against manual calculation as suggested above to pin down the load case that is causing problem?

Other items that you can do is apply your loads on cantilever as line loads.

I also want to comment that this thread is a perfect example of why SEFP should ban people from sharing their models. Everyone, expects someone else to check and figure out the problem and the discussion about potential problem is lost. Other items that are observed are that original poster (generally speaking) may only entertain the replies that require less to zero effort and totally avoid or not answer things that require him to crunch some manual numbers or to do math. Something that Admins/Moderators can consider. I believe this will improve the quality of discussion on this forum.

 

Edited by Ayesha
Link to comment
Share on other sites

On 8/22/2019 at 10:07 PM, Beenay Beenay said:

@mortezamobariz Thanks a lot for taking time to check my model. But I think here is one problem. I mistakenly uploaded the etabs file in which I have deleted all the cantilever beams and just slab has remained. I am uploading the file that has cantilever beams. 

house for thulo kancha uncle 2.EDB 270.12 kB · 1 download

I suggest that redefine your section and remodel the members that fails

also don't forget to check your load pattern, load case and mass source carefully. 

Link to comment
Share on other sites

  • WR1 locked this topic
Guest
This topic is now closed to further replies.
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       