Insulated Concrete Load Bearing Wall Penals


Recommended Posts

 Wall panels are required to be designed which should be load bearing as well as insulated. A concept is developed to build such panels with total thickness of 8” (20 cm), having two layers of high-performance concrete sheets on the sides filled with the insulation, each of these two sheets to be of 3-4 cm thick reinforced concrete, using welded wire mesh as reinforcement, both sheets should be linked with vertical reinforced concrete ribs (columns) placed at short distance, in order to; (1) provide enough stiffness against axial load and buckling, (2) carrying the built-in beam to transfer the load of slab and (3) the entire panel will work as bracing for the frame structure to take the lateral loads in seismic zones. In addition to that the house construction with such panels is assumed to be more economical than the overall brick and concrete structure.

The question is that how can we perform the analysis and design calculation of such panels especially can we use ETABS to conduct such analysis and design calculations? If yes, please let me know how? As I have tried to find out in my ETABS 2016 but could not. There is a provision for core wall design but not the hollow insulated wall as mentioned above.

Thanks and best regards.

Aslam

Link to comment
Share on other sites

Here are a few observations - i am not a user of ETABS, so my comments are of a general nature.

1. Shear walls have large lateral (wind, earthquake) forces that are transferred from the floor diaphragms down to the foundations. The connections between precast wall panel and floors/columns should be able to transfer (shear) load; This often is not possible unless reinforcement crosses through the insulation and connects the wall to the floor/column element. You cannot rely on four connectors at corners or pure friction of concrete to concrete.

2. For a 200mm (8") panel, one would require minimum 50mm (2") insulation to achieve any meaningful thermal benefit. This leaves two concrete biscuits of 75mm each. I m assuming theses are connected around the perimeter only? Ii there any connection of reinforcement (truss-like) between the panels with panel area?

3. I think the system may be ok for say 2-storey low rise building.

4. For modelling i would take 200mm - 50mm = 150mm thick panel.

See what other learned colleagues say. 

Link to comment
Share on other sites

This topic has been discussed in the forum in detail. Please check this topic.

 

Also, a good resource for masonry properties is  NCMA TEK 14-1A publication. You should be able to get it off google. I am attaching TEK 14-01B with this reply. It is a freely available resource. 

 

TEK 14-01B.pdf

Link to comment
Share on other sites

On 4/18/2020 at 6:24 PM, Simple Structures said:

Here are a few observations - i am not a user of ETABS, so my comments are of a general nature.

1. Shear walls have large lateral (wind, earthquake) forces that are transferred from the floor diaphragms down to the foundations. The connections between precast wall panel and floors/columns should be able to transfer (shear) load; This often is not possible unless reinforcement crosses through the insulation and connects the wall to the floor/column element. You cannot rely on four connectors at corners or pure friction of concrete to concrete.

2. For a 200mm (8") panel, one would require minimum 50mm (2") insulation to achieve any meaningful thermal benefit. This leaves two concrete biscuits of 75mm each. I m assuming theses are connected around the perimeter only? Ii there any connection of reinforcement (truss-like) between the panels with panel area?

3. I think the system may be ok for say 2-storey low rise building.

4. For modelling i would take 200mm - 50mm = 150mm thick panel.

See what other learned colleagues say. 

Thanks for your valid observations. Yes, there are a few elements which I supposed to mention which are follows:

1- The panels would not only be connected at four corners only to the plinth beam or foundation, if so, you are right; in such case we cannot transfer the sheer forces on the joints. Actually, both side layers of each panel have reinforced concrete connectivity at every 45-60 cm, which will increase the effective stiffness of overall panel to counter the buckling as well as to cary the load of beam and slab to the foundation. In addition to that these connectors will have the rebar dowels inserted coming out of the plinth beams or foundation. These inserted rebar dowels will be grouted with special grout having compressive strength of no less than 30-40N.  

2- Insulation is required to be of 100 cm think in order to increase the thermal insulation and to decrease the thickness of side layers concrete to 50 mm with concretors at 450-600 mm C/C. These elements of concrete (layers and connectors) will be made of high-performance concrete with increased ductility. Instead of considering 150mm thick simple sheer wall, we need to run it as a composite panel as mentioned, in order to acheive good ecconomy scale. This is the reason we need to run it in ETABS with different configration of this panwl to acheive the optimum thickness of the layers and connectors.   

3- Moreover, it is important to note that this concept will provide a highly effective bracing system, bracing all the beams and corner columns diagonally at both levels (top and bottom) which works well to counter high lateral loads.

Herewith attached is the section of panel for clearer picture.

Panel Design.pdf

Link to comment
Share on other sites

7 hours ago, Ayesha said:

This topic has been discussed in the forum in detail. Please check this topic.

 

Also, a good resource for masonry properties is  NCMA TEK 14-1A publication. You should be able to get it off google. I am attaching TEK 14-01B with this reply. It is a freely available resource. 

 

TEK 14-01B.pdf 261.57 kB · 1 download

Thanks for the document, it is useful to see the properties of blocks. We have been using such insulated blocks in UAE for long time. They provide good insulation and same time you can design load bearing walls too by some types of those blocks. 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       