Jump to content
  • Welcome to SEFP!

    Welcome!

    Welcome to our community forums, full of great discussions about Structural Engineering. Please register to become a part of our thriving group or login if you are already registered.

Torsion Releases For Balconies


Osama Anwar
 Share

Recommended Posts

Assalaam o Alliakum Everyone!

I was wondering that if we could apply torsional release to the beam between the slab and balcony as shown in the attachment.

Moreover, what about the beams at the side of balconies? What about beam at outer side of balcony?

Screenshot (28).png

Link to comment
Share on other sites

You can can take away the ability of balcony-beam to take torsion in this case as the beam is not the only load path available. However, you have to design it for cracking torsion at-least as per guidelines of ACI 318.

The beam on sides and the outer end are not needed. Slab is enough to carry forces if it  is normal balcony of less than 6 feet in width.

 

Link to comment
Share on other sites

Attached is another solution. You can add new beams. Red and Blue.

The end condition for Red beams can be pinned/ moment released. For Blue, the end towards the red beam can be pinned/ moment released only. The size of blue beam should be same as balcony beam. 

Thanks.

 

image.png

Link to comment
Share on other sites

Good points made by BAZ & Umar.

Just to add, there is more than one way to skin an animal, as they say – here is another approach to take.

The third option would be not to put in "releases" and to "detail" the beam appropriately for torsion - this means the longitudinal bars in the beam may increase in size, and the links (stirrups) are detailed as torsion links. Transferring “releases” from computer software to the steel fixer on site can be tricky. Concrete behaves as you detail it!

It is the combination of vertical shear and torsion that induce cracking and failure - unless the reinforcement (longitudinal & links/stirrups) are detailed to cater for it for it. In the beam there will be additional longitudinal reinforcement in the top, bottom AND SIDES to cater for any torsion.

The figures below may help you understand the "practical" on site concept of catering for torsion with properly detailed reinforcement.

1.     What is torsion:

 

2.     Below is a torsion "link" or "stirrup" shape – what it looks like:

 

 

Below is a torsional situation: In Pakistan always include a bar in bottom (shown red) of cantilever balcony ALSO, same shape as top bar, but bend up and around towards to top of beam/slab, to allow for load reversal during an earthquake!

 

 

When I built my house in Pakistan, the steel fixer managed to bent one bar thus for the balcony - the workers in Pakistan (where material is expensive and labour is cheap) are very talented, but do not have the technical know-how sadly..... that's the challenge for the likes of you the structural engineer to disseminate down!

 

 

Keep an eye on this forum. There is Pakistan RC Building Reinforcement Detailing Manual in preparation and will include this torsion detail now that it has come up here! This Manual be an advisory document but will assist both "young" structural engineers and reinforcement detailers (draftsmen) to understand reinforcement detailing and fixing!

Passing down knowledge – think of it as “zakat”, then it gets easier then to give and share!

 

 

image.png

image.png

image.png

image.png

image.png

Link to comment
Share on other sites

On 6/17/2020 at 2:54 AM, Badar (BAZ) said:

You can can take away the ability of balcony-beam to take torsion in this case as the beam is not the only load path available. However, you have to design it for cracking torsion at-least as per guidelines of ACI 318.

The beam on sides and the outer end are not needed. Slab is enough to carry forces if it  is normal balcony of less than 6 feet in width.

 

What if there is a line load along the sides of balcony? I have a 0.65 k/ft line load at sides and 0.3 k/ft at front beam. Btw my balcony is 4' wide.

9 hours ago, UmarMakhzumi said:

Attached is another solution. You can add new beams. Red and Blue.

The end condition for Red beams can be pinned/ moment released. For Blue, the end towards the red beam can be pinned/ moment released only. The size of blue beam should be same as balcony beam. 

Thanks.

 

image.png

Should I provide beams if balcony is 4' wide? Rooms are 12.25' x 17.75'. Balcony is 8' long.

I have attached the photo below for visual aid.

I thank you from the bottom of my heart for such deep insights. May Allah grant success to all of you in here and hereafter. Jazak Allah.

