Hi!
Is there any way to design this type of Beam-Girder connection? The bottom one is the beam and the top one is the girder. There will be a pulley that will be running at the bottom of the beam that's why the beam has to be downwards. I tried Ram Commection and Idea statica but none has such connection templates. Can anyone advise me how should I design or analyze such type of connection?
This kind of connection is very common. What is the weight of the hoist/ trolley that would be running on the lower beam. The following  things should be considered.
1) Include impact forces (vertical, longitudinal, and lateral) for design of beam as well as connection.
2) I suggest adding stiffener between the two bolts on each side of girder.
3) Deflection of bottom beam should be limited to L/600 or vendor criteria whichever is more stringent.
4) 12 mm bolts are very small. Generally we don't use less than 19mm (3/4" bolts). Bolts should be ASTM A325 or A490.
5) For hoists,  bolts should be pretensioned. This is important.
Now, for designing such connection, you need to resolve the force at beam end for different position of hoists, the use the maximum value. You have 4 bolts, so calculate shear and tension for each bolt. Consider prying in your calculation. How to do the calculation is very simple. I don't have an example but you can get it from any text book on connection design.