Formula for short term horizontal displacement


Thila
 Share

Recommended Posts

Hi All,
How to calculate the short term horizontal displacement (with adopting cracked section of the concrete) on free standing wall with eccentric footing at bottom, which is subjected to wind pressure alone. This is same as calculating torque of cantilever wall.

This is a plot boundary wall with eccentric footing. 

Thank you

Link to comment
Share on other sites

Assuming the support of the wall is acting like an ideal fixed support, you can easily determine the deflection at the free end of a cantilever for uniformly distributed load using u=WL^3/8EI. To take into account the cracking of concrete you just need to use the effective moment of inertia in place of gross moment of inertia.

Link to comment
Share on other sites

Thank you for your response. .

Can I take “Ig” instead “Ie”, if Mservice /Mcracking <1, .Because, Ms is not exceeded the cracking moment. Also , kindly review the calculation below. If it is not correct, kindly guide me. Thank you

This is cantilever wall rests in eccentric footing, subjected to wind. The calculation is considering wind load only. kindly find attached for sketch

 l                                      1.1 kN/m

 l_________________mmmmmmmmmmmm

 l        0.85m                        2.5m

 l----------------l----------------------l

 

B = 1000 mm (taken per meter width)

D = 120mm (thickness of wall)

 

Ig = 1000 x 1203 / 12 = 144x106 mm4

 

n = Es/Ec = 200000/ 26587 = 7.52

Fr = 0.62 SQRT (32) = 3.56 N/mm2

Yt = 120/2 = 60 mm

 

Mcr = Fr*Ig/ yt = 3.56 *144x106 / 60 = 8.544 kNm

 

Ma = 5.775 kNm

 

Ma/Mcr <1, Hence Ie = Ig

Deflection = w (uniformly distributed) *l4 / 8*E*Ig

 

w = 1.1 kN/m = 1.1 n/mm

loaded length = 2500 mm

total length = 3350 mm

E = 26587 n/ mm2

Ig = 144 x 106 mm4

 

Deflection = 1.1 * 2500*2500* 2500*3350 / 8 * 26587 * 144x 106

 

                    = 1.88 mm

sep-BW.PNG

sep-wind.PNG

Link to comment
Share on other sites

On 12/15/2020 at 12:52 PM, Thila said:

Can I take “Ig” instead “Ie”, if Mservice /Mcracking <1, .Because, Ms is not exceeded the cracking moment.

Yes, your reasoning is right.

On 12/15/2020 at 12:52 PM, Thila said:

Also , kindly review the calculation below.

Calculation steps looks ok. But for calculating displacement, i would take L = 2.5 m since this is the length on which wind udl is acting.

If you want to take the full length of wall upto the base of footing, then you need to consider the soil lateral load on the wall as well.

Link to comment
Share on other sites

I don’t believe that modeling the wall with a pin support at ground level resemble the actual condition of the wall. The model more close to reality will be a wall with lateral springs distributed along the embedded depth.

This is easier said than done, because, we all know that soil is not a linearly elastic material and calculating its lateral subgrade modulus will not be as easy as dividing the, let’s say, passive resistance with a correlating estimated deflection. And before you ask, No, I will not be of much help in calculating the said property of the soil because most structural engineers (including me) are in a state of blissful ignorance when it comes to the properties of soil. We mostly rely on our geotech counterparts to provide us with all pesky soil related properties, such as, allowable capacity and subgrade reactions.

Now as for solution to your problem if I were you, I’ll simply design the wall, for both serviceability and ultimate limit states, ignoring the soil on the passive side and considering the total length upto the base of footing loaded with wind and active soil pressure. This, I believe, will be a safer approach in case of a boundary wall, because, you can never be sure of the possibility if someone is not going to dig up the soil on the other side of the property in future.

Link to comment
Share on other sites

Ok. Thank you.

But how can we ignore the soil fill load above the footing? How should we consider in calculating deflection.

If I consider only the wind and active pressure, deflection grows higher. Footing size and thickness of boundary wall also increases. 

To satisfy the overturning and sliding, 1.0m x 1.2m footing size is enough. But just because of this deflection criteria, footing size and also the thickness of wall increases. 

The below is link is related to the same discussion. FYI

https://www.sepakistan.com/topic/3126-short-term-cracked-deflection-for-cantilever-slab-in-safe/?tab=comments#comment-10203

Link to comment
Share on other sites

  • 1 month later...
On 12/24/2020 at 10:59 AM, Thila said:

But how can we ignore the soil fill load above the footing? How should we consider in calculating deflection.

Both the gravity and lateral load due to soil on the active side should be considered in the calculation. The soil resistance on the passive side however could be ignored to:

1.  Simplify the calculation.

2. There is a possibility that owner of the surrounding property can excavate the soil mass on the other side of the boundary wall in future without your consent.

3. Soil full passive resistance is something that develops as the soil mass is pushed due to significant wall rotation (approximately in order of 0.02 to 0.04 rad). And a designer would not really want this to be true for the serviceable live of the wall.

And, apologies for the delayed response.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.