How to design a greenhouse shed


Usman Altaf
 Share

Recommended Posts

Hi All,

I am designing a greenhouse that has steel as main supporting members and polythene sheet as cladding. Have a look at this image.
My Client wants a minimal design. The governing loading is wind load. 

We all know that polythene sheet has significantly less strength as compared to steel and designing the steel frame assuming that the wind pressures are fully resisted by polythene cladding is not wise and would lead to a over design.

 

I have following 2 questions:

1. Am I right that I should reduce the wind intensity/ wind forces on the steel members by a coefficient due to the presence of polythene sheet vs Steel, as it will burst/ puncture far earlier before resisting all the design wind pressures.

2. How to measure wind pressure sustaining capability of a polythene sheet. I knows its thickness (200 micron) and I know its tensile yield strength (20MPa). I know the spans across which its supported on the steel (300mm and 500mm). Is the method for calculating tensile stress similar to method used to determine tensile stress in steel sheet supported on all four sides (the coefficient method). or is there another method. Please guide. 

Thanks

Usman

02420385-ca0e-450a-b485-28597a596eed.jpg

Link to comment
Share on other sites

11 hours ago, Usman Altaf said:

1. Am I right that I should reduce the wind intensity/ wind forces on the steel members by a coefficient due to the presence of polythene sheet vs Steel, as it will burst/ puncture far earlier before resisting all the design wind pressures.

This is tricky. The sheet would be punctured only if a sharp object tears through it. Surface area wind might not be able to puncture plastic. It might cause some permanent deformation (strain based) but the thing might stick there.

Enclosed or partially enclosed sheds also have internal pressure that adds to members in addition to externally applied pressure. 

There is no horizontal and vertical bracing provided for the structure . The structure might be unstable. There should be some bracing no matter how small or big the wind load is.

11 hours ago, Usman Altaf said:

2. How to measure wind pressure sustaining capability of a polythene sheet. I knows its thickness (200 micron) and I know its tensile yield strength (20MPa). I know the spans across which its supported on the steel (300mm and 500mm). Is the method for calculating tensile stress similar to method used to determine tensile stress in steel sheet supported on all four sides (the coefficient method). or is there another method. Please guide. 

You can get these values from the manufacturer. If the manufacturer that you are using has no data like that you can google to see what other manufacturers provide an establish a basis for your structure design.

Out of curiosity, how are these poles connected with the structure below? How are you resisting the tension due to wind.

 

 

 

Link to comment
Share on other sites

7 hours ago, Ayesha said:

This is tricky. The sheet would be punctured only if a sharp object tears through it. Surface area wind might not be able to puncture plastic. It might cause some permanent deformation (strain based) but the thing might stick there.

Enclosed or partially enclosed sheds also have internal pressure that adds to members in addition to externally applied pressure. 

There is no horizontal and vertical bracing provided for the structure . The structure might be unstable. There should be some bracing no matter how small or big the wind load is.

You can get these values from the manufacturer. If the manufacturer that you are using has no data like that you can google to see what other manufacturers provide an establish a basis for your structure design.

Out of curiosity, how are these poles connected with the structure below? How are you resisting the tension due to wind.

 

 

 

Got your point.
Yes.

there is bracing provided in alternate/ end panels.

Manufacturer of materials normally share the mechanical properties. I have those with me. I was curious if method of determining plate stresses will be applicable or not.

The poles, i mean the columns have a proper concrete base, base plate and anchor bolts. They are not appearing in the picture.
Thanks for your response. 

 

So to conclude your point, you are opting that i should not reduce the wind intensity and total force applicable on frame elements?

Link to comment
Share on other sites

On 4/23/2020 at 12:00 AM, Usman Altaf said:

So to conclude your point, you are opting that i should not reduce the wind intensity and total force applicable on frame elements?

You shouldn't do any reductions and also your members look too flimsy. You should check KL/r.I doubt they would pass.

 

Link to comment
Share on other sites

Just to add a bit more to what is said above, these structures are a combination of Strut and ties capable of full design loads as per codes, they take tension and compression only with pinned connections. 

Link to comment
Share on other sites

2 hours ago, Nustian371 said:

Just to add a bit more to what is said above, these structures are a combination of Strut and ties capable of full design loads as per codes, they take tension and compression only with pinned connections. 

This would be true if it was a pure space truss. The V in between will take the loads as compression tension couple, but the bottom and top chord will have flexural stresses as they are "bending".

 

Link to comment
Share on other sites

1. The wind loading should not be reduced, even with fabric structures - the give (flexibility) in the polythene  even could create dynamic loading (flapping of the sheet) causing both pressure/suction quickly, one after the other.

2. I can see that one gable end is closed. If the other end is fully open, then you can get is known as a "dominant opening effect" which increase wind pressure inside the structure. You see this is large aircraft hangers with large open doors. If both ends are open then the dominant opening effect is greater - for your structure you do not need to worry.

3. The issue will be wind uplift on the foundations - ensure weight of foundation is heavier than net total wind uplift... this is key check. I am assuming you have concrete beam strip foundation that the structure is bolted, and the factor of safety against wind uplift varies from 1.2 - 1.4 depending on code used.

4. The structure you have is a "tied-arch" in my view. You can use either a computer analysis or empirical formulae book for various wind loading - you can undertake a simple design using Roark's book.

image.thumb.png.591f8ac5c93e0332a3892824d39316af.png

5. For lateral (side-way) movement and sway I can see you have have a knee brace to provide lateral stiffness at the the eaves location (where horizontal tie / column meet).

image.png.9009f8ae4db5f3ba55d4f25261839822.png

This alone may not be enough and you may need to provide base fixity (4-bolts fixed base) at base of column and foundation junction.

6. Wind loading on tied arches can vary - here are a few permutations for you to thinking.

image.thumb.png.03eef2c3a6a171f34da9810f02b4d987.png

 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.