Dual System Modeled as Sway/Non-Sway?


Wajahat Latif
 Share

Recommended Posts

Hi all, wanted your take on the following. 

Columns in a dual system (shear walls + IMRF) behave as non-sway since the shear walls provide bracing for the moment resisting frame (ACI 318-19, 6.2.5). When this system is modeled in ETabs, should we select 'Sway Intermediate' or 'Non-sway' framing type in 'concrete design overwrites'?

I believe the important IMRF checks of ACI chapter 18 would get ignored if we select 'non-sway'. 

An IMRF system on its own is designed to have an inherent ductility to resist seismic forces through sway action. 

Thanks.

Link to comment
Share on other sites

1 hour ago, Wajahat Latif said:

I believe the important IMRF checks of ACI chapter 18 would get ignored if we select 'non-sway'. 

Yes, they will be ignored.

But why do you want to select the non sway option?  Your design moments will not be effected much by the moment magnification factors and P-delta analysis if l/r ratio of columns is small, and if lateral drifts are also with in the limits.

If you are enabling the P-delta analysis option, program will magnify your column moments anyway based on the results of P-delta iterations even if non-sway option has been selected (sway part of moment magnification equation of ACI 318 is still there because of lateral loads).

One should not rely on the seismic checks performed by ETABs. Unless you have specified the actual reinforcement ( the ones in structural drawings) to the program, these results are useless.

Link to comment
Share on other sites

Thanks. I agree with your points. I was running into a problem with a couple of columns in a dual system building. Based on the ACI 318-19 criteria of slenderness effects (Section 6.2.5), these columns are classified as slender in a sway frame but non-slender in a non-sway frame (based on the different slenderness limits for sway and non-sway frames in this section). When they're behaving slender, the ACI check mentioned in Section 6.2.5.3 (i.e, second order moments < 1.4 * first order moments, screenshot attached) should be applied. For my case, these columns are failing this check. However, I know from manual calculation that this is a non-sway frame and the columns are infact non-slender, therefore, this check can be ignored. 

In ETabs 19, this check is applied whether the framing type is sway or non-sway (columns fail this check in both cases). This makes me wonder, does ETabs perform all slender column checks and calculations regardless of whether the column is slender or not? Any idea how ETabs checks column slenderness? 

Capture.PNG

Link to comment
Share on other sites

3 hours ago, Wajahat Latif said:

This makes me wonder, does ETabs perform all slender column checks and calculations regardless of whether the column is slender or not?

I have also pointed out this observation in this attached post.

3 hours ago, Wajahat Latif said:

Any idea how ETabs checks column slenderness? 

I  have looked at its manual. Here is what I found, and which also addresses why the ETABS magnifies moments even if you set column as non-sway.

ETABS split design forces in columns as M= Ms + (sway factor for amplification of forces)Mns; the component Ms is from lateral loads and Mns is from gravity loads only.

image.png

Sway factor is taken as 1, as the program "assumes" that Ms comes from the P-delta analysis. If P-delta analysis is performed, the moment magnification is already incorporated in that, and there is no need to amplify moments. So sway factor is taken as 1.

Once M has been calculated, the program amplifies it further by using a non-sway factor, see the attached.

image.png

So, if you have used non-sway option, then this non-sway factor will be 1. But, since you have performed the P-delta analysis for drift related checks, your forces have already been amplified. 

 

 

Link to comment
Share on other sites

I agree with your observations. The 'sway moment' is amplified by P-Delta considerations, whether the frame is sway or non-sway and whether the column is slender or not. Regarding your following statement:

1 hour ago, Badar (BAZ) said:

So, if you have used non-sway option, then this non-sway factor will be 1. But, since you have performed the P-delta analysis for drift related checks, your forces have already been amplified. 

I think the non-sway factor (catering for deformations between the member ends, i.e., P_smallDelta effects) would be computed in both non-sway and sway cases. No? In non-sway frames, only non-sway factor needs to be applied. However, since we're doing a P-Delta analysis, the sway factor is also inherently present. Similarly, in sway cases, both sway and non-sway factors need to be applied. So, in essence, ETabs is applying both sway and non-sway factors for all kinds of framing. 

As you've pointed out in the post you shared, as per code the moment magnification should not be applied for short columns, i.e., they can be designed on first order moments. However, given the above discussion, it seems these amplifications are being applied regardless if the column is short or slender. 

Now, I just noticed that the non-sway moment factor in "Concrete Frame Design Overwrites" is by default set as 1. We would need to set it to 0 for the program to compute this itself for each member for each load combination (screenshot attached). I suppose if we're confident that our columns are non-slender, then we can avoid the non-sway factor by keeping this as 1. The sway factor would still be applied via P-Delta. 

Capture.PNG

Link to comment
Share on other sites

16 minutes ago, Wajahat Latif said:

I think the non-sway factor (catering for deformations between the member ends, i.e., P_smallDelta effects) would be computed in both non-sway and sway cases. No

Yes, I agree.

 

20 minutes ago, Wajahat Latif said:

I suppose if we're confident that our columns are non-slender, then we can avoid the non-sway factor by keeping this as 1. The sway factor would still be applied via P-Delta. 

Yes!

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       