Pick Up Columns - Column Connection to Slab
Assalam O Alykum
Can anybody help on the below.
 1. How to calculate the anchorage length of rebar planted on the existing super structural slab (casted). Or it will be as per lock fix material supplier catalogs (for instance Hilti)
I read some where in Euro code that it should not be less than 10 times the diameter of rebar.  It would be great if can get reference from ACI.
2  One additional small thing I am not considering any bending moment on these pick up or planted columns and release the columns from the existing slab side.
I am also attaching pdf sketch for the column for guidance.
Thank you
PC 1 DETAIL.pdfFetching info...
Edited by UmarMakhzumi
Edited Topic Title.
You need to follow the guidelines of chapter 17 of AC318-14/19 or equivalent sections from older versions of the same code. Assuming, you do not have tension in the column, your post installed rebars must have enough embedment to satisfy the limit states corresponding to steel failure, concrete pry out and concrete breakout failure modes.
I have done a lot of these using Canadian Code.
In older versions of ACI, Appendix D in ACI 318 used to cover all the limit states (mentioned by Baz above as well). I don't know what is in the latest version but you calculate your loads including moments if any, and then calculate the minimum embedment capacity for different limit states against applied loading using ACI Appendix D.
If you are using Hilit, they have a free software called Profis Anchor that can do all the calculations for you. Just download and provide your rebar configurations, concrete edge distances and loads and it will calculate the embedment using Hilti Products.
  • UmarMakhzumi changed the title to Pick Up Columns - Column Connection to Slab
Assalam O Alykum
Salute :) Thanks to both of you . Just again 1 small question.
1. Can we ignore these minor bending moments as these pickup columns are starting from slab of 300mm thick and I am releasing the member from the slab side.
2. Do you mean Hilti profis rebar or Profis Anchor.
Thank you
member release.pdfFetching info...
Moments would be small as slab is thin. Don’t release. Model as fixed and design for that case accordingly.
I think different regions might have different versions of Hilti Softwares available. Normally Profis Anchor also has rebar option. I used it a few years ago. Umar and Zeeshan can also comment if needed.
Edited by Ayesha