Composite section
Muhammad Hashmi
Assalam O Alykum
The attached clause extracted from ACI318-11.
The supplier of pre-engineered structure is using  Metal Deck profile P-3623 that is a composite decking.
On the other hand they are saying  that steel joists are designed as a non-composite sections, then no need for the shear studs.
Is it logical ? Without connecting the shear studs and decking profile still works as a composite and metal deck will work as a positive reinforcement.
Can anybody advise?
ACI Code clause.pdf
Without shear studs, horizontal shear can not transfer between RC slab and metal and there is no composite action between metal deck and RC slab .
Some manufacturers of metal deck have designed their product such that their decks develops some degree of composite action without shear studs. Depending on the design loads, that may be enough.
Check your design loads and related effects to decide if you need 100% composite action.
As explained above that metal deck have inbulit shear capacity for the shear flow in some cases and if the joists or beams below are designed for the simply supported cases than the metal deck is pretty much behaving like a scaffold. So it is possible but again check your design requirements and if they are complied than should be no issue.