WhatsApp Image 2020-06-15 at 11.26.16 AM.jpeg

Link to comment
Share on other sites

1 hour ago, Osama Anwar said:

Should I provide beams if balcony is 4' wide? Rooms are 12.25' x 17.75'. Balcony is 8' long.

You should at-least try the suggested solution. It will fix your model. There are other good points raised by other members that you can consider as well.

If the load on balcony is not much(not sure as I see a masonry facade in the picture) you can also try designing it as a cantilever slab.

Thanks.

Link to comment
Share on other sites

59 minutes ago, UmarMakhzumi said:

If the load on balcony is not much(not sure as I see a masonry facade in the picture) you can also try designing it as a cantilever slab.

Don't Consider the middle part but only the side buildings. You would be able to see masonry facade. 

InkedWhatsApp Image 2020-06-15 at 11.26.16 AM_LI.jpg

Link to comment
Share on other sites

3 hours ago, Osama Anwar said:

What if there is a line load along the sides of balcony? I have a 0.65 k/ft line load at sides and 0.3 k/ft at front beam. Btw my balcony is 4' wide.

This does not mean you need beam under the line load. The line load at the end will act as point load per unit width of your balcony. The line load at sides can be treated as line for that unit width of balcony. No  beams are needed,which means you will not have forces which need enlarged cross-section. Do your calculations; figure out bending moment and shear at critical section;  you will know.

Link to comment
Share on other sites

3 hours ago, Badar (BAZ) said:

This does not mean you need beam under the line load. The line load at the end will act as point load per unit width of your balcony. The line load at sides can be treated as line for that unit width of balcony. No  beams are needed,which means you will not have forces which need enlarged cross-section. Do your calculations; figure out bending moment and shear at critical section;  you will know.

You mean I convert line load into area load and apply it on balcony slab?

Edited by Osama Anwar
Link to comment
Share on other sites

If there is a masonry wall won't it create serviceability issues? It was the reason a decided to provide beams.

On 6/18/2020 at 6:15 AM, Badar (BAZ) said:

This does not mean you need beam under the line load. The line load at the end will act as point load per unit width of your balcony. The line load at sides can be treated as line for that unit width of balcony. No  beams are needed,which means you will not have forces which need enlarged cross-section. Do your calculations; figure out bending moment and shear at critical section;  you will know.

I'm really sorry can you explain it again. I didn't get it. You mean I design slab as a cantilever beam with a point load at end (equal to UDL at face) + UDL (equal to udl at sides) throughout span of 4'. What about the area loads on slab L.L. L.L etc? 

Link to comment
Share on other sites

On 6/18/2020 at 6:15 AM, Badar (BAZ) said:

This does not mean you need beam under the line load. The line load at the end will act as point load per unit width of your balcony. The line load at sides can be treated as line for that unit width of balcony. No  beams are needed,which means you will not have forces which need enlarged cross-section. Do your calculations; figure out bending moment and shear at critical section;  you will know.

 

On 6/19/2020 at 9:02 AM, Badar (BAZ) said:

You can do the same for section B-B

balcony.png

Sorry for the late reply.

I calculated the shear and bending moment at outer face of balcony beam (not at a distance d from balcony beam, just to be more conservative). I solved for section B-B only but also included the Imposed dead load and live load and self weight of balcony. 

Shear came out to be 4656 lbs and Moment came out to be 120384 lb.in. 

Effective depth was 4.72. So 6in slab without beam would be sufficient in my case.

Spacing came out to be 7.06 for #5 bar. I would be going with 6 in c/c.

 

Link to comment
Share on other sites

On 6/18/2020 at 1:24 AM, Simple Structures said:

Good points made by BAZ & Umar.

Just to add, there is more than one way to skin an animal, as they say – here is another approach to take.

The third option would be not to put in "releases" and to "detail" the beam appropriately for torsion - this means the longitudinal bars in the beam may increase in size, and the links (stirrups) are detailed as torsion links. Transferring “releases” from computer software to the steel fixer on site can be tricky. Concrete behaves as you detail it!

