Use of structural lean concrete / blinding concrete
Muhammad Hashmi
Assalam O Alykum
In the same project / same consultant engineer
1. For G+1 story building having length 45m and width of 16m emphasizing to use the structural lean / blinding concrete ( non reinforced with fiber or mesh) having thickness 200mm and 200mm offsets minimum from all sides from the footing with compressive strength 30MPA.
2. Provide the size of footing by considering the bearing capacity of blinding / lean concrete 300 Kn per meter square or  30 MPA. In other words, footings will be designed based on the compressive strength of concrete.
3 Provide the size of blinding offsets from the face of footing by considering the bearing capacity of soil that is 200 Kn per meter square.
Does any code allow us to use such type of practice to get economical result. My practice is to provide blinding just to have plain surface /level or safe from mud at the time of raining.
If seniors can help particularly in this regard
Salam,
For foundation design actual bearing capacity of soil shall be considered, lean concrete can improve immediate bearing under foundation but soil bearing shall not be improved, this is my understanding, other fellows and seniors shall share their opinion please.
Walikum us Salam
1- Concrete having strength 30 mpa is not a lean concrete. In fact Aci 318-19 chapter 19 prescribes minimum strength of 2500 psi for structural concrete which is slightly more than 17 mpa.
2- For plain concrete footing refer to ACI 318-19 chapter 14 in general and 14.3.2 in particular.
3- you need to design the thickness on basis of reaction and footing offset.
Edited by Muhammad Imran Zafar