HOLLOW CORE SLABS


Muhammad Hashmi
 Share

Recommended Posts

Assalam O Alykum 

Small question

The hollow core slabs are defined as a membrane or shell element ( In the direction of hollow core panels)

As a hollow core slabs are rests by bearing on the beams with grout and screed on the top with no composite action between beams and hollow core slab.

Thank you 

1.JPG

Link to comment
Share on other sites

This structural element has shear, flexural and axial stiffness. It is not a membrane. Having said that, you can model it as membrane; You need  to decide about the modelling approach based on your design assumptions for supporting members and structural system as whole.

Link to comment
Share on other sites

Thanks Muhammad for your reply

Dowel bar will be provided to make it as connection between the hollow core slab and cast in place beams.

Beams supporting the hollow core slabs will be designed by us and hollow core slabs will be designed by the specialists.

My question is that this dowel bar will really create a composite action between hollow core slabs and cast in place beams

& considered enough to define the slab as shell in our E-tabs model.

To design the slab as membrane will increase the amount of reinforcement too much.

 

 

image.png.cd50eb5a5ecce4be8fe19f691569d9fa.png

 

 

 

Link to comment
Share on other sites

Yes, membrane assignment will do the job assuming that you are only concerned abut estimation of demands on the frame elements and not the hollow-core slab itself.

With your shear connection detail between beam and slab in the form of rebar-dowels, it would be wrong to model the slab with flexural stiffness (shell) , as it would lead to an underestimation of flexural demands on beams.

Link to comment
Share on other sites

Thanks Muhammad 

What if I can define slab as a shell and reduced the bending M11 direction ,  bending M22 direction and bending M12 direction = 0.01. 

Or apply the linear load on the beam in the direction of one way slab or in other words as per the below snap shot 

 

image.png.393938912db4a790637f4ef0e6fe4519.png

Link to comment
Share on other sites

2 minutes ago, Muhammad Hashmi said:

What if I can define slab as a shell and reduced the bending M11 direction ,  bending M22 direction and bending M12 direction = 0.01. 

This approach will give you the same behavior as membrane.

4 minutes ago, Muhammad Hashmi said:

Or apply the linear load on the beam in the direction of one way slab or in other words as per the below snap shot 

I am not sure about your intent. The UDL is not the only effect of connection that you intend to use.

Let me explain it this way: The beams supporting the ends of one-way ribs of hollow-core floor system will need to be loaded with the line load and torsion. See the attachment.

 

16032022155325-0001.jpg

Link to comment
Share on other sites

Thank you Muhammad for clarification

1. You mean linear load plus torsion on the beam will be the effect on the cast in place beams. Shall I understand torsional constant must be applied on the program along with stiffness modifiers of beams 0.35?

3. Diaphragm I applied as a semi rigid.

4. Building components such as columns , shear walls will be designed based on the membrane as well or can say shell with stiffness modifier 0.01? shall I say like that

image.png.e8013860104ff9c8d5ca641383429301.png

Link to comment
Share on other sites

My name is Badar. You are addressing me with the wrong name.

2 hours ago, Muhammad Hashmi said:

You mean linear load plus torsion on the beam will be the effect on the cast in place beams. Shall I understand torsional constant must be applied on the program along with stiffness modifiers of beams 0.35?

It seems that you are not able to realize that the eccentric nature of connection between  cast-in-place beam and pre-cast hollow core slab will transfer torsion in addition to the UDL in the beam.

It is better, in this case, to design the beam for the torsion due to eccentric transfer to shear between slab-beam interface. Do not use 0.35 modifier for torsional constant.

The practice of using a modifier <1 for torsional constant is for monolithic construction involving combability torsion, which is due to the transfer of negative moment from slab end to  the supporting beam (you do not have these moments because of your connection detail).

Link to comment
Share on other sites

Thank you Badar for your continuous support.  

You are right I am unable to realize How much will be the torsional constant shall I consider design the beams. 

apologies if you advice about the below as well 

Diaphragm I applied as a semi rigid.

Building components such as columns , shear walls will be designed based on the membrane as well or can say shell with stiffness modifier 0.01? shall I say like that

Link to comment
Share on other sites

14 hours ago, Muhammad Hashmi said:

Diaphragm I applied as a semi rigid.

I do not have enough information about your framing to comment on that.

 Generally speaking, this assignment, in most cases, has a limited effect on  elements of Vertical Lateral load resisting system.

When Structural Engineers  intend to check forces in chord members of diaphragm, for the purpose of estimating its suitability to transfer lateral forces to vertical elements, they use this semi-rigid option. The rigid-option does not let you check these  diaphragm forces.

