Buoyancy Pressure on Raft.
Hamza Ahmad
AOA!!
Which parameters should be consider for design of raft foundation if the bottom of foundation is 2' above the GWT ? To be on conservative side, should we apply upward pressure (unit weight of water x 1'or 2') on  the bottom of raft foundation?
Edited by Hamza Ahmad
On 11/22/2019 at 6:06 AM, Hamza Ahmad said:
AOA!!
Water table can seasonally fluctuate and you can have a condition where the soil below raft is submerged in water. In that case, bearing capacity of the soil would be reduced to some degree. Speak with your geotechnical consultant to get the exact number.
You can do a separate buoyancy check if you want but I don't suggest providing an uplift pressure and you might not end with a lower bound solution.
Uplift on a Raft:
Groundwater table fluctuates;
However, site investigation companies can monitor GWL (piezometers are used for this purpose) over time and get a fair assessment of the water table. If you are founding on impermeable clay, then you can get a perched ground water table and pressure.
In some countries with a lot of rain they assume GWL at 1m below ground level .... unlikely in majority of Pakistan where ground water levels/table are sinking (a major worry for future PK generations that we are not now addressing in our ignorance).
Uplift Calc: Working to metric units:
2' above GWL = 0.6m;
Uplift = 10x0.6= 6kN/sqm (can be resisted by 0.25m (equivalent to 10" thickness of concrete!) - hence uplift should not an issue! RAFT and building DEAD WEIGHT would be much greater!
Say FoS= 1.1 against uplift and take Dead weight load factor as 0.9, for conservative design check.
As @Ayesha said check fluctuation of Ground Water Table with the geotechnical engineer - geotechnical Engineers and their investigation report worth needs to be appreciated!
There may be other practical construction related issues with constructing a raft under water - hence ground water level would need to be temporarily lowered - should not be an issue of the experienced builder who knows what he is doing.
Is this correct to calculate Buoyancy force only for 2' depth? shouldnt be the buoyancy force equivalent to the confined heigth of water? say if EGL is 8' above the Raft, then the buoyancy force should be 8*62.4 psf upward. correct me please.
Edited by callmeismail
Normally what I have seen is that almost all Client Specifications require buoyancy checks to be done assuming GWT is at grade irrespective of where it is  (to account for seasonal fluctuations and also because the approach is conservative). You only need to consider buoyancy for the volume of concrete that is displacing the water (assuming water table is at grade). For soil, you will have submerged unit weight that accounts the buoyancy affects.
Water pressure uplift - further thoughts
@UmarMakhzumi approach is safe so go with it.
Such technical deliberations, are also a matter of qualitative assessment by the Engineer.
Engineers everywhere take a different approach to ground water level. Here we assume the water table (i.e. a possible perched water table) at 1m (3.3’) below ground level - for a conservative approach to basements uplift calculations, unless we have definitive information otherwise.
If the structure is in water, or underwater, then the water level is taken as top tide level, or floor plain level.
Do remember water density is 1000kg/cum (62.4 p/cuf) whilst concrete is 2500kg/cum (156 p/cuf) ... therefore 400mm thick concrete slab equals to buoyancy force from 1m (3.3') on water uplift - then add the factor of safety. Then there is also the 'permanent' dead weight of the structure above too.
For shallow basements or structure,  2ft as you say, it may not be an issue provided there is sufficient dead concrete/structure weight?
For un-factored loading - Factor of Safety against uplift, I use is 1.2 - some codes use 1.25.
Most of the time dead wight of structure is well above uplift forces on shallow basements - there may be a need to control ground water pressures during construction of say basement slabs. Often water lowering (say pumping) methods are used during construction; Or you can use tension piles to hold the basement slab down against uplift for very deep basements.