Hello all,

I am designing a Billboard Structure in StaadPro the details are 12 meter High, 5 meter wide and it is in "V" shape, I need to now the number of directions I need to apply the wind loads.

The claculated wind load as per ASCE is 1.3 kN/m on each column as columns are spaced at 1.25 meter Spacing along its width as shown with cross marks in pic below. Can anyone please elborate on number of load cases I need to consider for the design. A Hand Sketch for the same would be helpful.

Thanks !!

Struct.JPG

Link to comment
Share on other sites

You can simplify this. Calculate the maximum wind load and apply it perpendicular to the surface. I would connect the member between the two billboards to make a “space truss”. 
 

I am not familiar with ASCE but in National Building Code of Canada we have different formulae to calculate wind load on signage and boards, walls etc so make sure you are using the correct formula in ASCE as I assume they would have something similar (assuming) .. take some time and research the document.

Thanks. 

Link to comment
Share on other sites

For directionality, perpendicular to surface would make sense. Some people might say that wind will simultaneously act on say both surfaces (say if it blows left to right) first it hits the first billboard and then the second one by entering inside the V, but I personally believe that would be unlikely since inside the V, there would be “dead air” that would let external wind slide by. I got this concept is one of AISC presentations. Let me find it if you are interested in it. Again this is just an opinion. It all depends what you think as engineer if you are the engineer of record.  Also a lot of engineers that I have worked with will just make a very conservative first case, for example, for your situation like double the wind load and see if everything still passes and if it does, leave it there. 

Thanks. 

Edited by UmarMakhzumi
Added additional response.
Link to comment
Share on other sites

Yes I did the same but Load, I kept it same as per calculation. According to my understanding The maximum load will from one direction, as the back side is open the wind load will be on bracings only and that too will be very less.

Just a question out of context is, do you have idea of allowable deflection for the columns of such signs as I am getting maximum deflection under service loads as 13mm at the tip.

I am also attaching staad files for your reference.

Wind Load.JPG

PS-Sign board.std

Link to comment
Share on other sites

I don't personally think that there is any deflection requirement unless you are mounting cladding type advertising panels that have deflection requirement(higher deflection might break the panel)   Also, I am noticing that you have used fixed base. What kind of details you have for the column base. If you change it to pin, (assuming columns are connected), the deflection will increase substantially.

Kind Regards,

 

Link to comment
Share on other sites

Thanks Mr.Umar for, your response. I used fixed support as I am going to use a base plate mounted on a contineous concrete pad measuring around 5.8 meter in length 1.2 in width and depth.

Is there any issue if I use it as fixed base.

Link to comment
Share on other sites

No, there are no concerns. Generally speaking, with narrow edge distance and shallow embedment of anchor bolts,  it is hard to develop them for tension. Your loads might not be big enough so you might be good, but the base fixity just caught my eye so I thought I will ask you. 
 

Thanks. 

Link to comment
Share on other sites

  • 2 weeks later...
On 8/31/2021 at 8:08 PM, SMAQ said:

Thanks Mr.Umar for, your response. I used fixed support as I am going to use a base plate mounted on a contineous concrete pad measuring around 5.8 meter in length 1.2 in width and depth.

Is there any issue if I use it as fixed base.

hi i would have done it with pinned support in the model to get the net tension compression force at the base. i suspect your foundation size is not adequate ( just experience), as the framing you said above is 12mx5m = 60m2 *1.33= 79.8Kn *6= 473kn-m say the moment arm below 1.2m (foundation size) , 473/1.2= 394kN times your safety factor = 394*1.5 = 591 kN, if you go further and increase your moment arm still you got quite a force to resist the uplift. have a look at your foundation in each direction.   

Link to comment
Share on other sites

@Nustian371Thanks for your interest and feedback. Yes, you are right, those foundations were failing in uplift. Those were as per my initial assumptions. I Finally opted for a Trapezoidal Raft of 8X3.2X0.6 meter ☺️.

Edited by SMAQ
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       