The assignment also depends on your structural system. CSi has a simple video on it. 

 

 

14 hours ago, Muhammad Hashmi said:

Building components such as columns , shear walls will be designed based on the membrane as well or can say shell with stiffness modifier 0.01? shall I say like that

You cannot assign membrane behavior to column.

You can assign membrane behavior to shear walls. It is reasonable simplification for a majority of design scenarios. 

Link to comment
Share on other sites

Straying away from your questions, I am curious how will the construction of floor-system with these connection details take place?

Will they cast the frame with rectangular X-sections of beams first, and then install the panels?

Will they drill the dowels afterwards? Will the dowels be left in place during pouring of concrete for RC beams.

How will they adjust the dowels at their right position in precast hollow-core panels?

For these kind of construction, I have seen following construction methodologies:

1- Hollow-core panels supported on ledges of RC/Pre-case beams.

2- Hollow-core panels supported on horizontal joint of RC beams. In this case, they do not pour concrete on the full depth of beam, leaving room equal to the thickness of floor on top of horizontal joint with-in beam's depth.

Link to comment
Share on other sites

21 hours ago, Muhammad Hashmi said:

Framing plan is attached for one floor almost same for other floors as well.

How much will be the torsional constant shall I consider to design the beams. 

Rigid diaphragm is reasonable assumption for this kind of arrangement for vertical members of lateral-structural system. 

I already answered the issue of torsion constant. In the first run, analyze the section with out using any reduction in constant for torsion (use 1).

Make changes if you are redistricted in the choice of section size for beam. In this case, how will you know if the additional flexural demands in hollow-core panels, due to torsion-related cracking in RC beam, will be taken into account?

Link to comment
Share on other sites

Make changes if you are redistricted in the choice of section size for beam. In this case, how will you know if the additional flexural demands in hollow-core panels, due to torsion-related cracking in RC beam, will be taken into account?

Eng Badar I could not get this point 

Link to comment
Share on other sites

Do you understand that the supporting beam is subjected to torsion, in addition to shear and bending moment, due to connection detail chosen for transferring forces from the precast hollow-core slab to RC beam?

Can you imagine what will happen if beam has not been designed for the interaction of torsion and shear?

Can you imagine that the beam will tend to twist or rotate about its longitudinal axis if the adequate amount of torsional reinforcement is not present?

What will be the result of that rotation?

In this case, can it lead to an increase in connection forces that may not have been accounted for?

Link to comment
Share on other sites

Assalam O Alykum

Do you understand that the supporting beam is subjected to torsion, in addition to shear and bending moment, due to connection detail chosen for transferring forces from the precast hollow-core slab to RC beam?

yes i understand. Final connection detail is not yet received from the designer of HCS. The detail which I shared is preliminary. 

Can you imagine what will happen if beam has not been designed for the interaction of torsion and shear?

Can you imagine that the beam will tend to twist or rotate about its longitudinal axis if the adequate amount of torsional reinforcement is not present?

What will be the result of that rotation? 

Yes I can understand. 

In this case, can it lead to an increase in connection forces that may not have been accounted for?

Any possibility of sending any recommended connection details to avoid any torsion or reduced the torsion on the cast insitu beams.

Link to comment
Share on other sites

7 hours ago, Muhammad Hashmi said:

 

In this case, can it lead to an increase in connection forces that may not have been accounted for?

Any possibility of sending any recommended connection details to avoid any torsion or reduced the torsion on the cast insitu beams.

Baz replies are very detailed, and here is one item I can re-elaborate on since you have asked it again.

Because the way your slabs are being connected to your beam (The slab is connected to the face of the beam), you will always have torsion and you need to deign for that torsion as that is the only load path from slab to beam with the provided connection concept. 

If you want to reduce or avoid torsion, your slab to beam connection philosophy needs to be revised. For example, if this hollow slab was "casted above the beam" you will not have this issue (torsion will reduce at the center beams but will still have torsion at corner beams), but you will need to connect your slab and beam through some system and in that way your beam depth will be much smaller. 

Thanks.

Edited by UmarMakhzumi
Updated the response to make more detailed. See underlined and italic.
Link to comment
Share on other sites

  • 2 months later...

Assalam O Alykum

Dear Badar 

Do you have any authentic ledge design spread sheet for the cast in place ledge for L and T ledges both.

Small confusion regarding the torsion on cast in place T Beams. If we are talking about torsion on the T-beam or the middle beams where the Hollow core slab is resting on both sides. We are saying that torsion occurs during construction right?

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       