foundation design for 8 story building
Muhammad SAqib shah
hel0o,
i need an expert openion as i a, designing a raft foundation for 8 story building ,
1 ) i have provided a deep beam in the raft foundation , below the columns(column strip) , which is 48"x36 " (24" raft+ reamaining 24" beam ) and in the middle strip the raft is 24 " see attached (Fig111) , is this practice alright to make the design economical ? column size 24x24
secondly what if i shift the raft to the top of foundation  beam and , or in other words move the beams 24" below the raft  which is more suitable for clayey soil?
2) i want to assign soil springs as i want to do the analysis in ETABS so what should be the value of Area springs for .6tone/sqft ??
3) when i preform the analysis in SAFE (fig 222)t gives no results for column punching ? why is this so ?
4)why dosen't SAFE provide punching data for shear walls ?
4 ) My plot area is limited so the columns are on the edge of the raft  ,is this ok ?
thanks in advance
Edited by Muhammad SAqib shah
part 3 answer : We check punching shear for Raft when column is directly placed over the raft ( in case of no beam b/w raft and column similarly in case of flat plat slab ) but in your case column load is directly tranfered to the beam  which distribute it to the raft so there is no possibility of punching failure .
Note : you should then design the Beam of raft and also Beam stirrups spacing