It is the combination of vertical shear and torsion that induce cracking and failure - unless the reinforcement (longitudinal & links/stirrups) are detailed to cater for it for it. In the beam there will be additional longitudinal reinforcement in the top, bottom AND SIDES to cater for any torsion.

The figures below may help you understand the "practical" on site concept of catering for torsion with properly detailed reinforcement.

1.     What is torsion:

 

2.     Below is a torsion "link" or "stirrup" shape – what it looks like:

 

 

Below is a torsional situation: In Pakistan always include a bar in bottom (shown red) of cantilever balcony ALSO, same shape as top bar, but bend up and around towards to top of beam/slab, to allow for load reversal during an earthquake!

 

 

When I built my house in Pakistan, the steel fixer managed to bent one bar thus for the balcony - the workers in Pakistan (where material is expensive and labour is cheap) are very talented, but do not have the technical know-how sadly..... that's the challenge for the likes of you the structural engineer to disseminate down!

 

 

Keep an eye on this forum. There is Pakistan RC Building Reinforcement Detailing Manual in preparation and will include this torsion detail now that it has come up here! This Manual be an advisory document but will assist both "young" structural engineers and reinforcement detailers (draftsmen) to understand reinforcement detailing and fixing!

Passing down knowledge – think of it as “zakat”, then it gets easier then to give and share!

 

 

image.png

image.png

image.png

image.png

image.png

I have not changed torsional coefficient to 0.01 for my balcony beam so I guess I could go with your configuration. What would be the development lengths in this case?

Someone said to me that another alternative could be to just extend the bars into the slab by same length (in my case it would be 4'). What is your comment on that?

 

Link to comment
Share on other sites

Designing buildings via such forums can lead to engineering failures - its a dangerous thing.

This forum is for general advise, and then you as the engineer need to make the necessary engineering judgement based on your knowledge and experience.

However, as rules of thumb:

1. Which code are you designing the concrete to? American or European?  Follow the rules given in the code!!

2. Here is general advice, based on European Codes.

For say 30N/mm2 concrete strength, and straight ribbed bars:

ANCHORAGE:

Good concrete/rebar bond conditions, good quality control: 40 x bar diameter;

Poor concrete/rebar bond conditions, poor quality control: 60 x bar dai

 

LAPS: 30 N/mm2 conc

Bar laps, good bond, good conc quality control on site: 60 x bar dia

Bar laps, poor bond, poor quality control on site: 90 x bar dia

 

Below are defined "good" and "poor bond" conditions. If your slab is less than 250mm thick, then you have good bond condition, provided there is good concrete quality control regime on site. Quality is not something Pakistan construction sites are renowned for from my limited experience.

image.thumb.png.d23272c5297f7c1f6dfd3bc37b705515.png

 

 

 

 

 

Link to comment
Share on other sites

7 hours ago, Simple Structures said:

This forum is for general advise, and then you as the engineer need to make the necessary engineering judgement based on your knowledge and experience.

1. Which code are you designing the concrete to? American or European?  Follow the rules given in the code!!

 

The project I am working on is kind of an assessment. It is my first time so I want to explore different options and alternatives to expand my engineering knowledge. I am very thankful to all of you for your guidance and deep insights. I am very happy to find you guys who can guide me regarding the problems faced by structural engineers in Pakistan. I hope to benefit from you guys in the future.

I am using ACI. Slab thickness is 6" and fc' is 3000psi.

Edited by Osama Anwar
Link to comment
Share on other sites

  • 9 months later...
On 6/25/2020 at 7:52 AM, Osama Anwar said:

The project I am working on is kind of an assessment. It is my first time so I want to explore different options and alternatives to expand my engineering knowledge. I am very thankful to all of you for your guidance and deep insights. I am very happy to find you guys who can guide me regarding the problems faced by structural engineers in Pakistan. I hope to benefit from you guys in the future.

I am using ACI. Slab thickness is 6" and fc' is 3000psi.

These Type of problems and Deep technical Ambiguites should/must be shared  to get the Experience Str Engineers opinions . I appreciate you on highlighting this issue and Thanks to all the Engineers who responded to your post

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.