Improve Bearing Capacity of Soil
Muhammad Ameen Ali
  • 4 weeks later...
There are many factors that need to be considered here, to answer the post properly:
1. Type of soil - cohesive or non-cohesive? Techniques are different for both.
2. There are many techniques for improving soil bearing capacity. What techniques are readily available in the local market?
3. Water table level - impacts bearing capacity is sandy soils;
4. Is ground settlement your concern?
5. Working in metric units:  kN & m;     0.75 tsf (80kN/sqm) to 1.8tsf (190kN/sqm): You must consider the "overburden removed". Two basements means (say 7-8m dig), therefore overburden (soil) removed would be 18kN/cum times say 7m = 126kn/sqm (1.3 ton per sq ft pressure removed). i.e. bearing pressure at the depth would be Pb+1.3tsf ...close to what you want. .... the key being water table or finding a low strength soil like "peat", in such or similar low strength ground cases  ground improvement or piling solution would be needed - don’t undervalue the expertise of a geotechnical engineering specialist - consult them always!
6. Immediately after the dig protect the formation level surface by blinding with 75mm lean mix concrete or say 100mm of small stone gravel sub-base;
7. Raft footings - depending on thickness and stiffness, tend to then spread load over a large area, and would limit settlement etc. Not sure why a raft is needed in this case, as technically you have a 6-storey building - unless ground is very poor?
8. You have six/seven storey building - say superimposing a total load of 75kNsqm - 0.8ton per sq ft -  (load obviously concentrated on column locations)!
Hope this helps?
On 12/29/2019 at 8:46 AM, UmarMakhzumi said:
You are better off using a different foundation system if your bearing capacity is super low than expected. Have you considered piling? You can use friction piles if loads are low.
Piling is impossible due to site conditions.
Hope this helps?
Thankyou Sir for your suggestion
i answers below your all points according to site condition.
1. partly cohesive soil.
2. At site Soil compaction possible.
3. water table depth about 500feet.
4.Yes
5. Already 30feet excavation was done long time ago, there is no secant piles for the retaintion of letarel soil pressure, if i go for piling .
and at that 30feet bearing capacity is 0.75tsf.
7. Yes this building is supported by Raft footing, there is no other option.
8. how you can total load on column is 0.8tsf
Sir i am searching for the solution that how to compact the soil to increase the bearing pressure upto atleast 1.5tsf and what is the methodology of compaction.
1. Engineers need to be specific on soils - 'partly cohesive' can mean many things. Is there a site investigation report ? i.e have boreholes been undertaken to identify soil types etc below the excavated surface? One should always have a geotechnical / soils report for the site before undertaking any ground-works, such as compaction. Get a soils site investigation done first! Depth of boreholes ( i would suggest 5, 4 near corners and one in middle) below raft should be at least equal to width of raft;
In this case as the overburden has been removed for sometime, the soil may have heaved (up) and this will settle as building load is applied! See option below with layer of 400mm small stone replacement;
2. After SI compaction options: 1, Dynamic compaction from height (could cause vibration to adjacent structures!); 2. Impact compaction special compaction adaption fixed to excavator; 3. rollers etc; 4.  I would removed 400mm of top soil and put in stone compacted by roller, placed in 100mm layers; This will provide a good hard surface locally.
3. OK, water table is low...good... don't forget it will rain and if soil has too much clay you will get a perched water table around the basement!
4. Very difficult to judge if all future settlement will be taken out by compaction technique; use of raft footings will help limit this or the settlement will be uniform;
5. Basement walls will resist any lateral pressure - secant wall is only need for an excavation where site is tight and excavation slopes are not possible?
6. -
7. Raft ok
8....blank load on raft .... at column 0.8tsf (say 75kN/sqm) ... if columns are at say 6m centres then typical INTERNAL column load would be: 75x7x7 = 3675kN (or 0.8 x 21 x 21 = 350t) - for example!
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik