AoA Members,
1)  As per UBC  torsional irregularity exists if "Maximum story drift, computed including accidental torsion, at one end of the structure transverse to an axis is more than 1.2 times the average of the story drifts of the two ends of the structure".
In our general practice, we compare the ratio of maximum displacement to average displacement with 1.2 to confirm if the torsional irregularity exists or not. But as per the above stated UBC Statement, we should consider the story drift instead of displacement. What could be then the possible reason for considering displacements instead of Story drift?
2) If ratio of Story drifts are to be considered for torsional irregularity check, then In ETABS 2016 there are two types of tables for drifts, one is " Story Max/Avg Drifts" and the other is "Diaphragm Max. / Avg. Drifts"(Pic Attached). Which is to be considered and what is the difference in between story drifts and diaphragm drifts?
3) What does accidental torsion means in the above statement and how it is calculated?
Edited by M.Arslan Umar
Accidental torsion: distribution of floor mass could be eccentric with respect to center of rigidity of lateral load system.
You do not calculate accidental torsional, you just assume it be displaced equal to 5 percent of building's dimension perpendicular to seismic force.
Drifts or displacement: drifts are displacements normalized by story heights. You will get the same result. No difference at all.
Thanks and Regards
A few further thoughts on ‘accidental torsion’, and how to compensate for it in structural design. I would agree with @BAZ comments above.
There seems to be too much reliance on “computer software outputs” with little understanding of converting the analysis output to practical structural design details – I may be wrong.
If for example the lateral forces resistance system, say lift core walls, are located bang on CENTRAL in the building, and no other shear walls are provided, then there will be global torsion that would be greater during an event, than if there are shear walls or cores on the four corners of a rectangular building. The structural elements (slabs, columns, walls etc) are then designed to cater for this torsion & any eccentricity.
It is important that the SE appreciates that the ....
1. Plan geometry (layout) of the building;
2. Location and distribution of the lateral forces resisting system (i.e. shear walls, braced bays and cores)
...do matter in limiting earthquake damage.
The use of infill blockwork walls as is common in PK. With no physical (vertical) shear tying/transfer of the infill panels to columns for force transmission, limited shear resistance is achieved, hence limited benefit. If infill panels are part of the lateral forces system, then they need to be detailed and tied to the column (never done?) .... the builder on site does not understand the structural robustness matters pertaining to infill panels ... he only gets paid for putting up more walls in a day!
Hi Arslan, I just came across this and since its a very old post you might already have your answers. But just to share my two cents, we should check the torsional irregularity against story drifts. However, we should calculate the amplification factor "Ax" based on story displacements. There are instances where you have torsional irregularity along an axis in a building (checked against story drifts) but your amplification factor is less than 1 (checked against story displacements), so you don't need to apply it. Its still important to check whether torsional irregularity exists along both axes or not to determine whether we need to consider orthogonal effects in our load combinations. I'm attaching an excerpt from "Guide to the Seismic Load Provisions of ASCE 7-16" to clarify the point about checking torsional irregularity and calculating Ax against story drifts and displacements respectively. This applies to UBC 97 as well.
Both options would give you same results if you have a single diaphragm per story.