Stiffness Modifiers for Pick Up Columns
Wajahat Latif
Hi,
I need to provide pick up columns to support the landing beam of staircase. The story-level beams will also rest on these columns. The stiffness modifiers prescribed for columns by ACI is 0.7. I was wondering if I can reduce that to (say) 0.35 or less, since I don't want these columns to participate in resisting bending moments as much as the 'actual' columns. Note that their primary purpose was to support the staircase landing beam, so designing them on gravity only load should be fine?
Also, any thoughts on providing a pick up shear wall with f12 stiffness modifier = 0.0001 i.e. not letting it participate in lateral shear resistance?
Best,
Wajahat
The shear wall / column will still attract load based on deformation compatibility. I think there are some minimum ductility requirement for columns that are not part of lateral force resisting system. Check the building code you are designing too.
22 hours ago, Wajahat Latif said:
Hi,
Best,
Wajahat
Can you share your Pickup Column Drawing ,so that we can learn new thing?
15 hours ago, Badar (BAZ) said:
Yes, it is. You can also release rotational restraint at the the end of landing beam.
Thanks. That makes sense.
I guess in my case, since the pick-up columns are also connected to the slab-level beams, I should probably provide the same modifiers as the rest of the columns.
That's a good point. I'll see if I can find something in ACI. If you come across any such requirement, would be great if you can share it here. Thanks!
One more question, what support conditions do you recommend providing for pick up columns?
It's my understanding that no support restraint should be provided.
Here is the pick up column modeled in Etabs. Capture.thumb.PNG.5e753eb42a45f3a9cb0ea77a45262037.PNG
To ensure this in the field, we would need to provide a pin-connection detail, correct? A mesnager hinge would probably do. Do you have any details on that? Have you seen that in any project? Thanks.
22 minutes ago, Badar (BAZ) said:
You do not need any complicated detail for that. Just leave the top bars without hook in beam-column joint.
Okay. Hooks provided at the top-most and bottom-most ends of the column can be omitted. What about the intermediate story-level beam-column connections (referring to the circled region in the attached diagram)? Column bars are continuous here. Should we discontinue the column bars?
Idea is to stop the beam form transferring the negative moment to column. It is applicable at all levels. The longitudinal reinforcement of column does not effect. If I understood your situation correctly, there is no need for pick-up column to go beyond the landing slab at each level.