Column Reinforcement along the stories
Sundass
in the image attached below, i am confused about the reinforcement of column "3E". As you can see the reinforcement in 2nd and third storey is 2.250 where as in 1st storey it jumped to 6.414. loading and panels on all stories are same. so what might be the reason for this change? is there any mistake or its normal behavior. if its normal, then what are the possible reasons for this. Moreover it is pertinent to mention that is the heaviest column in whole structure. its a three storey commercial building 45 x 48 sq feet. Looking forward to your valuable guidance.
Sundass,
The first thing will be to confirm if the loads are applied correctly and modelling is done correctly. That can be confirmed on your end.
For loads, should first see which load combination is governing. Say 0.9*D + 1.5Live is governing. You can manually calculate the dead load, and the live load. Check the reactions of basic load case of live and dead to your manual numbers to see if they match.
Once you have done it then comes the modelling. For modelling, the easiest thing would be to confirm deformed shape for each load case in the governing load combination and observing if it makes sense. Another thing that you can do is to use a spreadsheet or manual calc for column design or another software like PCA Col and check ETABS results.
It could be, be it requires checking and making sure there are no mistakes. Basic checking is required.
Hi Sundass, it would be better if you upload your model. However, In addition to what @Ayesha had suggested, I can see from your attached pic that, some of your columns are fixed and some are hinged at the base. Is it done deliberately or overlooked? Please check, as this may affect the model too. Also try changing the orientation of the columns and study the behaviour.