Assalaam o Alliakum Everyone,

Can Anybody guide me regarding the values of L1 and L2 in the image attached below? It is "Fig. 5—Typical seismic-resistant details: flexural members." of ACI-315-99 Detailing Manual. And also are the values same for edge beams and continuous beams?

Screenshot (94).png

Link to comment
Share on other sites

1 hour ago, Simple Structures said:

The attached may help Anchorage ACI 318 calc procedure.pdf

Thank you so much for the reply. 

I was curious if we will apply this method when we are taking steel areas from ETABs? Does ETABs give values according to Ld or simply after L/3 for continuous part or L/4 for discontinuous part? I knew the procedure to drive Ld but this thing is annoying me. If we calculate the Ld values manually they will be shorter than L/3 (most probably) and there would be some part (L/3-Ld) which may have greater moment than the flexural strength. So won't it be conservative to use L/3.

Can you elaborate for which lengths (Ld or L/3 and L/4) ETABs give the 3 top and 3 bottom longitudinal steel area values? 

 

Link to comment
Share on other sites

Analyse on ETABS (and then detail drawing to L/4)- the extra bit helps during an earthquake dynamic loading - L/4 should be fine.

I am not a ETABS user myself .... but am learning that its Pakistan's most favourite analysis programme....wow!

As an engineer you should be able to calculate the MINIMUM anchorage (from previous information i sent you) and then always provide a bit more. My rule of thumb sketched below.

 

261989139_Simplifiedbeamdetailingrules.thumb.jpg.eaef45369c8cd9152b6744937149da2b.jpg

 

 

Link to comment
Share on other sites

As I said 

2 hours ago, Osama Anwar said:

I knew the procedure to drive Ld

I know how to calculate Ld for tension and compression and Ldh etc. Thing that confused me was that we do not have the Bending moment envelop. But I know Max +ive and -ive values from the software. And I have checked Longitudinal area of steel against them it is equal to manual calculations.

Suppose if my steel is as follows (which it is for one beam)

62528150_Annotation2020-07-09212451.png.ad9f32ea015fc8d8526b74dcaa9a5159.png

My B.M. diagram would be SOMEWHAT similar to this not necessarily.1539819218_Annotation2020-07-09212451.png.f9e96df15a7ef280ca5d62682b4bf25a.png

Seismic zone is 3 so I am getting high negative moments at ends.

So my Reinforcement would be somewhat like this

858399126_Annotation2020-07-09212451.thumb.png.daf49b8c91c5672635126a1a7883567a.png

Software must divide the beam in three pieces like this to get the value of highest moment in each section

359342517_Annotation2020-07-09212451.png.14276f9224250499672c2dd43c99f49c.png

ETABs do divide the section in three parts because sometime it would give highest value say at station 7.5". In short what I want to say is that the reinforcement values are not the values of moment at left end, middle and right end of beam but rather maximum moment values in the three respective sections. 

Suppose if steel area is 1.71 in left section then the highest moment (for which As came out to be 1.71) in that section may be lying at the start, end or in between of that section. What I am interested in is that what is the length of the section used by ETABs? In what proportion ETABs divide sections? Are all section L/3? Or first and last section is L/4 and middle is (L-2*L/4).

I calculated Ld and min length values as advised by you and got the following results

1425237391_Annotation2020-07-09212451.png.f973f7a7b2832319e063444e5840c476.png

Where Ln is clear length. 

If I am not mistaken, by 0.15*L+h you meant Ld>=0.15*L+h. Right?

In that case, top length would be 3.8375' and bottom would be 2.05. Right?

What I am is saying that what if ETABs is dividing sections in L/3 (or Ln/3) or even L/4 (or Ln/4) and Max moment is lying at the very end of section 1 at L/3 (or Ln/3) then would not it be under design if we take value as calculated through Ld>=0.15*L+h? Should not we be using Max(L/3,Ld,0.15*L+h)? 

 

 

Annotation 2020-07-09 212451.png

Link to comment
Share on other sites

ETABS divides the region of member to report forces and perform design based on the option shown in attached screen shot.

You can divide the member into different regions either by specifying minimum number of stations(sections) or maximum spacing of stations(sections).

The default setting is that it will check the beam at every section located at 500 mm distance along the clear length of the member (max station spacing).

See the attached screen shot of the ETABS's manual (CFD ACI 318-14) as well.

image.png

Screenshot (77).png

Screenshot (78).png

Link to comment
Share on other sites

image.png.729e676356ebe60a6545159857663861.png

1. Apologies - I can only think in metric units - so ASSUMING all the above numbers to be metric units , for argument sake, 

Then, If L/4 = 2.75, then L = 11 m

Therefore, 0.15L = 1.65m + depth of beam ..... which you say then totals 3.835m : This would mean your beam is 2.185m deep (L/5) which cannot be right! Get an Engineer in your office to check you numbers!

