AoA,
Need clarification about the concept of TS/YS ratio of reinforcing steel. There's a figure of 1.25, what does that mean, whats the reference and is it minimum or maximum. Further more ASTM-615 mentions min yield and tensile strengths for steel in Table-2 e.g. 60 000 psi for Grade 40 and 90 000 psi for Grade 60, does this allow specifies the range for the earlier grade upto the later or else.
Moreover kindly check the attached results, are these acceptable?
You can check these values against recommendation in ACI. The following excerpt is from ACI 318-08.
21.1.5.2 — Deformed reinforcement resisting earthquake- induced flexural and axial forces in frame members, structural walls, and coupling beams, shall comply with ASTM A706. ASTM A615 Grades 40 and 60 reinforcement shall be permitted in these members if:
(a) The actual yield strength based on mill tests does not exceed fy by more than 18,000 psi; and
(b) The ratio of the actual tensile strength to the actual yield strength is not less than 1.25.
From the commentary:
R21.1.5 — Reinforcement in special moment frames
and special structural walls
Use of longitudinal reinforcement with strength substantially
higher than that assumed in design will lead to higher
shear and bond stresses at the time of development of yield
moments. These conditions may lead to brittle failures in
shear or bond and should be avoided even if such failures
may occur at higher loads than those anticipated in design.
Therefore, a ceiling is placed on the actual yield strength of
the steel [see 21.1.5.2(a)].
The requirement for a tensile strength larger than the yield
strength of the reinforcement [21.1.5.2(b)] is based on the
assumption that the capability of a structural member to
develop inelastic rotation capacity is a function of the length
of the yield region along the axis of the member. In interpreting
experimental results, the length of the yield region has been
related to the relative magnitudes of nominal and yield
moments.21.8 According to this interpretation, the larger the
ratio of nominal to yield moment, the longer the yield
region. Chapter 21 requires that the ratio of actual tensile
strength to actual yield strength is not less than 1.25.
Members with reinforcement not satisfying this condition
can also develop inelastic rotation, but their behavior is
sufficiently different to exclude them from direct consideration
on the basis of rules derived from experience with members
reinforced with strain-hardening steel.
The restrictions on the values of fy and fyt apply to all types
of transverse reinforcement, including spirals, circular
hoops, rectilinear hoops, and crossties. The restrictions on
the values of fy and fyt in 11.4.2 for computing nominal
shear strength are intended to limit the width of shear
cracks. Research results21.9-21.11 indicate that higher yield
strengths can be used effectively as confinement reinforcement
as specified in 21.6.4.4.
I hope this answers your question.
On 7/9/2020 at 5:47 PM, Muhammad Nakhshab Ajaz said:
AoA,
According to ASTM A615 , the tensile strength for low carbon steel should be 1.25 times the yield strength. The values specified are based on lower bound values and in lab you should be definitely getting higher values than this. However the ratio of 1.25 drops below in case of high strength bars such as grade 90 and 105 where it is limited to 1.1 only. B