With regards to rebar from fixed ends: Left or right , one would take 100% of the reinforcement for distance GREATER THAN 0.15L+h, then take 60% to distance 0.3L+4, and so on. You could decide to take 100% to 0.3L+h length. It depends how many bars you have in top. These are detailing rules are guidance and you as the engineer need to make safe choices based on that.

For example, If you have 2 bars on top as 100% reinforcement, at say 0.15L+h you can splice them with smaller bars (60%), than after 0.3L+h, you can splice them again with small bars to take 40% etc. With so many splices, this is not practical, increases tonnage of rebar ... so based on ones engineering judgement, one would take the two bars to say 0.3L+ha and splice there with two small bars and just have two bars in top..... remember you have to do this from both ends, so it may be better and practical to take the 100% bars all the way across the top of the beam.

If you had 5 bars on top, you can go continue with say 3 bars after the point beyond 0.15L+h (stop two there) and then you are continuing on with 60% etc.

With seismic loading you will get M reversal at bottom (-ve M) so you may need to follow same rules for bottom bars.

-------------------------------------------------------------------------

2. Secondly, you must appreciate anchorage of top (& bottom) bars into the column needs to be sufficient to avoid joint failure. Calculate the anchorage length as shown "blue" on sketch below.... what the computer printout illustrates is inadequate! Your joint will fail under seismic loading .... or use long U-bars at ends in the  beam. You must provide sufficient anchorage of beam bars into the column, both top and bottom bars.... Calculate anchorage length from centre-line of the column !

Master "reinforcement curtailment into the beam &, anchorage into the column or wall".

 

image.png.066c2135d370c28df7e4e945959fd8c7.png

 

3. The BM envelope will come from gravity loads + seismic loads. Most computer programme give the BM diagrams envelopes for various load combinations.  Like I say I am not a ETABs user, leave to that to others to advise.

Below is an example - based on Eurocode EC2, the code i use - for beam pinned at LH side and continuous on the right... showing typical reinforcement curtailment based on BM. This is a general illustration only, and shows how BM Envelopes and Curtailment of reinforcement works.

When I trained as a structural engineer I had to follow a training sequence and learn three things: 1. Work as reinforcement detailer/draughtsman for two years, then work out and draw bending moment diagrams by hand for another few years for beams and frames, and then design by computer! 

image.png.3c7eeb29fa189c75f0352df761b64659.png

 

 

 

 

 

Link to comment
Share on other sites

8 hours ago, Badar (BAZ) said:

ETABS divides the region of member to report forces and perform design based on the option shown in attached screen shot.

You can divide the member into different regions either by specifying minimum number of stations(sections) or maximum spacing of stations(sections).

The default setting is that it will check the beam at every section located at 500 mm distance along the clear length of the member (max station spacing).

See the attached screen shot of the ETABS's manual (CFD ACI 318-14) as well.

image.png

Screenshot (77).png

Screenshot (78).png

Thank you so much for the reply.

8 hours ago, Badar (BAZ) said:

The default setting is that it will check the beam at every section located at 500 mm distance along the clear length of the member

ETABs neither considers full length (c/c) nor clear length while dividing the member into sections but average of both full length (c/c) and clear length like this

874991741_Annotation2020-07-09212451.png.31709b478e14c805597b8e846596e4bb.png

My default is at Maximum Station Spacing and number of stations are 24. This means that ETABs divide each member in 24 parts and report values for each load combination. I have checked it.

When we design our model ETABs give out 3 values for top and bottom reinforcement. I am interested to know that if members are being divided into 24 parts/sections/stations then each of the 3 values is being reported from highest of the 8 parts/sections/stations? i.e. left value is the highest values reported in the 8 parts/sections/stations on the left side and middle value is the highest values reported in the 8 parts/sections/stations located in the middle part of the member and right value is the highest values reported in the 8 parts/sections/stations located on the right side of the member. Right?

Link to comment
Share on other sites

On 7/10/2020 at 1:21 PM, Simple Structures said:

image.png.729e676356ebe60a6545159857663861.png

1. Apologies - I can only think in metric units - so ASSUMING all the above numbers to be metric units , for argument sake, 

Then, If L/4 = 2.75, then L = 11 m

Therefore, 0.15L = 1.65m + depth of beam ..... which you say then totals 3.835m : This would mean your beam is 2.185m deep (L/5) which cannot be right! Get an Engineer in your office to check you numbers!

Thanks for the reply

I deal with imperial units L/4 is not equal to 2.75. Ln/4 is equal to 2.75. And Ln=11' not L=11'. My beam depth is 24" and L is 12.25"

so 0.15*L+h = 0.15*12.25 + 24/12 = 3.875'

On 7/10/2020 at 1:21 PM, Simple Structures said:

image.png.066c2135d370c28df7e4e945959fd8c7.png

 

As I said my beam depth is 24" and I am using #6 (0.75") bar. Hook length greater than 12db (12*0.75=8) does not contribute in holding concrete. I see no reason to increase my hook length unnecessarily.

Edited by Osama Anwar
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.